You may also want to look into putting a combination of roof sprinklers and
in-rack sprinklers to accomplish this.
Are there smoke and heat vents in the building? If so and a roof height of 27'
or lower, you could do the special design of .60/2000 with standard heads.
Have a good day.
Anthony
Per NFPA 25 only automatic standpipes are required to be flow tested. Why is
this one being tested?
From: Brian Harris
Sent: Monday, July 1, 2024 7:57 AM
To: Discussion list on issues relating to automatic fire sprinklers
Subject: [Sprinklerforum] Re: Water Tank for Standpipe
Mostly volume,
with the
FM to discuss this in advance as NFPA 14 states.
Anthony Carrizosa
Project Manager | Fire Protection
7855 S 206th St Kent, WA 98032
Cell: 206-679-5283 | Office Dir: 253-341-4593
[cid:image001.jpg@01DA868C.6225F890]
https://archerconstruction.com<https://linkprotect.cudasvc.com/
I think Don kern hit it on the head, Unless it’s a high rise then a manual
standpipe system is all that’s needed.
Anthony Carrizosa
Project Manager | Fire Protection
7855 S 206th St Kent, WA 98032
Cell: 206-679-5283 | Office Dir: 253-341-4593
[cid:image001.jpg@01DA85A5.421C2610]
https
We do backflows and risers in stairs all the time, typically below the
intermediate landing, as long as it’s a minimum 1 hour construction then it has
been ok with most jurisdictions. Remember standpipes and floor controls are
typically in stairs as a standard.
Anthony Carrizosa
Project
Brian,
You could use a non-ESFR sprinkler like the Tyco K17-231 standard response,
standard coverage sprinkler. It comes in both upright and pendent. Area density
method with a .60/2000.
Then the rules for ESFR do not apply.
Anthony Carrizosa
Project Manager | Fire Protection
7855 S 206th St
Yes Steve, you made us all think and use our brains today..
Anthony Carrizosa
Project Manager | Fire Protection
7855 S 206th St Kent, WA 98032
Cell: 206-679-5283 | Office Dir: 253-341-4593
[cid:image001.jpg@01DA7619.DC46AC10]
https://archerconstruction.com<https://linkprotect.cudasvc.com/
Well summed up Ken..
Anthony Carrizosa
Project Manager | Fire Protection
7855 S 206th St Kent, WA 98032
Cell: 206-679-5283 | Office Dir: 253-341-4593
[cid:image001.jpg@01DA7619.39384560]
https://archerconstruction.com<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2farcherconstruction.com%2
I can't seem to find the required minimum clearance around an FDC.
I could swear I seen it in the past and believe it's 36" but can't seem to find
it now?
Anthony Carrizosa | Fire Protection Estimator / Project Manager
7855 S 206th St Kent, WA 98032
Direct: 253-341-4593 | Mobile: 206-679
Derik,
NFPA 25 states flow tests 6.3.1 Shall be conducted every 5 years on all
automatic standpipe systems.. your system is not automatic but manual. Since it
is under water pressure at all times no need for a hydro test either.
Anthony Carrizosa
Project Manager | Fire Protection
7855 S 206th
there..
Anthony Carrizosa
Project Manager | Fire Protection
7855 S 206th St Kent, WA 98032
Cell: 206-679-5283 | Office Dir: 253-341-4593
[cid:image002.jpg@01DA5B5F.DFD12F60]
https://archerconstruction.com<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2farcherconstruction.com%2f=
with 8.6.5.1.2
(3) Installed in each bay of obstructed construction, with the deflectors
located a minimum of 1 in. (25 mm) and a maximum of 12 in. (300 mm) below the
ceiling
Anthony Carrizosa
Project Manager | Fire Protection
7855 S 206th St Kent, WA 98032
Cell: 206-679-5283 | Office Dir: 253-341-4593
.
