RE: swimming pool

2022-02-04 Thread Kyle.Montgomery via Sprinklerforum
We should really start a "Reasonable AHJ of the Year" award. I nominate that guy. -Kyle M -Original Message- From: Sprinklerforum On Behalf Of Matt Grise via Sprinklerforum Sent: Friday, February 4, 2022 1:27 PM To: sprinklerforum@lists.firesprinkler.org Cc: Matt Grise Subject: [EXTER

RE: question about Storage height

2022-01-26 Thread Kyle.Montgomery via Sprinklerforum
Yeah, but the commodity is really the plastic container, right? Is the open-top container/tote still an issue from code standpoint if it's only ever on the lowest level? I thought the real problem with open-top containers that catch water was when they are above ground level. In this case, the

RE: [External]RE: Exposed CPVC pipe and residential upright sprinklers

2022-01-21 Thread Kyle.Montgomery via Sprinklerforum
SHOULD or SHALL? Mwahahahaha... -Original Message- From: Sprinklerforum On Behalf Of Dewayne Martinez via Sprinklerforum Sent: Friday, January 21, 2022 2:17 PM To: sprinklerforum@lists.firesprinkler.org Cc: Dewayne Martinez Subject: [EXTERNAL] RE: [External]RE: Exposed CPVC pipe and re

RE: ESFR obstruction shift

2022-01-18 Thread Kyle.Montgomery via Sprinklerforum
inkler as having its own operational area, but that concept is not normally accepted and has been shot down here without discussion. Allan Seidel > On Jan 18, 2022, at 10:50 AM, Kyle.Montgomery via Sprinklerforum > wrote: > > Matt, > > I haven't dealt with that

RE: ESFR obstruction shift

2022-01-18 Thread Kyle.Montgomery via Sprinklerforum
Matt, I haven't dealt with that situation in real life, but have in theory had several conversations about it. I am in agreement with you that this should be allowable per the code language. You never exceed 110 s.f. and the average ACTUAL FLOOR AREA (not SxL) does not exceed 100 s.f. -Kyle M

RE: [EXTERNAL] Re: Food trucks inside a building

2022-01-14 Thread Kyle.Montgomery via Sprinklerforum
It's always been my understanding that the different hazard classifications are based upon the fuel load of a potential fire, not the likelihood that there will be a fire. So whether there is a stove in operation or not shouldn’t really change the hazard. So you come back to fuel load, which is

RE: ESFR - Minimum Remote Area Size

2021-12-29 Thread Kyle.Montgomery via Sprinklerforum
t looking for some reassurance (or rebuke) when it comes to ESFR. -Kyle M -Original Message- From: Sprinklerforum On Behalf Of Kyle.Montgomery via Sprinklerforum Sent: Wednesday, December 29, 2021 12:41 PM To: sprinklerforum@lists.firesprinkler.org Cc: Kyle.Montgomery ; Mike Hairfield

RE: ESFR - Minimum Remote Area Size

2021-12-29 Thread Kyle.Montgomery via Sprinklerforum
> On Dec 29, 2021, at 2:11 PM, Kyle.Montgomery via Sprinklerforum > wrote: > > I'm dealing with an existing concrete tee building that the owner wants to > retrofit with an ESFR system. Heads will be closely spaced due to the > obstruction caused by the tees; 5-foot on ce

ESFR - Minimum Remote Area Size

2021-12-29 Thread Kyle.Montgomery via Sprinklerforum
I'm dealing with an existing concrete tee building that the owner wants to retrofit with an ESFR system. Heads will be closely spaced due to the obstruction caused by the tees; 5-foot on center. Does NFPA 13 have a minimum remote area size, or is it just 12 heads? -Kyle M _

RE: [EXTERNAL] Re: Mixing ESFR Sprinklers

2021-12-28 Thread Kyle.Montgomery via Sprinklerforum
How do you guys calc these systems? Just the K22 section and the K17 section separately? Or a combo? I think there are situations where having one line of K17s (at 52 psi) in your remote area would be the "worst-case" scenario because that 52 psi would drive some overflow in the two lines of K22

RE: Shoe store complications

2021-11-16 Thread Kyle.Montgomery via Sprinklerforum
I would assume that there are tons of these that exist with OH2 sprinkler designs. Are there any examples of fires in any of those and information about whether the fire was controlled or overwhelmed the sprinklers? If the theory says it should be protected like Group A plastics, but the history

RE: mixing EC sprinks with SC sprinks

2021-10-13 Thread Kyle.Montgomery via Sprinklerforum
This is actually a really interesting question, I think. My opinion would be to calculate the systems as standard response (no quick-response reduction) but install QR sprinklers. I'm not sure I can justify that, just kind of my gut feeling. -Kyle M -Original Message- From: Sprinklerfo

RE: [EXTERNAL] Definitions

2021-09-09 Thread Kyle.Montgomery via Sprinklerforum
That's the sole purpose of a draft curtain, so it better be acceptable for that use. In fact, I think your question is more directly addressed in 12.3(2) where it says the requirements of 12.3(1) shall not apply where the areas are separated by a draft curtain... Maybe I'm not understanding the

