Thanks, John, but it's still a storage occupancy, just a different
commodity/
2:05 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: [EXTERNAL] RE: Converting from ESFR to CMDA - Spacing Issues
Kyle,
Refer to NFPA-13, 2016 Ed, page 52, parag. 8.4.6.6. This may apply to your
situation.
John O'Connor
National Fire Sprinklers, Inc.
Nashville TN
From:
rforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: [EXTERNAL] RE: Converting from ESFR to CMDA - Spacing Issues
I think you're right. It just doesn't seem like that should be the case. How
can this spacing allowance be appropriate for the notoriously unfo
Kyle,
Refer to NFPA-13, 2016 Ed, page 52, parag. 8.4.6.6. This may apply to your
situation.
John O'Connor
National Fire Sprinklers, Inc.
Nashville TN
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Kyle.Montgomery
Sent: Monday, October 08, 2018 3:2
ERNAL] RE: Converting from ESFR to CMDA - Spacing Issues
I think you're right. It just doesn't seem like that should be the case. How
can this spacing allowance be appropriate for the notoriously unforgiving
ESFR criteria, but somehow not OK for the traditionally much more forgiving
: 602.763.4736
kmontgom...@aerofire.com<mailto:kmontgom...@aerofire.com>
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of MFP Design, LLC
Sent: Monday, October 8, 2018 2:03 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: [EXTERNAL] RE: Converting from ESF
FM allows it because all of their sprinklers are "storage" sprinklers. It
doesn't matter if it is CMDA, CMSA or ESFR, it is a "storage" sprinkler for
FM so the extended requirements are in play. I don't think you will find
any forgiveness on this issue in 13.
Every time we've dealt with this