Anthony Carrizosa
Project Manager | Fire Protection
7855 S 206th St Kent, WA 98032
Cell: 206-679-5283 | Office Dir: 253-341-4593
[cid:image001.jpg@01DA5A75.025354A0]
https://archerconstruction.com<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2farcherconstruction.com%2f=
Todd
The Appendix states every time you drain and refill the system you must release
the trapped air, so by definition a system has a control valve, Water flow
switch and a drain. thus each floor can be independently shut off and drained
then refilled, thus they would need an air vent.
From:
of
a system.
I agree that you would need an air vent for each floor.
Anthony Carrizosa
Project Manager | Fire Protection
7855 S 206th St Kent, WA 98032
Cell: 206-679-5283 | Office Dir: 253-341-4593
[cid:image001.jpg@01D9FA91.092E9530]
https://archerconstruction.com<https://linkprotect.cudasvc.
Very good point..
Anthony Carrizosa
Project Manager | Fire Protection
7855 S 206th St Kent, WA 98032
Cell: 206-679-5283 | Office Dir: 253-341-4593
[cid:image001.jpg@01D9EFB2.8A0830B0]
https://archerconstruction.com<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2farcherconstruction.com%2f=
pressure
at the suction side of the fire pump supplying the
automatic sprinkler system.
This is describing how the piping arrangement should be for this tank and pump.
Which is exactly how we have done it here.
Anthony Carrizosa
Project Manager | Fire Protection
7855 S 206th St Kent, WA 98032
Cell: 206
Per NFPA 25 Tank internal inspection is required every five years.
From: Travis Mack
Sent: Monday, September 25, 2023 12:22 PM
To: Discussion list on issues relating to automatic fire sprinklers
Subject: [Sprinklerforum] Re: Standpipe PRV Question
That makes total sense and I can see where
design pressures if the city
supply where to drop for any reason then the secondary pump comes on and
supplies the needed incoming pressure to this primary pump.
Anthony Carrizosa
Project Manager | Fire Protection
7855 S 206th St Kent, WA 98032
Cell: 206-679-5283 | Office Dir: 253-341-4593
Look into the QRS system from Tyco, it’s an electronic quick opening device. we
have used this system on some very large dry systems and it worked very well.
Each panel can control up to four dry systems so you’ll need three panels.
Anthony Carrizosa
Project Manager | Fire Protection
7855 S
And John with the forward flow requirements being enforced by more and more
jurisdictions then this full flow capability becomes essential.
Anthony Carrizosa
Project Manager | Fire Protection
7855 S 206th St Kent, WA 98032
Cell: 206-679-5283 | Office Dir: 253-341-4593
[cid:image001.jpg@01D9D5A3
John
NFPA 25 -2020
13.2.3 MAIN DRAIN TEST. Shall be conducted annually for each water supply
lead-in to a building.
13.2.3.1 Where the lead-in to a building supplies a header or manifold serving
multiple systems, A single main drain test shall be permitted.
Of course as you state the AHJ must be
Of note: NFPA 25 -2020 A13.2.3 states that if on a fire pump which is tested
annually it not required to perform a main drain test since the water supply is
tested through the fire pump. So tis main drain would just be used to drain the
wet system for any repairs needed.
From: John Denhardt
NFPA 25-2020
[cid:image001.png@01D97D96.8102C8B0]
From: tston...@comcast.net
Sent: Wednesday, May 3, 2023 7:57 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: [Sprinklerforum] Older dry pipe sprinkler systems
Is there an acceptable leakage rate for an existing dry pipe system?
A
Rieve Fire Protection
From: Anthony Carrizosa
mailto:anth...@archerconstruction.com>>
Sent: Wednesday, February 1, 2023 11:51 AM
To: Discussion list on issues relating to automatic fire sprinklers
mailto:sprinklerforum@lists.firesprinkler.org>>
Subject: [Sprinklerforum] Re: Definition of
% by Volume.
Then (6) Exposed only refers to weight..
I think they are making it clear that if in a carton or wooden crate then it’s
the volume of plastic within the box, if exposed then use the weight of the
product since there is no volume to determine.