RE: [EXTERNAL] Re: Transfer Switches

2021-08-27 Thread Kyle.Montgomery via Sprinklerforum
It's probably worth double-checking the jurisdictional requirements. I've dealt with some jurisdictions that state that if a backup generator is provided, it shall be sized for the fire pump. Their thought process is that if the building can remain operable (lights on, etc.) during a power outag

RE: [EXTERNAL] Re: Fire Pump Backflow

2021-08-27 Thread Kyle.Montgomery via Sprinklerforum
, Aug 26, 2021 at 9:30 AM Kyle.Montgomery via Sprinklerforum mailto:sprinklerforum@lists.firesprinkler.org>> wrote: Joe, Is this a real problem or a theoretical problem? What I mean is, are you still in the design phase or is it actually installed like this and causing a problem? I cou

RE: Fire Pump Backflow

2021-08-26 Thread Kyle.Montgomery via Sprinklerforum
Joe, Is this a real problem or a theoretical problem? What I mean is, are you still in the design phase or is it actually installed like this and causing a problem? I could see there maybe being some trouble initially just getting all the air out of the system. Maybe you could use a valved by

RE: [EXTERNAL] Conveyors

2021-08-17 Thread Kyle.Montgomery via Sprinklerforum
I think it's reasonable if there is no fuel load beneath the conveyors. Probably depends on the configuration and height of the conveyors and if there are any safeguards put in place to ensure there won't be anything place under the conveyors in the future. And by safeguards, I don't necessaril

RE: [EXTERNAL] RE: Solid-Piled and Palletized Storage Arrangement

2021-06-09 Thread Kyle.Montgomery via Sprinklerforum
Of Kyle.Montgomery via Sprinklerforum Sent: Wednesday, June 9, 2021 2:45 PM To: 'sprinklerforum@lists.firesprinkler.org' Cc: Kyle.Montgomery Subject: Solid-Piled and Palletized Storage Arrangement What determines the maximum size (length and width in plan view, not height) and/or min

Solid-Piled and Palletized Storage Arrangement

2021-06-09 Thread Kyle.Montgomery via Sprinklerforum
What determines the maximum size (length and width in plan view, not height) and/or minimum aisle width between storage piles when you've got palletized and solid-piled storage without racks? Or is there no aisle requirement? Everything I'm finding in NFPA 13 with regard to aisles is in relation

RE: [EXTERNAL] Re: CURIOUS

2021-05-21 Thread Kyle.Montgomery via Sprinklerforum
Well, if you send me the price for 5 gallons, I'll crunch the numbers using my secret formula and figure out what one gallon would cost. Sorry, I can't share the formula, too valuable. -Kyle M -Original Message- From: Sprinklerforum On Behalf Of Glen Buelow, Inc. via Sprinklerforum Se

RE: Available Pressure from Fire Water Storage Tank

2021-05-07 Thread Kyle.Montgomery via Sprinklerforum
on of the systems in fighting the fire. You are permitted to use the pumps productive curve at 150% of rated flow and 65% of rated pressure On Fri, May 7, 2021 at 11:13 AM Kyle.Montgomery via Sprinklerforum < sprinklerforum@lists.firesprinkler.org> wrote: > I'm working on a proj

Available Pressure from Fire Water Storage Tank

2021-05-07 Thread Kyle.Montgomery via Sprinklerforum
I'm working on a project where they are adding a new building to an existing campus. There is an existing fire water storage tank and fire pump that serves the site underground fire loop. The new building has a very demanding sprinkler system that just barely exceeds the fire pump's pressure av

RE: UL list concrete anchor

2021-04-20 Thread Kyle.Montgomery via Sprinklerforum
Hilti HDI appears to be UL-Listed for fire protection. -Original Message- From: Sprinklerforum On Behalf Of Sean Lockyer via Sprinklerforum Sent: Tuesday, April 20, 2021 2:48 PM To: sprinklerforum@lists.firesprinkler.org Cc: Sean Lockyer Subject: [EXTERNAL] UL list concrete anchor Is t

RE: [EXTERNAL] Re: Fire pump test through flow meter

2021-04-20 Thread Kyle.Montgomery via Sprinklerforum
Not to beat a moot horse, but one thing to be careful of with flowmeters is to make sure that you have the appropriate amount of straight pipe upstream and downstream of device. There will be a manufacturer's recommendation for these lengths and from my experience it does seem to make a differen

RE: Hose reel FM Approval

2021-04-14 Thread Kyle.Montgomery via Sprinklerforum
Kind of a tangent, but Mike is 100% correct here. FM's authority over the project only goes as far as the owner will allow. That being said, my experience with FM reviewers is that they are pretty accommodating and usually try to make the best decision for their customer (the owner) and underst

RE: Grooved joints in pump suction main

2021-04-06 Thread Kyle.Montgomery via Sprinklerforum
We use grooved all the time as well (like hundreds of times) and I'm not aware of any issue as a result of it. I'm pretty confident that there isn't a rule against it. I've never seen it suck one of the gaskets through the pump, if that's what you're concerned about. -Kyle M -Original Mess

