Re: [RE-wrenches] Tigo RSS Off Grid

2024-02-21 Thread Nick A Lucchese via RE-wrenches
Sorry Howie, I now see you were specifically asking about inverter/charge controller combo solutions. I should have caught that detail. Still seems as an easy workaround though if for some reason the inverter manufacturer failed to isolate the 12v output independent of the AC output LBCO.

Re: [RE-wrenches] Tigo RSS Off Grid

2024-02-21 Thread Nick A Lucchese via RE-wrenches
The 48v to 12v DC converter approach should be immune from the inverters LBCO since it lives on the battery side of the inverter/bus. I’ve done a few systems using Tigo’s without issue. The main concern is you now have a DC load attached to the battery output lacking DC load protection that

Re: [RE-wrenches] Tigo RSS Off Grid

2024-02-21 Thread Howie Michaelson via RE-wrenches
With the Sol-Ark (or other DC coupled inverter/charge controller combinations such as the Envy), will the system pass through solar power if the inverter has turned off on LBCO? If not, then these alternative methods for powering the RSD signal generators won't make a difference, correct? And does

Re: [RE-wrenches] Tigo RSS Off Grid

2024-02-17 Thread Ray Walters via RE-wrenches
I second using the 48v to 12 v DC DC converter.  I've had success with that, and avoided the issues Jeremy mentioned. Ray Walters Remote Solar On 2/17/2024 9:35 AM, Bradley Bassett via RE-wrenches wrote: I powered a MidNite LSOB transmitter from a Classic AUX, though the receivers didn't work

Re: [RE-wrenches] Tigo RSS Off Grid

2024-02-17 Thread bob--- via RE-wrenches
Hi Jeremy... The Classic AUX outputs will put out about 13 volts and allow up to about 200 mA maximum. That might be enough to power the transmitter. That is only about 2.5 watts so might not work directly. boB Docked at Trinidad/Tobago today.  Great sun here.  Have only seen one PV

Re: [RE-wrenches] Tigo RSS Off Grid

2024-02-17 Thread Bradley Bassett via RE-wrenches
I powered a MidNite LSOB transmitter from a Classic AUX, though the receivers didn't work with the Classic. The Classic is limited to 200ma output and the Tigo and APS transmitters are rated at up to 800ma input, so it might overload the Classic AUX output if they really do draw that much. I

[RE-wrenches] Tigo RSS Off Grid

2024-02-16 Thread Jeremy Rodriguez via RE-wrenches
Has anyone successfully used a MidNite Classic CC to power a Tigo Rapid Shutdown Transmitter in an off grid setting ? Specifically using the 12v Aux output to keep the PV circuits alive instead of relying on the inverter AC output to do this. Think of this scenario. Batteries reach LBCO,

[RE-wrenches] Tigo Hybrid Inverter

2023-05-08 Thread rick--- via RE-wrenches
Hey Wrenches, Does anyone have experience with Tigo’s new hybrid inverter? Thanks, rick brown SolShine Energy Alternatives, LLC Electrical & Solar Contracting Services www.SolShineEnergy.com O: 540.235.3095 M: 540.808.9502 VA Class A Contractor Lic# 2705147660 VA Master Electrician Lic#

Re: [RE-wrenches] Tigo Rapid Shutdown equipment

2021-08-27 Thread Corey Shalanski
Dave et al., Please note that SMA no longer offers the TS4-R-F devices—according to our distributor, they ceased offering them toward the end of last year. SMA maintains a list of compatible rapid shutdown receivers here

Re: [RE-wrenches] Tigo Rapid Shutdown equipment

2021-08-25 Thread Thomas Hall
1 at 3:03 AM To: cwar...@entech-engineering.com , RE-wrenches Subject: Re: [RE-wrenches] Tigo Rapid Shutdown equipment Hi Chris, I also am curious of others experiences. I've got one system with SMA and the TS4-R-F. No problems, but it's only 6 months old. I hear that SMA now recommends the ones

Re: [RE-wrenches] Tigo Rapid Shutdown equipment

2021-08-25 Thread Dave Tedeyan
Hi Chris, I also am curious of others experiences. I've got one system with SMA and the TS4-R-F. No problems, but it's only 6 months old. I hear that SMA now recommends the ones made by JMS, but it looks like essentially the same thing. Cheers, Dave On Tue, Aug 24, 2021, 11:22 AM Christopher

