[Sprinklerforum] Re: UUP / Plastics A unexpanded exposed

2024-07-19 Thread Anthony Carrizosa
.. You may also want to look into putting a combination of roof sprinklers and in-rack sprinklers to accomplish this. Are there smoke and heat vents in the building? If so and a roof height of 27' or lower, you could do the special design of .60/2000 with standard heads. Have a good day. Anthony

[Sprinklerforum] Re: Water Tank for Standpipe

2024-07-01 Thread Anthony Carrizosa
Per NFPA 25 only automatic standpipes are required to be flow tested. Why is this one being tested? From: Brian Harris Sent: Monday, July 1, 2024 7:57 AM To: Discussion list on issues relating to automatic fire sprinklers Subject: [Sprinklerforum] Re: Water Tank for Standpipe Mostly volume,

[Sprinklerforum] Re: Standpipe Calculations

2024-04-04 Thread Anthony Carrizosa
with the FM to discuss this in advance as NFPA 14 states. Anthony Carrizosa Project Manager | Fire Protection 7855 S 206th St Kent, WA 98032 Cell: 206-679-5283 | Office Dir: 253-341-4593 [cid:image001.jpg@01DA868C.6225F890] https://archerconstruction.com<https://linkprotect.cudasvc.com/

[Sprinklerforum] Re: Standpipe Calculations

2024-04-03 Thread Anthony Carrizosa
I think Don kern hit it on the head, Unless it’s a high rise then a manual standpipe system is all that’s needed. Anthony Carrizosa Project Manager | Fire Protection 7855 S 206th St Kent, WA 98032 Cell: 206-679-5283 | Office Dir: 253-341-4593 [cid:image001.jpg@01DA85A5.421C2610] https

[Sprinklerforum] Re: Riser in a rated stair enclosure

2024-03-26 Thread Anthony Carrizosa
We do backflows and risers in stairs all the time, typically below the intermediate landing, as long as it’s a minimum 1 hour construction then it has been ok with most jurisdictions. Remember standpipes and floor controls are typically in stairs as a standard. Anthony Carrizosa Project

[Sprinklerforum] Re: ESFR & Concrete Tee's

2024-03-19 Thread Anthony Carrizosa
Brian, You could use a non-ESFR sprinkler like the Tyco K17-231 standard response, standard coverage sprinkler. It comes in both upright and pendent. Area density method with a .60/2000. Then the rules for ESFR do not apply. Anthony Carrizosa Project Manager | Fire Protection 7855 S 206th St

[Sprinklerforum] Re: Gang drain crossing seismic joint

2024-03-14 Thread Anthony Carrizosa
Yes Steve, you made us all think and use our brains today.. Anthony Carrizosa Project Manager | Fire Protection 7855 S 206th St Kent, WA 98032 Cell: 206-679-5283 | Office Dir: 253-341-4593 [cid:image001.jpg@01DA7619.DC46AC10] https://archerconstruction.com<https://linkprotect.cudasvc.com/

[Sprinklerforum] Re: Gang drain crossing seismic joint

2024-03-14 Thread Anthony Carrizosa
Well summed up Ken.. Anthony Carrizosa Project Manager | Fire Protection 7855 S 206th St Kent, WA 98032 Cell: 206-679-5283 | Office Dir: 253-341-4593 [cid:image001.jpg@01DA7619.39384560] https://archerconstruction.com<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2farcherconstruction.com%2

[Sprinklerforum] Where does it say a minimum clearance of 36" is required around Exterior FDC

2024-03-07 Thread Anthony Carrizosa
I can't seem to find the required minimum clearance around an FDC. I could swear I seen it in the past and believe it's 36" but can't seem to find it now? Anthony Carrizosa | Fire Protection Estimator / Project Manager 7855 S 206th St Kent, WA 98032 Direct: 253-341-4593 | Mobile: 206-679

[Sprinklerforum] Re: Manual Wet Standpipe Inspection

2024-03-06 Thread Anthony Carrizosa
Derik, NFPA 25 states flow tests 6.3.1 Shall be conducted every 5 years on all automatic standpipe systems.. your system is not automatic but manual. Since it is under water pressure at all times no need for a hydro test either. Anthony Carrizosa Project Manager | Fire Protection 7855 S 206th