CPVC Drops in Seismic Areas

2021-03-02 Thread Kyle.Montgomery via Sprinklerforum
When installing a CPVC system in a seismic area (area where seismic bracing is required) are there any special considerations needed for the drops to sprinkler heads? In the past, with steel pipe systems we've often utilized flexible sprinkler connections to avoid any concern about differential

RE: [EXTERNAL] Re: Air Venting (2021)

2021-02-18 Thread Kyle.Montgomery via Sprinklerforum
It was my understanding that the committee's approach to requiring air vents was "one is better than none", without wanting to add a ton of extra complexity or expense to the systems. I would assume that the migration away from remote inspector's test valves to the on-riser test-n-drain style he

RE: [EXTERNAL] Noncontinuous obstructions More than 18" down

2021-02-15 Thread Kyle.Montgomery via Sprinklerforum
hat "inspired" the cloud > ceiling criteria at the link below, it is really great information. > > > https://urldefense.proofpoint.com/v2/url?u=https-3A__www.nfpa.org_News > -2Dand-2DResearch_Fire-2Dstatistics-2Dand-2Dreports_Research-2Dreports > _Suppression_Spri

RE: [EXTERNAL] Noncontinuous obstructions More than 18" down

2021-02-12 Thread Kyle.Montgomery via Sprinklerforum
Does "at least 1 inch of space between each panel" mean several feet of space between each panel, or does it mean just a couple of inches. To me, it sounds more like you would have to treat them as grouped obstructions and protect underneath. -Kyle M -Original Message- From: Sprinkler

RE: Bathroom Chase

2021-02-12 Thread Kyle.Montgomery via Sprinklerforum
JwQd9A&m=jC3qHHMvgwCRbErwQQ7RQnCkuh8NtYfpEDpz84KzNVs&s=iR8ULn5L6U6R6y-RgJQkjF7nClm59agtYo7p94AATWs&e= > ce...@sprinkleracademy.com<mailto:ce...@sprinkleracademy.com> ?? OUR STUDENTS SAVE LIVES!! ________ From: Sprinklerforum on behalf of Kyle

RE: Bathroom Chase

2021-02-12 Thread Kyle.Montgomery via Sprinklerforum
Brian, I agree with Skyler here. The picture may not look like what you're doing, but the book would be hard to carry if there were a figure representing every scenario. The intent seems to apply though: You've got a space that is sprinklered only because it is open to an adjacent sprinklered s

RE: [EXTERNAL] RE: Existing Dry System

2021-02-04 Thread Kyle.Montgomery via Sprinklerforum
I think the OP is the AHJ. I just want to say that I think it's cool that a plan reviewer/inspector would come here to get the industries opinion about something like that. We are all on the same team. Looks like Dane beat me to it, but I do think there is a fire separation required. Also, wh

RE: [EXTERNAL] NFPA 13R & NFPA 14

2021-02-04 Thread Kyle.Montgomery via Sprinklerforum
It is if there is no requirement for a standpipe. -Kyle M -Original Message- From: Sprinklerforum On Behalf Of Jose Anibal Castillo via Sprinklerforum Sent: Thursday, February 4, 2021 8:43 AM To: sprinklerforum@lists.firesprinkler.org Cc: Jose Anibal Castillo Subject: [EXTERNAL] NFPA 1

RE: Pan-Type Construction

2021-02-01 Thread Kyle.Montgomery via Sprinklerforum
If it's not a concrete tee, then I don't think you're going to be able to exceed 22" from the deck. -Kyle M -Original Message- From: Sprinklerforum On Behalf Of Dennis Wilson via Sprinklerforum Sent: Monday, February 1, 2021 3:08 PM To: sprinklerforum@lists.firesprinkler.org Cc: Dennis

Fluorine-Free Foams (FFF)

2021-02-01 Thread Kyle.Montgomery via Sprinklerforum
I'm looking at a small hangar (Group II Hangar) that the client is interested in protecting with SFFF (synthetic fluorine-free foam) as opposed to the standard AFFF closed-head system. Are there any standards that address the design criteria for these foams, or does each individual manufacturer

RE: ESFR & Obstruction in Light Hazard

2021-02-01 Thread Kyle.Montgomery via Sprinklerforum
I will counter your "is there a legally defendable argument" with "is there a feasible fire scenario on a tennis court that would not be adequately controlled by marginally obstructed ESFR sprinklers?" I mean, you only need a legally defendable argument if something bad happens, right? I say t

RE: Townhome - Common Areas

2021-01-27 Thread Kyle.Montgomery via Sprinklerforum
Are you saying to just extend the system from the adjacent home into that area to protect it? As opposed to providing another lead-in? Is that an option? -Kyle M -Original Message- From: Sprinklerforum On Behalf Of Steve Leyton via Sprinklerforum Sent: Wednesday, January 27, 2021 8:45

