So, what would make them non-compliant? Obstructions, like ductwork and stuff?

When we’ve gotten similar pushback, it’s been because we’ve had 155-degree 
heads and the inspector has claimed that they aren’t appropriate for an 
unconditioned space (we’re working in Phoenix, so it can get unbelievably hot 
in “attic” spaces). I don’t know if that’s actually a concern though; I’m not 
aware of any sprinklers activating in this scenario.

-Kyle M

From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of Tony Silva via Sprinklerforum
Sent: Thursday, June 18, 2020 2:49 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Tony Silva <apsen...@gmail.com>; Travis Mack, SET, CFPS, CWBSP, RME-G 
<tm...@mfpdesign.com>; Ed Vining <fpe...@gmail.com>
Subject: [EXTERNAL] Re: Uprights in non combustible concealed space

Yes, it is specified in NFPA 13. NFPA 13, does not tell you which buildings are 
required to be sprinklered, which task is up to the building code or local 
ordinances. However, if the building is sprinklered (whether by mandate or 
voluntarily), it has to comply with NFPA 13. Note that the scope of NFPA 13 is 
to provide minimum requirements for the design and installation of automatic 
sprinkler systems. Not just the requirements for systems that are mandated.

Just take the garage in your home. Depending on local requirements, you may not 
require one for your house. However, if you build one, it has to comply with 
code requirements.

So if you leave the sprinklers in the concealed space, make sure they comply 
with code requirements.

My two cents, Tony

On Thu, Jun 18, 2020 at 12:48 PM Travis Mack, SET, CFPS, CWBSP, RME-G via 
Sprinklerforum 
<sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>>
 wrote:
I could be wrong, but isn’t there something in IFC that states a fire 
protection system left in place needs to be compliant for the area?  I’ve had 
inspectors interpret as you indicate.  It’s the rationale that you can’t leave 
dead sprinkler pipe in the air.

Now, I have had this same situation and argued in the case the sprinkler was 
just a “glorified plug.”  Contractor was in a bind, no access to remove the 
sprinklers.

But, if you dig into the fire code, you may find where he is at least starting 
from.  You won’t find your answer in NFPA 13.


[MFP_logo_F]<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.mfpdesign.com_&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=Mob4mFnZn69hN4XUuGusdTNb0b4NOCBnatLXln4_TA4&s=-kLVx2brNHGaVRJeTfoRb5PzFUNdGr3iCMvNnKNARAw&e=>
Travis Mack, CFPS, CWBSP, RME-G, SET
Engineering Manager
MFP Design
3356 E Vallejo Ct
Gilbert, AZ 85298
NEW EXTENSION: 480-505-9271 ext. 700
NEW MOBILE: 480-272-2471
tm...@mfpdesign.com<mailto:tm...@mfpdesign.com>
travis.m...@ferguson.com<mailto:travis.m...@ferguson.com>
www.mfpdesign.com<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.mfpdesign.com&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=Mob4mFnZn69hN4XUuGusdTNb0b4NOCBnatLXln4_TA4&s=QGkovRjduynmuyNUH-eu5mlinx8TeAUj6ha1vDi5-UE&e=>

Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://urldefense.proofpoint.com/v2/url?u=https-3A__na01.safelinks.protection.outlook.com_-3Furl-3Dhttps-253A-252F-252Fwww.hightail.com-252Fu-252FMFPDesign-26data-3D02-257C01-257C-257C1121d49f9e6b4cf248f108d4df580e77-257C14e5497c16da42e69ffa77d19bafe511-257C0-257C0-257C636379016677342180-26sdata-3DeGdMZGu2wXhUupGwgGTrqF3b54OP5-252BAZvlHhABSexWY-253D-26reserved-3D0&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=Mob4mFnZn69hN4XUuGusdTNb0b4NOCBnatLXln4_TA4&s=HnHg1j7d0W7f3AVxarILDxilvFwr6J2lXyxSfX_Ockc&e=>
LinkedIn: 
https://www.linkedin.com/in/travismack<https://urldefense.proofpoint.com/v2/url?u=https-3A__na01.safelinks.protection.outlook.com_-3Furl-3Dhttps-253A-252F-252Fwww.linkedin.com-252Fin-252Ftravismack-26data-3D02-257C01-257C-257C1121d49f9e6b4cf248f108d4df580e77-257C14e5497c16da42e69ffa77d19bafe511-257C0-257C0-257C636379016677342180-26sdata-3DtT5E7LsZjSmyreKi4gDCa70EWN-252BZodi-252FhbeCbHNRijI-253D-26reserved-3D0&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=Mob4mFnZn69hN4XUuGusdTNb0b4NOCBnatLXln4_TA4&s=J_IKjOdCa7ZQGz_vx7-IhwZgrV8XXw8LxZDSMzil9oA&e=>

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”