[Sprinklerforum] Re: Concrete Beams -- NFPA 13, 2016

2024-02-09 Thread Anthony Carrizosa
there.. Anthony Carrizosa Project Manager | Fire Protection 7855 S 206th St Kent, WA 98032 Cell: 206-679-5283 | Office Dir: 253-341-4593 [cid:image002.jpg@01DA5B5F.DFD12F60] https://archerconstruction.com<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2farcherconstruction.com%2f=

[Sprinklerforum] Re: Concrete Beams -- NFPA 13, 2016

2024-02-09 Thread Anthony Carrizosa
with 8.6.5.1.2 (3) Installed in each bay of obstructed construction, with the deflectors located a minimum of 1 in. (25 mm) and a maximum of 12 in. (300 mm) below the ceiling Anthony Carrizosa Project Manager | Fire Protection 7855 S 206th St Kent, WA 98032 Cell: 206-679-5283 | Office Dir: 253-341-4593

[Sprinklerforum] Re: Small ESFR system

2024-02-08 Thread Anthony Carrizosa
. Anthony Carrizosa Project Manager | Fire Protection 7855 S 206th St Kent, WA 98032 Cell: 206-679-5283 | Office Dir: 253-341-4593 [cid:image001.jpg@01DA5A75.025354A0] https://archerconstruction.com<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2farcherconstruction.com%2f=

[Sprinklerforum] Re: Air venting

2023-10-09 Thread Anthony Carrizosa
Todd The Appendix states every time you drain and refill the system you must release the trapped air, so by definition a system has a control valve, Water flow switch and a drain. thus each floor can be independently shut off and drained then refilled, thus they would need an air vent. From:

[Sprinklerforum] Re: Air venting

2023-10-09 Thread Anthony Carrizosa
of a system. I agree that you would need an air vent for each floor. Anthony Carrizosa Project Manager | Fire Protection 7855 S 206th St Kent, WA 98032 Cell: 206-679-5283 | Office Dir: 253-341-4593 [cid:image001.jpg@01D9FA91.092E9530] https://archerconstruction.com<https://linkprotect.cudasvc.

[Sprinklerforum] Re: Standpipe PRV Question

2023-09-25 Thread Anthony Carrizosa
Very good point.. Anthony Carrizosa Project Manager | Fire Protection 7855 S 206th St Kent, WA 98032 Cell: 206-679-5283 | Office Dir: 253-341-4593 [cid:image001.jpg@01D9EFB2.8A0830B0] https://archerconstruction.com<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2farcherconstruction.com%2f=

[Sprinklerforum] Re: Standpipe PRV Question

2023-09-25 Thread Anthony Carrizosa
pressure at the suction side of the fire pump supplying the automatic sprinkler system. This is describing how the piping arrangement should be for this tank and pump. Which is exactly how we have done it here. Anthony Carrizosa Project Manager | Fire Protection 7855 S 206th St Kent, WA 98032 Cell: 206

[Sprinklerforum] Re: Standpipe PRV Question

2023-09-25 Thread Anthony Carrizosa
Per NFPA 25 Tank internal inspection is required every five years. From: Travis Mack Sent: Monday, September 25, 2023 12:22 PM To: Discussion list on issues relating to automatic fire sprinklers Subject: [Sprinklerforum] Re: Standpipe PRV Question That makes total sense and I can see where

[Sprinklerforum] Re: Standpipe PRV Question

2023-09-25 Thread Anthony Carrizosa
design pressures if the city supply where to drop for any reason then the secondary pump comes on and supplies the needed incoming pressure to this primary pump. Anthony Carrizosa Project Manager | Fire Protection 7855 S 206th St Kent, WA 98032 Cell: 206-679-5283 | Office Dir: 253-341-4593

[Sprinklerforum] Re: Very Large Dry pipe Systems

2023-08-29 Thread Anthony Carrizosa
Look into the QRS system from Tyco, it’s an electronic quick opening device. we have used this system on some very large dry systems and it worked very well. Each panel can control up to four dry systems so you’ll need three panels. Anthony Carrizosa Project Manager | Fire Protection 7855 S

[Sprinklerforum] Re: Roof Drain / Sprinkler Drain

2023-08-23 Thread Anthony Carrizosa
And John with the forward flow requirements being enforced by more and more jurisdictions then this full flow capability becomes essential. Anthony Carrizosa Project Manager | Fire Protection 7855 S 206th St Kent, WA 98032 Cell: 206-679-5283 | Office Dir: 253-341-4593 [cid:image001.jpg@01D9D5A3