RE: RV Storage

2021-01-08 Thread Kyle.Montgomery via Sprinklerforum
Certainly EH 2 seems like it will get the job done. But for those of you saying that, which commodity drives you to that? For example, if they were three separate buildings: RV Storage Building Boat Storage Building (just parked, not on racks) Storage lockers with height less than 12 feet Would

RE: [EXTERNAL] Re: potential freezing in ESFR system

2020-12-22 Thread Kyle.Montgomery via Sprinklerforum
Matt, I think I agree with all of Bob's points. Likelihood of freeze damage in a drained system should be lower, but in the event of damage the manufacturer would probably use that as an excuse to not be held liable. So there is some probably some risk there. What are they hoping to accomplish

Diesel Fuel Tank - Leak Protection

2020-11-20 Thread Kyle.Montgomery via Sprinklerforum
Our standard for diesel fire pumps is to provide a double-wall fuel tank with leak detection, steel supply and return fuel lines, and of course the connection at the diesel engine is generally a flexible connection provided with the diesel engine from the manufacturer. Anybody doing anything d

RE: Obstruction Clarification

2020-11-12 Thread Kyle.Montgomery via Sprinklerforum
There are specific rules and tables and figures for sprinklers and soffits. I think you should apply those. My understanding is that the normal obstruction rules assume that you could spray onto either side of the obstruction, but that isn't the case with a soffit. -Kyle M -Original Messag

Class IA Flammable Liquids

2020-11-05 Thread Kyle.Montgomery via Sprinklerforum
I'm confused about how to treat Class IA flammable liquids. We've got a cosmetics manufacturer that is moving into a shell building. They are planning a Hazardous Storage room to store the flammable liquids when not in use. The liquids being stored are primarily Class IB solvents, but I'm being

Self-storage Lockers

2020-10-15 Thread Kyle.Montgomery via Sprinklerforum
I'm looking at a project that is your typical self-storage building but with a feature I haven't dealt with before. There are some lockers that are 4' x 4' x 4' cubes stacked on top of each other. Just two high, so there is 128 cubic feet of storage space in a 16 square foot area. It's not reall

Re: [EXTERNAL] Re: Submittal Packages

2020-10-08 Thread Kyle.Montgomery via Sprinklerforum
“... if you don’t want liability, then don’t do construction.” Well said, my friend. -Kyle M > On Oct 8, 2020, at 4:20 PM, Ben Young via Sprinklerforum > wrote: > > As a former contractor who now works for an engineering firm, I think it > sounds like everyone is being a little bit hard hea

RE: 8.17.5 Hose Connections

2020-10-02 Thread Kyle.Montgomery via Sprinklerforum
ael Hill Subject: RE: 8.17.5 Hose Connections Would small hoses at a stage qualify? Mike Hill -Original Message- From: Sprinklerforum On Behalf Of Kyle.Montgomery via Sprinklerforum Sent: Friday, October 2, 2020 3:16 PM To: 'sprinklerforum@lists.firesprinkler.org' Cc

8.17.5 Hose Connections

2020-10-02 Thread Kyle.Montgomery via Sprinklerforum
So, I understand the "Small [1 ½ in. ] Hose Connections" that are discussed in 8.17.5.1. You typically find these in rack storage warehouses. But I'm confused by 8.17.5.2 Hose Connections for Fire Department Use. What hose connections would these be? Or, perhaps I should ask when these hose con

RE: FM 8-9

2020-10-01 Thread Kyle.Montgomery via Sprinklerforum
I think Travis is right, except for ceiling-only protection for ceiling heights over 40 feet. Then you go to 8-9, 2.3.6.9.6, which tells you to use 3-3-3-1 for slopes up to 5 degrees and 4-4-2 for ceiling slopes over 5 degrees. I think this is new for the update in July 2020. -Kyle M -Orig

RE: [EXTERNAL] RE: Hangers for CPVC Pipe going through TGI Joists

2020-09-30 Thread Kyle.Montgomery via Sprinklerforum
Some of you guys mentioned bushings or "other method to prevent chafing". Can we elaborate on that? I've seen bushings used where CPVC is run in a wall and passes through metal studs, but I don't think I've seem them installed in this scenario. Is that really a requirement? -Kyle M -Origin

RE: [EXTERNAL] RE: On/Off Switch in the Electric supply to a Dry Pipe System Air Compressor

2020-09-25 Thread Kyle.Montgomery via Sprinklerforum
e safety standards around air pressure. That doesn’t mean they are evaluating whether you’ll be happy at its ability to drive your impact wrench or charge up your dry system. That’s between the manufacturer and you. Mr. H. Hopper was first to point this out to me. Best. Bruce Verhei > On 09/25/2

RE: On/Off Switch in the Electric supply to a Dry Pipe System Air Compressor

2020-09-25 Thread Kyle.Montgomery via Sprinklerforum
Is there currently a listing criteria for "fire protection air compressors"? I see UL 1450 Standard for Motor-Operated Air Compressors, Vacuum Pumps, and Painting Equipment, but does that include any specifics for fire protection use? -Kyle M -Original Message- From: Sprinklerforum On

RE: Can a Clerestory be considered Skylight?