Hope this helps.
Anthony Carrizosa
Project
, if exposed then use the weight of the
product since there is no volume to determine.
Hope this helps.
Anthony Carrizosa
Project Manager | Fire Protection
7855 S 206th St Kent, WA 98032
Cell: 206-679-5283 | Office Dir: 253-341-4593
[cid:image001.jpg@01D93618.3510D1B0]
https://archerconstruction.com
See the definition of encapsulation in the Appendix of NFPA 13-19
[cid:image001.png@01D93085.72A463E0]
From: Fpdcdesign
Sent: Wednesday, January 25, 2023 4:59 AM
To: Discussion list on issues relating to automatic fire sprinklers
Subject: [Sprinklerforum] Class I commodity in bubble pack
I
of the IFC 108.1
Maintenance.
Anthony Carrizosa
Project Manager | Fire Protection
7855 S 206th St Kent, WA 98032
Cell: 206-679-5283 | Office Dir: 253-341-4593
[cid:image001.jpg@01D92CB1.40A4DC80]
https://archerconstruction.com<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2farcherconstruction.
It is in the IFC not IBC, you can view it online for free.. states NFPA 25-2020
Edition.
Anthony Carrizosa
Project Manager | Fire Protection
7855 S 206th St Kent, WA 98032
Cell: 206-679-5283 | Office Dir: 253-341-4593
[cid:image001.jpg@01D92CA7.5F114C30]
https://archerconstruction.com<ht
Party stores usually have them, for small candy bags. They sell them in packs
so you'l have a small stock to use.
From: Taylor Schumacher
Sent: Tuesday, November 29, 2022 6:05 AM
To: 'sprinklerforum@lists.firesprinkler.org'
Subject: [Sprinklerforum] Spray Booth-Cellophane Covers
We all
Well we all learned something today as I always thought that if you where in
each channel then your good? Looks like the minimum and maximum spacing
requirements still apply. Until we get the 2022 edition of NFPA 13.
Thanks for everyone’s input.
Anthony Carrizosa
Project Manager | Fire
Brian
I am glad you brought this up.. I had previously thought that if in each pocket
were good.
I didn’t see the next paragraph that states the minimum and maximum spacing
rules still apply.
Thanks again.
Anthony Carrizosa
Project Manager | Fire Protection
7855 S 206th St Kent, WA 98032
Cell
then the requirements for minimum sprinkler spacing per
14.2.9.4..shall not apply”
I am glad this was brought up as I have always thought that if in each
bay/channel we are good..
Anthony Carrizosa
Project Manager | Fire Protection
7855 S 206th St Kent, WA 98032
Cell: 206-679-5283 | Office Dir: 253-341-4593
Horse
If you look in the 2022 edition of NFPA 13 or in the most current FM9-8 and
2-0, this construction method is addressed.
Matt
From: Anthony Carrizosa
mailto:anth...@archerconstruction.com>>
Sent: Wednesday, November 02, 2022 11:27 AM
To: Discussion list on issues relating to a
Oh Boy this gets more complicated as you look closer.
8.4.6.3.2 the minimum spacing and area of coverage must also comply with 8.12.2
and 8.12.3.
From: Anthony Carrizosa
Sent: Wednesday, November 2, 2022 9:23 AM
To: Discussion list on issues relating to automatic fire sprinklers
Subject
Stonington, CT
860-535-2080 (ofc)
860-554-7054 (fax)
860-608-4559 (cell)
On Nov 2, 2022 at 12:11 PM, mailto:anth...@archerconstruction.com>> wrote:
Brian
See 8.12.4.1.6 Sprinklers in each bay between beams. The beams act as a baffle.
Anthony Carrizosa
Project Manager | Fire Protection
78
on the heads you are using, some
spell it out for you others are basic info.