[Sprinklerforum] Re: [EXTERNAL] Re: Fire Pump Drains

2023-05-11 Thread Anthony Carrizosa
John NFPA 25 -2020 13.2.3 MAIN DRAIN TEST. Shall be conducted annually for each water supply lead-in to a building. 13.2.3.1 Where the lead-in to a building supplies a header or manifold serving multiple systems, A single main drain test shall be permitted. Of course as you state the AHJ must be

[Sprinklerforum] Re: Fire Pump Drains

2023-05-11 Thread Anthony Carrizosa
Of note: NFPA 25 -2020 A13.2.3 states that if on a fire pump which is tested annually it not required to perform a main drain test since the water supply is tested through the fire pump. So tis main drain would just be used to drain the wet system for any repairs needed. From: John Denhardt

[Sprinklerforum] Re: Older dry pipe sprinkler systems

2023-05-03 Thread Anthony Carrizosa
NFPA 25-2020 [cid:image001.png@01D97D96.8102C8B0] From: tston...@comcast.net Sent: Wednesday, May 3, 2023 7:57 AM To: sprinklerforum@lists.firesprinkler.org Subject: [Sprinklerforum] Older dry pipe sprinkler systems Is there an acceptable leakage rate for an existing dry pipe system? A

[Sprinklerforum] Re: Definition of Volume

2023-02-01 Thread Anthony Carrizosa
Rieve Fire Protection From: Anthony Carrizosa mailto:anth...@archerconstruction.com>> Sent: Wednesday, February 1, 2023 11:51 AM To: Discussion list on issues relating to automatic fire sprinklers mailto:sprinklerforum@lists.firesprinkler.org>> Subject: [Sprinklerforum] Re: Definition of

[Sprinklerforum] Re: Definition of Volume

2023-02-01 Thread Anthony Carrizosa
% by Volume. Then (6) Exposed only refers to weight.. I think they are making it clear that if in a carton or wooden crate then it’s the volume of plastic within the box, if exposed then use the weight of the product since there is no volume to determine. Hope this helps. Anthony Carrizosa Project

[Sprinklerforum] Re: Definition of Volume

2023-02-01 Thread Anthony Carrizosa
, if exposed then use the weight of the product since there is no volume to determine. Hope this helps. Anthony Carrizosa Project Manager | Fire Protection 7855 S 206th St Kent, WA 98032 Cell: 206-679-5283 | Office Dir: 253-341-4593 [cid:image001.jpg@01D93618.3510D1B0] https://archerconstruction.com

[Sprinklerforum] Re: Class I commodity in bubble pack

2023-01-25 Thread Anthony Carrizosa
See the definition of encapsulation in the Appendix of NFPA 13-19 [cid:image001.png@01D93085.72A463E0] From: Fpdcdesign Sent: Wednesday, January 25, 2023 4:59 AM To: Discussion list on issues relating to automatic fire sprinklers Subject: [Sprinklerforum] Class I commodity in bubble pack I

[Sprinklerforum] Re: 2021 IBC

2023-01-20 Thread Anthony Carrizosa
of the IFC 108.1 Maintenance. Anthony Carrizosa Project Manager | Fire Protection 7855 S 206th St Kent, WA 98032 Cell: 206-679-5283 | Office Dir: 253-341-4593 [cid:image001.jpg@01D92CB1.40A4DC80] https://archerconstruction.com<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2farcherconstruction.

[Sprinklerforum] Re: 2021 IBC

2023-01-20 Thread Anthony Carrizosa
It is in the IFC not IBC, you can view it online for free.. states NFPA 25-2020 Edition. Anthony Carrizosa Project Manager | Fire Protection 7855 S 206th St Kent, WA 98032 Cell: 206-679-5283 | Office Dir: 253-341-4593 [cid:image001.jpg@01D92CA7.5F114C30] https://archerconstruction.com<ht

[Sprinklerforum] Re: Spray Booth-Cellophane Covers

2022-11-29 Thread Anthony Carrizosa
Party stores usually have them, for small candy bags. They sell them in packs so you'l have a small stock to use. From: Taylor Schumacher Sent: Tuesday, November 29, 2022 6:05 AM To: 'sprinklerforum@lists.firesprinkler.org' Subject: [Sprinklerforum] Spray Booth-Cellophane Covers We all