2020-09-24 Thread Kyle.Montgomery via Sprinklerforum
It may not be a skylight, but I don't see why you couldn't consider it a "similar pocket" to a skylight. >From a practical standpoint, what would be the justification behind requiring >a sprinkler in the pocket in this scenario? -Kyle M -Original Message- From: Sprinklerforum On Beh

RE: 13 R in a single family home

2020-08-13 Thread Kyle.Montgomery via Sprinklerforum
Out of curiosity, where are people building single family homes that 4+ stories? I don't think I've ever seen one. -Kyle M -Original Message- From: Sprinklerforum On Behalf Of Matthew J Willis via Sprinklerforum Sent: Thursday, August 13, 2020 7:27 AM To: sprinklerforum@lists.firesprin

RE: Heads Under Conveyors

2020-08-12 Thread Kyle.Montgomery via Sprinklerforum
I think you're on the right track. For the most part you just treat them like an obstruction. We've been allowed to omit sprinklers from underneath conveyors when they are very low to the ground, since there really isn't anything to protect underneath. What are you concerned about? Kyle Montgo

RE: [EXTERNAL] RE: Pump Suction Pressure (NPSH)

2020-08-06 Thread Kyle.Montgomery via Sprinklerforum
SH) I’d always used 20 psi as minimum pump in;et pressure, unless taking supply from a tank. Everywhere you go in AWWA you run into 20 psi as minimum pressure in the water system. Best. Bruce Verhei > On 08/06/2020 2:54 PM Kyle.Montgomery via Sprinklerforum > wrote: > > >

RE: Pump Suction Pressure (NPSH)

2020-08-06 Thread Kyle.Montgomery via Sprinklerforum
x27;ll probably need to perform a pump test or get water supply information. -Kyle M -Original Message- From: Sprinklerforum On Behalf Of Kyle.Montgomery via Sprinklerforum Sent: Thursday, August 6, 2020 11:57 AM To: sprinklerforum@lists.firesprinkler.org Cc: Kyle.Montgomery ; Matt

RE: Pump Suction Pressure (NPSH)

2020-08-06 Thread Kyle.Montgomery via Sprinklerforum
Let me clarify, the gauge will tell you the static pump suction pressure. You have to use the pump test or a flow test and some math do figure the NPSH. -Original Message- From: Sprinklerforum On Behalf Of Kyle.Montgomery via Sprinklerforum Sent: Thursday, August 6, 2020 11:55 AM To

RE: Pump Suction Pressure (NPSH)

2020-08-06 Thread Kyle.Montgomery via Sprinklerforum
These two options or the last pump test all should satisfactorily answer the question. The "suction pressure" has nothing to do with the pump itself, just the pressure that is available from the city source (or tank or whatever). As mentioned, they generally need to know that so they can calcula

RE: [EXTERNAL] Re: Uprights in non combustible concealed space

2020-06-18 Thread Kyle.Montgomery via Sprinklerforum
So, what would make them non-compliant? Obstructions, like ductwork and stuff? When we’ve gotten similar pushback, it’s been because we’ve had 155-degree heads and the inspector has claimed that they aren’t appropriate for an unconditioned space (we’re working in Phoenix, so it can get unbelieva

RE: [EXTERNAL] RE: Floor area less than required

2020-06-16 Thread Kyle.Montgomery via Sprinklerforum
That sounds correct. It seems strange that your calculation is over-discharging by more than 100% though. Minimum discharge is 90 GPM and you’re discharging over 200 GPM? Do you have like 13 sprinklers jammed into this area? -Kyle M From: Sprinklerforum On Behalf Of Bob Knight via Sprinklerf

RE: [EXTERNAL] Edge of a platform

2020-06-12 Thread Kyle.Montgomery via Sprinklerforum
Since the area inside of the beams is covered by the sprinklers below the mezzanine, could you just call the extension from the beams an obstruction to the overhead system of 12" width or less? Would you need protection under this size of an obstruction? -Kyle M From: Sprinklerforum On Behalf

RE: [EXTERNAL] RE: Unsprinklered Parking Garage

2020-06-11 Thread Kyle.Montgomery via Sprinklerforum
If that’s the case, why not let him decide if he wants them or not, regardless of whether they would be required in a new build? A requirement has little to do with whether or not they provide additional value or safety/protection. -Kyle M From: Sprinklerforum On Behalf Of Ken Haney via Sprin

RE: [EXTERNAL] Re: mattress storage

2020-06-04 Thread Kyle.Montgomery via Sprinklerforum
Todd: I wonder how the compressed foam mattresses behave when the box burns away? FM Global Engineer: … (comes to startling realization) … Mother of God… This had me chuckling. You’ve piqued my curiosity. Maybe we should start a ‘Go Fund Me’ for full scale fire testing of compressed foam mattr

RE: ESFR spacing

2020-05-29 Thread Kyle.Montgomery via Sprinklerforum
Matt, For what it’s worth (probably less than $0.02), I agree with you that it should provide an equivalent level of protection to be, say 5’-6” off of the wall as it would be if you were 11’-0” between sprinkler heads due to some obstruction. I suppose someone could make a strong argument that