Anthony Carrizosa
Project Manager | Fire Protection
7855 S 206th St Kent, WA 98032
Cell: 206-679-5283 | Office Dir: 253-341-4593
[cid:image001.jpg@01D8EE9C.00789140]
https://archerconstruction.com<ht
Brian
See 8.12.4.1.6 Sprinklers in each bay between beams. The beams act as a baffle.
Anthony Carrizosa
Project Manager | Fire Protection
7855 S 206th St Kent, WA 98032
Cell: 206-679-5283 | Office Dir: 253-341-4593
[cid:image001.jpg@01D8EE9A.E1AC4F50]
https://archerconstruction.com<ht
NIsXIu5cHladNUdrAJCMsxD35KUBWvWx0B=1
To unsubscribe send an email to
sprinklerforum-le...@lists.firesprinkler.org<mailto:sprinklerforum-le...@lists.firesprinkler.org>
Anthony Carrizosa | Fire Protection Estimator / Project Manager
7855 S 206th St Kent, WA 98032
Cell: 206-679-5283 | Direct: 2
new problem of exposure to the elements over time.
I typically wont agree to it when doing design build of course knowing that the
AHJ most likely will shoot it down anyways.
Good luck.
Anthony Carrizosa
Project Manager | Fire Protection
7855 S 206th St Kent, WA 98032
Cell: 206-679-5283 | Office
According to NFPA 703 NFPA 703 Fire Retardant – Treated Wood.
[cid:image001.png@01D8BDD1.70F3F3C0]
This cannot be a paint applied after construction, but must be during the wood
manufacturing process.
Anthony Carrizosa
Project Manager | Fire Protection
7855 S 206th St Kent, WA 98032
Cell: 206
Mike,
I remember looking at the NFPA website and seeing some information on the
storage of these batteries and what they said about what type of suppression
would be needed. Even for storage they said that a design density similar to
common storage commodities was effective.
Lithium ion
Taylor
Every time the jockey pump turns on it will ring the bell? Unless you use a
very large retard chamber.
From: Taylor Schumacher
Sent: Friday, August 5, 2022 8:44 AM
To: Discussion list on issues relating to automatic fire sprinklers
Subject: [Sprinklerforum] Re: WFD In Pump Suction
Taylor, you could show him this section of NFPA 20.
NFPA 20 2016
4.15.9* Devices in Suction Piping.
4.15.9.2 The following devices shall be permitted in the
suction piping where the following requirements are met:
(2) Where the authority having jurisdiction requires positive
pressure to be
will notice.
Anthony Carrizosa
Project Manager | Fire Protection
7855 S 206th St Kent, WA 98032
Cell: 206-679-5283 | Office: 253-872-7222
[cid:image001.jpg@01D8A8A1.0C1AE5C0]
https://archerconstruction.com<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2farcherconstruction.com%2f=
not required
to be separate.
Like you said earlier we do this within stairs when protecting the landings or
below the lowest landing, we feed these sprinklers from the floor at that level.
Thanks again for your input.
Anthony Carrizosa
Project Manager | Fire Protection
7855 S 206th St Kent, WA
multiple
hazards protected by the same system as long as the limitations in square
footage of the highest hazard are not exceeded and or the total system area
does not exceed the maximum for the lighter hazard.
Thanks again for your input.
Anthony Carrizosa
Project Manager | Fire Protection
7855 S
Yes, Fire Sprinkler protection question. They are asking if the fire sprinkler
system also needs to be separate per Fire Area. I know it typically does not
have to be separate and our system can span across two different fire areas, we
just have to protect our penetrations.
Anthony Carrizosa
but
they are asking me to confirm.
Thanks
Anthony Carrizosa
Project Manager | Fire Protection
7855 S 206th St Kent, WA 98032
Cell: 206-679-5283 | Office: 253-872-7222
[cid:image001.jpg@01D8A0CC.A76FBC80]
https://archerconstruction.com<https://linkprotect.cudasvc.com/url?a=https%3a
on this?