[Sprinklerforum] Re: ESFR Dead Horse

2022-11-02 Thread Anthony Carrizosa
Well we all learned something today as I always thought that if you where in each channel then your good? Looks like the minimum and maximum spacing requirements still apply. Until we get the 2022 edition of NFPA 13. Thanks for everyone’s input. Anthony Carrizosa Project Manager | Fire

[Sprinklerforum] Re: ESFR Dead Horse

2022-11-02 Thread Anthony Carrizosa
Brian I am glad you brought this up.. I had previously thought that if in each pocket were good. I didn’t see the next paragraph that states the minimum and maximum spacing rules still apply. Thanks again. Anthony Carrizosa Project Manager | Fire Protection 7855 S 206th St Kent, WA 98032 Cell

[Sprinklerforum] Re: ESFR Dead Horse

2022-11-02 Thread Anthony Carrizosa
then the requirements for minimum sprinkler spacing per 14.2.9.4..shall not apply” I am glad this was brought up as I have always thought that if in each bay/channel we are good.. Anthony Carrizosa Project Manager | Fire Protection 7855 S 206th St Kent, WA 98032 Cell: 206-679-5283 | Office Dir: 253-341-4593

[Sprinklerforum] Re: ESFR Dead Horse

2022-11-02 Thread Anthony Carrizosa
Horse If you look in the 2022 edition of NFPA 13 or in the most current FM9-8 and 2-0, this construction method is addressed. Matt From: Anthony Carrizosa mailto:anth...@archerconstruction.com>> Sent: Wednesday, November 02, 2022 11:27 AM To: Discussion list on issues relating to a

[Sprinklerforum] Re: ESFR Dead Horse

2022-11-02 Thread Anthony Carrizosa
Oh Boy this gets more complicated as you look closer. 8.4.6.3.2 the minimum spacing and area of coverage must also comply with 8.12.2 and 8.12.3. From: Anthony Carrizosa Sent: Wednesday, November 2, 2022 9:23 AM To: Discussion list on issues relating to automatic fire sprinklers Subject

[Sprinklerforum] Re: ESFR Dead Horse

2022-11-02 Thread Anthony Carrizosa
Stonington, CT 860-535-2080 (ofc) 860-554-7054 (fax) 860-608-4559 (cell) On Nov 2, 2022 at 12:11 PM, mailto:anth...@archerconstruction.com>> wrote: Brian See 8.12.4.1.6 Sprinklers in each bay between beams. The beams act as a baffle. Anthony Carrizosa Project Manager | Fire Protection 78

[Sprinklerforum] Re: ESFR Dead Horse

2022-11-02 Thread Anthony Carrizosa
on the heads you are using, some spell it out for you others are basic info. Anthony Carrizosa Project Manager | Fire Protection 7855 S 206th St Kent, WA 98032 Cell: 206-679-5283 | Office Dir: 253-341-4593 [cid:image001.jpg@01D8EE9C.00789140] https://archerconstruction.com<ht

[Sprinklerforum] Re: ESFR Dead Horse

2022-11-02 Thread Anthony Carrizosa
Brian See 8.12.4.1.6 Sprinklers in each bay between beams. The beams act as a baffle. Anthony Carrizosa Project Manager | Fire Protection 7855 S 206th St Kent, WA 98032 Cell: 206-679-5283 | Office Dir: 253-341-4593 [cid:image001.jpg@01D8EE9A.E1AC4F50] https://archerconstruction.com<ht

[Sprinklerforum] Re: Fire pump package weight ?

2022-09-15 Thread Anthony Carrizosa
NIsXIu5cHladNUdrAJCMsxD35KUBWvWx0B=1 To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org<mailto:sprinklerforum-le...@lists.firesprinkler.org> Anthony Carrizosa | Fire Protection Estimator / Project Manager 7855 S 206th St Kent, WA 98032 Cell: 206-679-5283 | Direct: 2

[Sprinklerforum] Re: Intumescent Paint

2022-09-01 Thread Anthony Carrizosa
new problem of exposure to the elements over time. I typically wont agree to it when doing design build of course knowing that the AHJ most likely will shoot it down anyways. Good luck. Anthony Carrizosa Project Manager | Fire Protection 7855 S 206th St Kent, WA 98032 Cell: 206-679-5283 | Office

