Friends:
On a r
in their installation manuals, SolArk indicates black and red colors for PV
conductors.
___
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email
complicated!”
>
>
>
> William Miller
>
>
>
> Miller Solar
>
> 17395 Oak Road, Atascadero, CA 93422
>
> 805-438-5600
>
> www.millersolar.com
>
> CA Lic. 773985
>
>
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org]
;
>
>
> Confusing? Yeah, a bit. But as my local roofing companies say: “Solar?
> It can’t be that complicated!”
>
>
>
> William Miller
>
>
>
> Miller Solar
>
> 17395 Oak Road, Atascadero, CA 93422
>
> 805-438-5600
>
> www.millersolar.com
&
alf of
William Miller via RE-wrenches
Sent: Wednesday, June 5, 2024 12:53:52 PM
To: RE-wrenches
Cc: William Miller
Subject: Re: [RE-wrenches] Sol-Ark 15k solar panel frame grounding
Friends:
On a related subject, I was researching the question: What color should my
grounded PV conduc
ches.or
g] On Behalf Of Jason
Szumlanski via RE-wrenchesSent: Wednesday, June 5, 2024 6:02 AMTo:
RE-wrenchesCc: Jason SzumlanskiSubject: [RE-wrenches] Sol-Ark 15k solar panel
frame grounding Can anybody clarify the following instruction from the manual?
"GND the panel MOUNTS/FRAMES to any
*Sent:* Wednesday, June 5, 2024 6:02 AM
*To:* RE-wrenches
*Cc:* Jason Szumlanski
*Subject:* [RE-wrenches] Sol-Ark 15k solar panel frame grounding
Can anybody clarify the following instruction from the manual?
"GND the panel MOUNTS/FRAMES to any GND outside the circuit via 12AWG wire"
This is a partial backup scenario and the main service panel has a solid
neutral to ground bond. I have not been able to find anywhere else where
there is a bond, but there is always the chance that there is a neutral
wire in a switch box or outlet box somewhere in the house that is touching
an equ
Hi Jason,
You should be able to land your PV EGC in the inverter ground bar. You
could do a quick resistance check to verify the +, - PV
Is there a bond somewhere (upstream service panel or in the Sol-Ark itself)
between ground and neutral? If not, this can cause this fault.
On Wed, Jun 5, 202
I usually get the 08 GFDI error when I haven’t bonded neutral to ground
downstream. (Typically because I booted up the inverter after DC connection but
before any AC wires are landed.) That goes away once it is fully commissioned.
I get the F23 - Tz_GFCI_OC_Fault If is related to the PV array,
Can anybody clarify the following instruction from the manual?
"GND the panel MOUNTS/FRAMES to any GND outside the circuit via 12AWG wire"
Does this mean do not connect the array equipment grounding conductor to
the grounding terminal in the inverter? Where would be the suggested place
to connect