RE: [EXTERNAL] Re: NFPA 13, 2013 ed - hangers and pressures above 100psi

2020-05-29 Thread Kyle.Montgomery via Sprinklerforum
This has been addressed in the 2016 Edition: 9.2.3.4.4.4 and 9.2.3.5.2.2 both state “unless flexible sprinkler hose fittings are used”. So it doesn’t say it in 2013 Edition, but it’s clear what the intent was an the direction the code is going. -Kyle M From: Sprinklerforum On Behalf Of Jeff

RE: [EXTERNAL] Re: Help Finding Code Section

2020-05-20 Thread Kyle.Montgomery via Sprinklerforum
I agree with Skyler, this should be an acceptable way to protect the area. I also agree that the wording is poorly written for what the intent is. Also, the picture in the book (it’s even in the appendix of the regular version) is showing a condition where the larger area has no ceiling and the

RE: [EXTERNAL] Re: NFPA 13D

2020-03-30 Thread Kyle.Montgomery via Sprinklerforum
I agree that it looks like the head is going to be too close to a diffuser. As far as the CPVC pipe “supporting” the flex duct… is it really? I think there is a difference between “supporting” and “touching”. If I lean against the wall, I am not now supporting the house. It looks like the duct m

RE: [EXTERNAL] RE: Boat and RV storage units

2020-03-18 Thread Kyle.Montgomery via Sprinklerforum
We've done some of those in the Phoenix area. Everyone agreed to OH2, but there was certainly some debate about whether they should be something higher. We went back and forth all the way from OH1 (vehicle parking) to EH2 (mobile home manufacturing). We settled on OH2 because we figured a parke

RE: [EXTERNAL] Re: Air Venting

2020-03-09 Thread Kyle.Montgomery via Sprinklerforum
chamber From: Sprinklerforum mailto:sprinklerforum-boun...@lists.firesprinkler.org>> On Behalf Of Kyle.Montgomery via Sprinklerforum Sent: Monday, March 9, 2020 12:02 PM To: sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>; b...@firebyk

RE: [EXTERNAL] Re: Air Venting

2020-03-09 Thread Kyle.Montgomery via Sprinklerforum
How in the world would that work? I mean, the air is in the pipe when it’s installed, it doesn’t enter at a later date. From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Ben Young via Sprinklerforum Sent: Friday, March 6, 2020 2:04 PM To: b...@firebyknight

RE: [EXTERNAL] RE: Sprinklerforum Digest, Vol 83, Issue 6

2020-02-27 Thread Kyle.Montgomery via Sprinklerforum
You can't use that head on a pre-action system, can you? -Kyle M -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Anthony C via Sprinklerforum Sent: Thursday, February 27, 2020 7:34 AM To: sprinklerforum@lists.firesprinkler.org

RE: [EXTERNAL] Re: Shell Spaces and Bushed Outlets

2020-02-05 Thread Kyle.Montgomery via Sprinklerforum
different than I expect. I always thought more like parts of a strip mall building that might end up OH-2. Best. On Feb 5, 2020, at 07:58, Kyle.Montgomery via Sprinklerforum mailto:sprinklerforum@lists.firesprinkler.org>> wrote: That’s the crux of my question. A literal interpretation cou

RE: [EXTERNAL] Re: Shell Spaces and Bushed Outlets

2020-02-05 Thread Kyle.Montgomery via Sprinklerforum
: Shell Spaces and Bushed Outlets That doesn't sound legit - I would keep the tee in the calculations. A bushing isn't really recognized as a fitting per table 23.4.3.1.1 - more like a transient fitting. On Tue, Feb 4, 2020 at 1:22 PM Kyle.Montgomery via Sprinklerforum mailto:spri

RE: [EXTERNAL] Re: Shell Spaces and Bushed Outlets

2020-02-05 Thread Kyle.Montgomery via Sprinklerforum
, at 2:22 PM, Kyle.Montgomery via Sprinklerforum mailto:sprinklerforum@lists.firesprinkler.org>> wrote: Esteemed members of the fire sprinkler community, NFPA 13 (2016 Edition) section 8.15.20 is basically telling us to provide bushed 1” outlets for sprinklers in shell spaces, right? S

Shell Spaces and Bushed Outlets

2020-02-04 Thread Kyle.Montgomery via Sprinklerforum
Esteemed members of the fire sprinkler community, NFPA 13 (2016 Edition) section 8.15.20 is basically telling us to provide bushed 1" outlets for sprinklers in shell spaces, right? Section 23.4.4.8.1(9) tells us that friction loss can be excluded for the fitting directly connected to a sprinkle

RE: [EXTERNAL] Re: Misc. Storage

2020-01-29 Thread Kyle.Montgomery via Sprinklerforum
get to share the blame. So designing a system that is 2000 sq. ft. over what NFPA states is the maximum, would mean you just took responsibility for the entire thing. Mike Hill From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Kyle.Montgomery via S