[Sprinklerforum] Re: Intumescent Paint

2022-09-01 Thread Anthony Carrizosa
According to NFPA 703 NFPA 703 Fire Retardant – Treated Wood. [cid:image001.png@01D8BDD1.70F3F3C0] This cannot be a paint applied after construction, but must be during the wood manufacturing process. Anthony Carrizosa Project Manager | Fire Protection 7855 S 206th St Kent, WA 98032 Cell: 206

[Sprinklerforum] Re: Lithium Ion Battery Manufacturing (not storage)

2022-08-26 Thread Anthony Carrizosa
Mike, I remember looking at the NFPA website and seeing some information on the storage of these batteries and what they said about what type of suppression would be needed. Even for storage they said that a design density similar to common storage commodities was effective. Lithium ion

[Sprinklerforum] Re: WFD In Pump Suction Line

2022-08-05 Thread Anthony Carrizosa
Taylor Every time the jockey pump turns on it will ring the bell? Unless you use a very large retard chamber. From: Taylor Schumacher Sent: Friday, August 5, 2022 8:44 AM To: Discussion list on issues relating to automatic fire sprinklers Subject: [Sprinklerforum] Re: WFD In Pump Suction

[Sprinklerforum] Re: WFD In Pump Suction Line

2022-08-05 Thread Anthony Carrizosa
Taylor, you could show him this section of NFPA 20. NFPA 20 2016 4.15.9* Devices in Suction Piping. 4.15.9.2 The following devices shall be permitted in the suction piping where the following requirements are met: (2) Where the authority having jurisdiction requires positive pressure to be

[Sprinklerforum] Re: WFD In Pump Suction Line

2022-08-05 Thread Anthony Carrizosa
will notice. Anthony Carrizosa Project Manager | Fire Protection 7855 S 206th St Kent, WA 98032 Cell: 206-679-5283 | Office: 253-872-7222 [cid:image001.jpg@01D8A8A1.0C1AE5C0] https://archerconstruction.com<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2farcherconstruction.com%2f=

[Sprinklerforum] Re: Do separate fire areas require sprinkler system to be separated

2022-07-26 Thread Anthony Carrizosa
not required to be separate. Like you said earlier we do this within stairs when protecting the landings or below the lowest landing, we feed these sprinklers from the floor at that level. Thanks again for your input. Anthony Carrizosa Project Manager | Fire Protection 7855 S 206th St Kent, WA

[Sprinklerforum] Re: Do separate fire areas require sprinkler system to be separated

2022-07-26 Thread Anthony Carrizosa
multiple hazards protected by the same system as long as the limitations in square footage of the highest hazard are not exceeded and or the total system area does not exceed the maximum for the lighter hazard. Thanks again for your input. Anthony Carrizosa Project Manager | Fire Protection 7855 S

[Sprinklerforum] Re: Do separate fire areas require sprinkler system to be separated

2022-07-26 Thread Anthony Carrizosa
Yes, Fire Sprinkler protection question. They are asking if the fire sprinkler system also needs to be separate per Fire Area. I know it typically does not have to be separate and our system can span across two different fire areas, we just have to protect our penetrations. Anthony Carrizosa

[Sprinklerforum] Re: Do separate fire areas require sprinkler system to be separated

2022-07-26 Thread Anthony Carrizosa
but they are asking me to confirm. Thanks Anthony Carrizosa Project Manager | Fire Protection 7855 S 206th St Kent, WA 98032 Cell: 206-679-5283 | Office: 253-872-7222 [cid:image001.jpg@01D8A0CC.A76FBC80] https://archerconstruction.com<https://linkprotect.cudasvc.com/url?a=https%3a

[Sprinklerforum] Do separate fire areas require sprinkler system to be separated

2022-07-26 Thread Anthony Carrizosa
on this? Anthony Carrizosa Project Manager | Fire Protection 7855 S 206th St Kent, WA 98032 Cell: 206-679-5283 | Office: 253-872-7222 [cid:image001.jpg@01D8A0CA.4D068320] https://archerconstruction.com<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2farcherconstruction.com%2f=

[Sprinklerforum] Re: K3.9 replacements

2022-07-25 Thread Anthony Carrizosa
-factor (± 5 percent) shall be permitted to be used provided the currently listed coverage area for the replacement sprinkler is not exceeded. You could go with a 4.0 and be within the 5 % and not have to recalculate the system. Anthony Carrizosa Project Manager | Fire Protection 7855 S 206th St

[Sprinklerforum] Re: Sprinkler protection in above-ceiling concealed spaces

2022-04-11 Thread Anthony Carrizosa
by Bob Caputo not to share copyrighted material. Good luck on your design Anthony Carrizosa Project Manager | Fire Protection 7855 S 206th St Kent, WA 98032 Cell: 206-679-5283 | Office: 253-872-7222 [cid:image001.jpg@01D84DB1.EB6F7510] https://archerconstruction.com<https://linkprotect.cudasvc.