Anthony Carrizosa
Project Manager | Fire Protection
7855 S 206th St Kent, WA 98032
Cell: 206-679-5283 | Office: 253-872-7222
[cid:image001.jpg@01D8A0CA.4D068320]
https://archerconstruction.com<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2farcherconstruction.com%2f=
-factor (± 5
percent) shall be permitted to be used provided the currently listed coverage
area for the replacement sprinkler is not exceeded.
You could go with a 4.0 and be within the 5 % and not have to recalculate the
system.
Anthony Carrizosa
Project Manager | Fire Protection
7855 S 206th St
by Bob
Caputo not to share copyrighted material.
Good luck on your design
Anthony Carrizosa
Project Manager | Fire Protection
7855 S 206th St Kent, WA 98032
Cell: 206-679-5283 | Office: 253-872-7222
[cid:image001.jpg@01D84DB1.EB6F7510]
https://archerconstruction.com<https://linkprotect.cudasvc.
.
From: Sergio Braga
Sent: Monday, March 21, 2022 2:53 PM
To: Anthony Carrizosa
Cc: Brett Peters ; sprinklerforum@lists.firesprinkler.org
Subject: Re: [Sprinklerforum] Re: Water Curtain Hydraulic Calculation
Anthony,
I am in NYC, the NYC BC doesn't include the commercial kitchens in the same
Segio,
Why do you need a fire separation? Both the dinning and Kitchen areas are the
same Occupancy
IBC-2018. 303.3 Assembly Group A-2. Group A-2 occupancy includes
assembly uses intended for food and/or drink consumption
including, but not limited to:
.
Restaurants, cafeterias and similar
look at the specific
hazard and design a system that will provide the proper sprinkler protection
from chapters 12 - 17 of NFPA 13.
Just my two cents..
Anthony Carrizosa
Project Manager | Fire Protection
7855 S 206th St Kent, WA 98032
Cell: 206-679-5283 | Office: 253-872-7222
https
uot;residential sprinklers are permitted to be used in
dwelling units" not necessarily required in NFPA 13 designed systems.
Anthony Carrizosa
OFFICE: 253-872-7222
Cell: 206-679-5283
Fire Protection Division
-Original Message-
From: Sprinklerforum [mailto
.
I dont have any pictures but I know I have seen one somewhere.
Anthony Carrizosa
OFFICE: 253-872-7222
Fire Protection Division
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of sprinklerforum-requ...@lists.firesprinkle
Michael
Look at NFPA 13 section 8.6.4.1.1.3 B
Anthony Carrizosa
OFFICE: 253-872-7222
Cell: 206-679-5283
Fire Protection Division
From: Michael Hill [mailto:mi...@phoenixfp.net]
Sent: Thursday, November 30, 2017 8:33 AM
To: sprinklerforum
).
The piping is sized by Hydraulic calculations and is based on the required flow
rate.
Anthony Carrizosa
ARCHER CONSTRUCTION,INC.
Fire Protection Division
OFFICE: 253-872-7222
Cell: 206-679-5283
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun
Then you are in NFPA 30. As Flammable combustible liquids are not covered in
NFPA 13.
Anthony Carrizosa
Fire Protection Division
OFFICE: 253-872-7222
Cell: 206-679-5283
cid:703393518@19082013-11F7
From: James Crawford [mailto:jcrawf...@phaserfire.ca]
Sent: Friday
e is but I would
assume less than 12'.
Perhaps you will find your storage arrangement in chapter 14. Good Luck.
Anthony Carrizosa
Fire Protection Division
OFFICE: 253-872-7222
Cell: 206-679-5283
cid:703393518@19082013-11F7
From: James Crawford [mailto:jcrawf...@phaserfire
sprinkler shall not be more than 6
ft (1.8 m) from the wall or obstruction.
Hope this helps.
Anthony Carrizosa
Fire Protection Division
OFFICE: 253-872-7222
Cell: 206-679-5283
cid:703393518@19082013-11F7
From: Brian Harris [mailto:bhar...@bvssystemsinc.com]
Sent: Friday, July 07