RE: [EXTERNAL] Re: Misc. Storage

2020-01-29 Thread Kyle.Montgomery via Sprinklerforum
0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=Ny9euLltibCgctyfRXVZGuicLBdjOVrigQ2i3WLuKGg&s=CLCVR8_SFo0LibV2pOZMu0Zbv_OaKcqDvUuxtkt0XeM&e=> On 01/29/2020 9:30 AM, Kyle.Montgomery via Sprinklerforum wrote: Don't mean to hi-jack, but does anyone here think that

RE: Misc. Storage

2020-01-29 Thread Kyle.Montgomery via Sprinklerforum
Don't mean to hi-jack, but does anyone here think that breaking a 42,000 sq. ft. building up into two separate systems actually improves the level of protection? If your AHJ is reasonable, they might let you save that extra riser and feed main and just use one system. Or, if there is a small off

RE: [EXTERNAL] 13D Residential Sprinkler use in open Bar joists?

2020-01-20 Thread Kyle.Montgomery via Sprinklerforum
Viking makes an upright residential head, I think that could work for you. -Kyle M From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of J H via Sprinklerforum Sent: Monday, January 20, 2020 1:36 PM To: sprinklerforum@lists.firesprinkler.org Cc: J H Subject:

RE: Storage Tank High Level Sensor

2020-01-17 Thread Kyle.Montgomery via Sprinklerforum
I don’t believe the high-water sensor is required, but I am far from a tank expert. I am curious; if 12” is too small of a range (less than 0.5 psi) for the fill valve to operate in, what range can it reliably operate in? It’s just using pressure for the on/off, right? They have some fill valv

RE: [EXTERNAL] Re: NFPA 13, 23.1.3 (37)

2020-01-14 Thread Kyle.Montgomery via Sprinklerforum
Are you familiar with the term ‘C.O.J.’? Heheheh… Just in case you aren’t, it’s not dirty or anything. It means “cut on job”. -Kyle M From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Bruce Verhei via Sprinklerforum Sent: Monday, January 13, 2020 7:42 PM

RE: [EXTERNAL] Re: Looking for a 6" hanger for sloped roof

2020-01-02 Thread Kyle.Montgomery via Sprinklerforum
I think the Tolco/Cooper B-Line Fig. 75 is similar, if you want another option. From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of James Litvak via Sprinklerforum Sent: Thursday, January 2, 2020 7:55 AM To: vi...@wtfp.net Cc: James Litvak ; sprinklerforum@li

RE: [EXTERNAL] RE: Panel Construction

2019-12-20 Thread Kyle.Montgomery via Sprinklerforum
I agree that if the spaces are less than 300 sq. ft. and there are no unfilled penetrations, that you can treat it as panel construction. Even if it’s the walls of the room that help create the less than 300 sq. ft. area. Although Mr. Layton’s example of the TJIs makes me at least question that

RE: [EXTERNAL] RE: Panel Construction

2019-12-18 Thread Kyle.Montgomery via Sprinklerforum
Or, if they use spray-on fireproofing, that usually fills up the gaps. But the OP's theory should be sound for calling it obstructed construction. More to Travis's point, every time this comes up I wonder about that requirement for Panel Construction. Beam and Girder Construction doesn't requir

RE: [EXTERNAL] RE: Hydraulic Calc Phenomena?

2019-12-06 Thread Kyle.Montgomery via Sprinklerforum
That’s a good plan. From: Nick Maneen [mailto:nman...@sentryfp.com] Sent: Friday, December 6, 2019 9:03 AM To: Kyle.Montgomery ; sprinklerforum@lists.firesprinkler.org Cc: 'Brian Harris' ; 'Travis Mack' Subject: RE: [EXTERNAL] RE: Hydraulic Calc Phenomena? Yes Kyle, it was weird but it happene

RE: [EXTERNAL] RE: Hydraulic Calc Phenomena?

2019-12-06 Thread Kyle.Montgomery via Sprinklerforum
Changing pipe type to schedule 40 to improve hydraulics? Over-discharging is a result of imbalance in the system, not pipe sizes that are too big. The only way you improve the hydraulics by “choking down” a system is if you strategically do it so that you don’t need more pressure to make the mo

RE: [EXTERNAL] RE: Trouble getting Architects to give Revit files

2019-12-04 Thread Kyle.Montgomery via Sprinklerforum
/SME – Fire Protection | 864.676.5252 | craig.pr...@jacobs.com<mailto:craig.pr...@jacobs.com> | www.jacobs.com<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.jacobs.com_&d=DwMGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=i-9e61heIZz94tEwJ5KyalBxOjClmU4dKUZn8Q

RE: [EXTERNAL] RE: Trouble getting Architects to give Revit files

2019-12-04 Thread Kyle.Montgomery via Sprinklerforum
bs.com> | www.jacobs.com<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.jacobs.com_&d=DwMGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=i-9e61heIZz94tEwJ5KyalBxOjClmU4dKUZn8QOWQnY&s=VZkEuwQJf3cCcQhKmLVf3f0trjHf0UWe7BsJcjQUJKs&e=> 1041 East Butler Road Gree