[RE-wrenches] Tigo Rapid Shutdown equipment

2021-08-24 Thread Christopher Warfel
WRENCHES, We are meeting our customer demand for more multimode systems. All are grid interconnected. I wanted to use micro inverters to ac couple, but I have to look at the better economics of dc coupling.  I have never used a dc module level Rapid Shutdown device. In the past we have had

Re: [RE-wrenches] Tigo

2015-10-15 Thread Solar
I've used them a few times and have them on my home due to a small shade issue. Like mentioned the monitoring is great, lots of data. Never had a problem with any parts. Jesse Sent from my iPhone > On Oct 14, 2015, at 8:22 PM, Marco Mangelsdorf wrote: > > Hola amigos y

Re: [RE-wrenches] Tigo

2015-10-14 Thread Roland Shackelford
Aloha Marco, We have been very happy with their operation and online monitoring capabilities. We have had DOA management units, but Tigo technical support has been accessible and replaced them with no difficulties. We have had no failures on module maximizers. Their ability to manage shading is

[RE-wrenches] Tigo

2015-10-14 Thread Marco Mangelsdorf
Hola amigos y amigas. I'd appreciate feedback on the use of Tigo DC optimizers, specifically with the SMA TL line. Any good, bad or ugly stories to share? Mahalo, marco provision_highres_solar_logo2 with C-26351 Marco Mangelsdorf, President 69 Railroad Avenue, A-7 Hilo, Hawai'i

[RE-wrenches] TIGO/ Classic 250 fights?

2014-07-04 Thread dan
Anyone else having problems with Midnight Classics Flaming out (Literally)? We know they don't play nice with Tigo Optimizers. Wondering if a Midnight SPD might also look like a short to a classic when it clamps. only affected two of the four controllers. Two seemed to be un affected, one tripped

Re: [RE-wrenches] TIGO/ Classic 250 fights?

2014-07-04 Thread b...@midnitesolar.com
The SPD will (or, should), clamp the input voltages, both positive and negative to ground at the MOV voltage rating during a lightning strike. The SPD 300 starts at about 500 volts on each leg of the SPD. The 600 SPD is higher voltage of course. Since, on the PV input side, the MOVs appear

Re: [RE-wrenches] TIGO/ Classic 250 fights?

2014-07-04 Thread b...@midnitesolar.com
In addition, an SPD is supposed to keep any input lines to the equipment from breaking over the insulation. For the Classic, the hipot voltage is over 2000 volts to chassis (gnd). If the SPDs are grounded and connected well they should be able to do their job unless maybe it is a direct

Re: [RE-wrenches] Tigo

2014-02-08 Thread dan
Corp.Renewable Energy Systems(802)-483-2564www.Foxfire-Energy.comNABCEP #092907-44 Original Message Subject: [RE-wrenches] Tigo From: Dana Brandt d...@ecotechenergy.com Date: Thu, February 06, 2014 8:48 pm To: RE-wrenches re-wrenches@lists.re-wrenches.org We haven't used any

Re: [RE-wrenches] Tigo

2014-02-07 Thread Solar
I have them on my system at home and on a system at a local community college. I like the data available from the system. My system had shade issues so I like the idea of them with issues suck as mine. I mounted the gateway device in the attic bellow the array instead of outside at the array.

[RE-wrenches] Tigo

2014-02-06 Thread Dana Brandt
We haven't used any of these yet but I'm considering it. Anyone have any experience they can share? Thanks, Dana Dana Brandt Ecotech Energy Systems, LLC www.ecotechenergy.com d...@ecotechenergy.com 360.318.7646 ___ List sponsored by Home Power

[RE-wrenches] Tigo and SMA AFCI - Was: AC coupled, grid-tied Sunny Island - contactor bypass

2013-06-05 Thread SunHarvest
Just an FYI for anyone wanting to use Tigo optimizers with SMA inverters incorporating AFCI - According to SMA the Tigo optimizers will not operate with the SMA inverters. They didn't go into detail. They just said the AFCI feature of the Sunny Boy is not compatible with Tigo. After further

Re: [RE-wrenches] Tigo and SMA AFCI - Was: AC coupled, grid-tied Sunny Island - contactor bypass