Need/Want a faster way to check material pricing?  Build a material quote?  
Check availability ?   Searching for an invoice?
*If you do not already have an account with 
ferguson.com<https://urldefense.proofpoint.com/v2/url?u=http-3A__ferguson.com&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=Mob4mFnZn69hN4XUuGusdTNb0b4NOCBnatLXln4_TA4&s=u3nRNd7HJHYYrAco0yCE_vzkcdGBxt-jDixE0lcW9yM&e=>,
 click 
here<https://urldefense.proofpoint.com/v2/url?u=https-3A__www.ferguson.com_account-2Dregistration&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=Mob4mFnZn69hN4XUuGusdTNb0b4NOCBnatLXln4_TA4&s=_tiIBy4pv__3ZnNyX2y1l2ugwJGWYJTb0cr5zR4INnU&e=>
 to register.*
**Have a Ferguson account? Download the Ferguson app for on-the-go access to 
your favorite 
ferguson.com<https://urldefense.proofpoint.com/v2/url?u=http-3A__ferguson.com&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=Mob4mFnZn69hN4XUuGusdTNb0b4NOCBnatLXln4_TA4&s=u3nRNd7HJHYYrAco0yCE_vzkcdGBxt-jDixE0lcW9yM&e=>
 features. Apple iOS 
devices<https://urldefense.proofpoint.com/v2/url?u=http-3A__fergusoncommunications.us.newsweaver.com_hq7bgesq7f_1qtklpp37l9byeftyuoy12_external-3Femail-3Dtrue-26a-3D6-26p-3D2591775-26t-3D517003&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=Mob4mFnZn69hN4XUuGusdTNb0b4NOCBnatLXln4_TA4&s=6F2UbCRGBeLvSTyKiKs3S4kEsRUYhfN7735xWEiVe6k&e=>
 or Android 
devices<https://urldefense.proofpoint.com/v2/url?u=http-3A__fergusoncommunications.us.newsweaver.com_hq7bgesq7f_n1gewi5ud95byeftyuoy12_external-3Femail-3Dtrue-26a-3D6-26p-3D2591775-26t-3D517003&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=Mob4mFnZn69hN4XUuGusdTNb0b4NOCBnatLXln4_TA4&s=K1if_M7lnUnJDQktg6xiOFtHfiPEWnE19KYjBxyBf_g&e=>**



From: Sprinklerforum 
<sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Ed Vining via Sprinklerforum
Sent: Thursday, June 18, 2020 11:35 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Cc: Ed Vining <fpe...@gmail.com<mailto:fpe...@gmail.com>>
Subject: Re: Uprights in non combustible concealed space

Not really. The codes and standards determine the decision.

This may be my last post. At the age of 95 I am starting to lose interest.


Ed Vining
2770 Pleasant Hill Rd Apt 228
Pleasant Hill CA 95423
925-448-2159
fpe...@gmail.com<mailto:fpe...@gmail.com>


On Thu, Jun 18, 2020 at 11:28 AM Cary Webber via Sprinklerforum 
<sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>>
 wrote:
On the downside, if all areas above the ceilings are not protected, it may give 
a false sense of security. On the upside, more sprinklers are better, and even 
if not required they can act as detectors in the space. Bottom line is that the 
AHJ has ultimate decision making authority.



Cary Webber CFPS Director, Technical Services
Reliable Automatic Sprinkler Co., Inc.
1470 Smith Grove Road, Liberty, SC  29657
Tel: 864-843-5161

[Image removed by 
sender.]<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.reliablesprinkler.com_&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=Mob4mFnZn69hN4XUuGusdTNb0b4NOCBnatLXln4_TA4&s=XjZij7r9cTJxYwa_gXlt9g8oIoBWgW10u78QrYMbErI&e=>

From: Sprinklerforum 
<sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of John Irwin via Sprinklerforum
Sent: Thursday, June 18, 2020 2:21 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Cc: John Irwin <jir...@quickresponsefl.com<mailto:jir...@quickresponsefl.com>>
Subject: Uprights in non combustible concealed space

CAUTION: This email originated from outside of the organization. Do not click 
links or open attachments unless you can confirm the sender and know the 
content is safe.

We installed temporary upright Protection in a partially occupied building 
during a major renovation. We then came back and dropped pendent heads in the 
new ceiling. We left the uprights above the new ceiling. Fire inspector says we 
need to remove the uprights now. Is there a basis for removing these? I realize 
they are not required but are they permitted to remain?

John Irwin
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org<https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=Mob4mFnZn69hN4XUuGusdTNb0b4NOCBnatLXln4_TA4&s=Na--_Rcj91I2d50TIG8KPzJmXw2UqzQPo1b0kxshiVU&e=>
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org<https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=Mob4mFnZn69hN4XUuGusdTNb0b4NOCBnatLXln4_TA4&s=Na--_Rcj91I2d50TIG8KPzJmXw2UqzQPo1b0kxshiVU&e=>
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
  • Uprights in non co... John Irwin via Sprinklerforum
    • RE: Uprights ... Cary Webber via Sprinklerforum
      • Re: Uprig... Ed Vining via Sprinklerforum
        • RE: U... Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
          • R... Tony Silva via Sprinklerforum
            • ... Kyle.Montgomery via Sprinklerforum
        • RE: U... Steve Leyton via Sprinklerforum
          • R... Fpdcdesign via Sprinklerforum
        • RE: U... Reed A. Roisum, SET via Sprinklerforum
        • Re: U... Ben Young via Sprinklerforum
      • RE: Uprig... Anthony via Sprinklerforum
        • RE: U... Steve Leyton via Sprinklerforum
          • R... Anthony via Sprinklerforum
            • ... Steve Leyton via Sprinklerforum
              • ... Dewayne Martinez via Sprinklerforum
    • RE: Uprights ... Richard Carr via Sprinklerforum

Reply via email to