RE: [EXTERNAL] RE: Trouble getting Architects to give Revit files

2019-12-03 Thread Kyle.Montgomery via Sprinklerforum
| Bamford Fire Sprinkler Co., Inc. P:785.825.7710 F: 785.825.0667 A: 1383 W. North Street Salina, KS 67401 -Original Message- From: Sprinklerforum mailto:sprinklerforum-boun...@lists.firesprinkler.org>> On Behalf Of Kyle.Montgomery via Sprinklerforum Sent: Monday, December

RE: [EXTERNAL] Groove rolled pipe under vibration

2019-12-02 Thread Kyle.Montgomery via Sprinklerforum
So, you are worried about the grooved joint failing due to the ends of the pipe distorting? I think you worry too much, but if you are going to worry about something, I think the nuts on the coupling coming loose would be a more likely failure mode. I've seen a LOT of diesel fire pump rooms wit

RE: [EXTERNAL] Re: Cane Detection

2019-11-22 Thread Kyle.Montgomery via Sprinklerforum
amp;r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=v0c6RYpM-3qtKhKszl6eqHTh4c2s2ahYnWf9LOrAMzY&s=AddRn1mo5PiyetLmfM5SSN2pZZaqT1aDKaK5G-2XYbs&e=> (803)896-9800 "Our firefighting starts with plan review..." From: Sprinklerforum mailto:sprinklerforum-boun...@lists.firesprinkler.org>> On

RE: [EXTERNAL] Re: Cane Detection

2019-11-22 Thread Kyle.Montgomery via Sprinklerforum
SN2pZZaqT1aDKaK5G-2XYbs&e=> (803)896-9800 "Our firefighting starts with plan review..." From: Sprinklerforum mailto:sprinklerforum-boun...@lists.firesprinkler.org>> On Behalf Of Kyle.Montgomery via Sprinklerforum Sent: Friday, November 22, 2019 3:32 PM To: sprinklerforum

RE: [EXTERNAL] Re: Cane Detection

2019-11-22 Thread Kyle.Montgomery via Sprinklerforum
Kyle.Montgomery via Sprinklerforum Sent: Friday, November 22, 2019 1:40 PM To: Nick Maneen mailto:nman...@sentryfp.com>> Cc: Kyle.Montgomery mailto:kmontgom...@aerofire.com>>; sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org> Subject: RE: [

RE: [EXTERNAL] Re: Cane Detection

2019-11-22 Thread Kyle.Montgomery via Sprinklerforum
t they haven't been around here in North Carolina yet. On Fri, Nov 22, 2019 at 12:40 PM Kyle.Montgomery via Sprinklerforum mailto:sprinklerforum@lists.firesprinkler.org>> wrote: All, I’m running into some issues on a project where the AHJ is asking for “Cane Detection”. For those of

RE: [EXTERNAL] Re: Cane Detection

2019-11-22 Thread Kyle.Montgomery via Sprinklerforum
on the 4" to act as the detection. I don't think bollards would be required or at least they haven't been around here in North Carolina yet. On Fri, Nov 22, 2019 at 12:40 PM Kyle.Montgomery via Sprinklerforum mailto:sprinklerforum@lists.firesprinkler.org>> wrote: All, I’m

RE: [EXTERNAL] Re: Cane Detection

2019-11-22 Thread Kyle.Montgomery via Sprinklerforum
e detection. I don't think bollards would be required or at least they haven't been around here in North Carolina yet. On Fri, Nov 22, 2019 at 12:40 PM Kyle.Montgomery via Sprinklerforum mailto:sprinklerforum@lists.firesprinkler.org>> wrote: All, I’m running into some issue

Cane Detection

2019-11-22 Thread Kyle.Montgomery via Sprinklerforum
All, I'm running into some issues on a project where the AHJ is asking for "Cane Detection". For those of you who may not be familiar with the term, the short answer is that cane detection is required for objects that protrude into the circulation path so that a blind/visually impaired person c

RE: [EXTERNAL] Anybody?

2019-11-20 Thread Kyle.Montgomery via Sprinklerforum
So it’s determined by testing the specific orifice, I kind of figured that. Do you (or anybody on the forum) know of a good way to estimate what the approximate Cd would be for an orifice? We’re sometimes asked to estimate what the discharge would be through an open orifice of unknown discharge

RE: [EXTERNAL] Anybody?

2019-11-20 Thread Kyle.Montgomery via Sprinklerforum
Phil, In the case of the 5.6k sprinkler you reference below, how is it determined that Cd = 0.75? -Kyle M From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Kerschner, Philip via Sprinklerforum Sent: Wednesday, November 20, 2019 8:32 AM To: vi...@wtfp.net

RE: Interstitial Spaces

2019-10-18 Thread Kyle.Montgomery via Sprinklerforum
Behalf Of Kyle.Montgomery via Sprinklerforum Sent: Friday, October 18, 2019 9:21 AM To: sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org> Cc: Kyle.Montgomery; Mike Hairfield; Steve Leyton Subject: RE: Interstitial Spaces Steve, Can you expound upon your questio