2013-06-05 Thread Ryan
From Robin It has been pointed out that the Tigo modules can and do blow up some charge controllers and inverters. When a charge controller or inverter has fairly fast tracking, the two units fight each other. We have found Classics using the fast tracking mode will blow up with Tigo's in the

[RE-wrenches] Tigo and Solar edge

2012-10-29 Thread Kirk Herander
I have been asked to design module-level monitoring for an old system with a string inverter. I see that Solar Edge has a SMI interface which allows panel monitoring without using their in-house inverter. Has anyone tried this yet? There is no manual that I can find on their website for the SMI.

Re: [RE-wrenches] Tigo Tech Support Response

2012-10-22 Thread Jesse Dahl
am out of hospital after 90 days looking forward to full recovery by spring, Hi everyone, I seem to have made it. From: David Katz dk...@aeesolar.com To: RE-wrenches re-wrenches@lists.re-wrenches.org Sent: Wednesday, October 17, 2012 11:34 AM Subject: Re: [RE-wrenches] Tigo Tech

Re: [RE-wrenches] Tigo Tech Support Response

2012-10-21 Thread Darryl Thayer
it.    From: David Katz dk...@aeesolar.com To: RE-wrenches re-wrenches@lists.re-wrenches.org Sent: Wednesday, October 17, 2012 11:34 AM Subject: Re: [RE-wrenches] Tigo Tech Support Response Larry and Dan, Jacob’s response is a bit misleading. Tigo Maximizers operate

Re: [RE-wrenches] Tigo Tech Support Response

2012-10-17 Thread David Katz
, October 17, 2012 7:16 AM To: RE-wrenches Subject: Re: [RE-wrenches] Tigo Tech Support Response Dan, Thanks for posting this. I am fascinated and puzzled with their response. Why would they not advertise this point? I see nothing on their site that suggests the Module Maximizer functions with off

[RE-wrenches] Tigo Tech Support Response

2012-10-16 Thread dan
Hi Guys, following is the response from Tigo on the question of using their optimizers for battery charging:Hello DanThank you for the phone call yesterday. I have answers to some of your questions.- At the moment, we only sell arc fault detection services to combiner box manufacturers to

[RE-wrenches] Tigo Optimizers.

2012-10-11 Thread Carl Emerson
Dan mentioned Tigo Optimizers. I looked at the website and can see that when shading is anticipated, this product has great potential. Is there any performance information available that would justify using this product on unshaded arrays??? Do we have a real alternative to the

Re: [RE-wrenches] Tigo Optimizers.

2012-10-11 Thread Jesse Dahl
I have Tigos on my system at home. I have very little shading on my array but I wanted to test these out. I do see increased harvest from my array using the Tigos. If you contact me off list I will send you the link to my systems so you can check it out. They do seem to work as advertised. I

Re: [RE-wrenches] Tigo to go?

2011-06-09 Thread Mark Frye
://www.berkeleysolar.com/ www.berkeleysolar.com _ From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Marco Mangelsdorf Sent: Wednesday, June 08, 2011 7:59 PM To: 'RE-wrenches' Subject: [RE-wrenches] Tigo to go? What's

[RE-wrenches] Tigo to go?

2011-06-09 Thread Marco Mangelsdorf
-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Marco Mangelsdorf Sent: Wednesday, June 08, 2011 7:59 PM To: 'RE-wrenches' Subject: [RE-wrenches] Tigo to go? What's the feedback on these Tigo buggers? I'm not talking about sites where shading is an issue, but a nice big commercial roof

[RE-wrenches] Tigo to go?

2011-06-08 Thread Marco Mangelsdorf
What's the feedback on these Tigo buggers? I'm not talking about sites where shading is an issue, but a nice big commercial roof with no shading. Specifically, I'm talking about a 400-module system feeding into a single PV Powered 100 kW inverter. Anyone have an opinion whether spending

Re: [RE-wrenches] Tigo to go?

2011-06-08 Thread Bill Brooks
for firefighters can help sweeten the deal. Bill. From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Marco Mangelsdorf Sent: Wednesday, June 08, 2011 7:59 PM To: 'RE-wrenches' Subject: [RE-wrenches] Tigo to go? What's