[Sprinklerforum] Re: Water Curtain Hydraulic Calculation

2022-03-21 Thread Anthony Carrizosa
. From: Sergio Braga Sent: Monday, March 21, 2022 2:53 PM To: Anthony Carrizosa Cc: Brett Peters ; sprinklerforum@lists.firesprinkler.org Subject: Re: [Sprinklerforum] Re: Water Curtain Hydraulic Calculation Anthony, I am in NYC, the NYC BC doesn't include the commercial kitchens in the same

[Sprinklerforum] Re: Water Curtain Hydraulic Calculation

2022-03-21 Thread Anthony Carrizosa
Segio, Why do you need a fire separation? Both the dinning and Kitchen areas are the same Occupancy IBC-2018. 303.3 Assembly Group A-2. Group A-2 occupancy includes assembly uses intended for food and/or drink consumption including, but not limited to: . Restaurants, cafeterias and similar

RE: Display vs. storage

2021-10-28 Thread Anthony Carrizosa via Sprinklerforum
look at the specific hazard and design a system that will provide the proper sprinkler protection from chapters 12 - 17 of NFPA 13. Just my two cents.. Anthony Carrizosa Project Manager | Fire Protection 7855 S 206th St Kent, WA 98032 Cell: 206-679-5283 | Office: 253-872-7222 https

RE: Sprinklerforum Digest, Vol 59, Issue 4

2018-02-13 Thread Anthony Carrizosa
uot;residential sprinklers are permitted to be used in dwelling units" not necessarily required in NFPA 13 designed systems. Anthony Carrizosa  OFFICE: 253-872-7222 Cell: 206-679-5283 Fire Protection Division -Original Message- From: Sprinklerforum [mailto

RE: Sprinkler forum Digest, Vol 59, Issue 2

2018-02-05 Thread Anthony Carrizosa
. I don’t have any pictures but I know I have seen one somewhere. Anthony Carrizosa  OFFICE: 253-872-7222 Fire Protection Division -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of sprinklerforum-requ...@lists.firesprinkle

RE: Saw-Tooth Ceilings

2017-11-30 Thread Anthony Carrizosa
Michael Look at NFPA 13 section 8.6.4.1.1.3 B Anthony Carrizosa OFFICE: 253-872-7222 Cell: 206-679-5283 Fire Protection Division From: Michael Hill [mailto:mi...@phoenixfp.net] Sent: Thursday, November 30, 2017 8:33 AM To: sprinklerforum

RE: Sprinklerforum Digest, Vol 56, Issue 18

2017-11-17 Thread Anthony Carrizosa
). The piping is sized by Hydraulic calculations and is based on the required flow rate. Anthony Carrizosa ARCHER CONSTRUCTION,INC. Fire Protection Division OFFICE: 253-872-7222 Cell: 206-679-5283 -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun

RE: Racking Question

2017-08-25 Thread Anthony Carrizosa
Then you are in NFPA 30. As Flammable combustible liquids are not covered in NFPA 13. Anthony Carrizosa Fire Protection Division OFFICE: 253-872-7222 Cell: 206-679-5283 cid:703393518@19082013-11F7 From: James Crawford [mailto:jcrawf...@phaserfire.ca] Sent: Friday

RE: Racking Question

2017-08-25 Thread Anthony Carrizosa
e is but I would assume less than 12'. Perhaps you will find your storage arrangement in chapter 14. Good Luck. Anthony Carrizosa Fire Protection Division OFFICE: 253-872-7222 Cell: 206-679-5283 cid:703393518@19082013-11F7 From: James Crawford [mailto:jcrawf...@phaserfire

RE: Looking For Opinions

2017-07-07 Thread Anthony Carrizosa
sprinkler shall not be more than 6 ft (1.8 m) from the wall or obstruction. Hope this helps. Anthony Carrizosa Fire Protection Division OFFICE: 253-872-7222 Cell: 206-679-5283 cid:703393518@19082013-11F7 From: Brian Harris [mailto:bhar...@bvssystemsinc.com] Sent: Friday, July 07