RE: k -- WHAT?

2012-04-23 Thread bcasterline
good eye! i happen to know it gets pretty hot in Ohio geo. even w/o a fire. i was lucky to start there, and trained by The Greatest Sprink Whom Ever Lived (thanks Vince). George, please google brad casterline, i am the first two, ask me 2 B ur FB friend, please, i would gladly accept and yo

RE: k -- WHAT?

2012-04-23 Thread George Church
ginal Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Vince Sabolik Sent: Monday, April 16, 2012 2:40 PM To: sprinklerforum@firesprinkler.org Subject: RE: k -- WHAT? Forum -- This was my question, so I'd like to clarif

RE: k -- WHAT?

2012-04-16 Thread Brad Casterline
er/sec (32.2/9.81=3.28 ft/m). Thanks for caring, I always appreciate the attention. -Original Message- From: George Church [mailto:g...@rowesprinkler.com] Sent: Monday, April 16, 2012 12:51 PM To: sprinklerforum@firesprinkler.org Subject: RE: k -- WHAT? Wasn't it a hose valve for forw

Re: k -- WHAT?

2012-04-16 Thread david . 001
4-330-6193 fax:  404-739-4172 - Original Message - From: "Vince Sabolik" To: sprinklerforum@firesprinkler.org Sent: Monday, April 16, 2012 2:40:06 PM Subject: RE: k   -- WHAT? Forum -- This was my question, so I'd like to clarify a little. OK, yes this IS for

RE: k -- WHAT?

2012-04-16 Thread Vince Sabolik
ch, Jr., CET Rowe Sprinkler Systems, Inc. PO Box 407, Middleburg, PA 17842 877-324-ROWE 570-837-6335 fax g...@rowesprinkler.com -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brad Casterline Sent: Mo

RE: k -- WHAT?

2012-04-16 Thread Art Tiroly
Behalf Of George Church Sent: Monday, April 16, 2012 1:51 PM To: sprinklerforum@firesprinkler.org Subject: RE: k -- WHAT? Wasn't it a hose valve for forward flushing of the BFP that was the original question? And don't K factors have to be empirically derived? I once tried to determin

RE: k -- WHAT?

2012-04-16 Thread George Church
11:37 AM To: sprinklerforum@firesprinkler.org Subject: RE: k -- WHAT? But since friction head with turbulent (sprinkler) flow is proportional to the velocity squared, and the data from Ron Greenman's link says 'K Value for use in the formula hf=k(v^2/2g)', and the velocity varies as the

RE: k -- WHAT?

2012-04-16 Thread Brad Casterline
and 100 PSI, but since they move away from v^2, we cannot trust them. Thanks again Sir! -Original Message- From: Brad Casterline [mailto:bcasterl...@fsc-inc.com] Sent: Monday, April 16, 2012 10:37 AM To: sprinklerforum@firesprinkler.org Subject: RE: k -- WHAT? But since friction head with

RE: k -- WHAT?

2012-04-16 Thread Brad Casterline
curve' we are looking for, as opposed to an average over a range? -Original Message- From: Roland Huggins [mailto:rhugg...@firesprinkler.org] Sent: Monday, April 16, 2012 10:00 AM To: sprinklerforum@firesprinkler.org Subject: Re: k -- WHAT? I started to say before getting overly prec

Re: k -- WHAT?

2012-04-16 Thread Roland Huggins
I started to say before getting overly precise (but that horse has left the barn), it might be helpful to keep in mind that the K valve on a sprinkler is NOT a constant at different flows. It is an AVERAGED result for flows from 7 psi to 100 psi. Roland ___

RE: k -- WHAT?

2012-04-16 Thread Brad Casterline
st run the numbers backwards and come up with a K Value --what? -Original Message- From: Brad Casterline [mailto:bcasterl...@fsc-inc.com] Sent: Saturday, April 14, 2012 2:36 PM To: 'Vince Sabolik' Cc: sprinklerforum@firesprinkler.org Subject: RE: k -- WHAT? Vince,

RE: k -- WHAT?

2012-04-14 Thread Brad Casterline
Vince, I get K=149. Instead of Q=K*P^2, I used Q=vA, (Q)cubic feet per second equals (v)feet per second times (A) square feet. A=PI*radius^2,=PI*((2.5"/12/2)^2)=.034 ft^2. This is the "theoretical" area, and we have to reduce it proportional to the friction loss through the valve. For lack of a

RE: k -- WHAT?

2012-04-13 Thread Bruce Verhei
---Original message- From: Cesar Lira To: sprinklerforum@firesprinkler.org Sent: Mon, Apr 9, 2012 15:53:38 GMT+00:00 Subject: RE: k -- WHAT? Each K value that you want to obtain only use the formula. Q=√(P)*K K=Q/ √(P)K=250/√(100) For the case of 1.5 hose. Q=√(P)*K

RE: k -- WHAT?

2012-04-12 Thread Cesar Lira
- De: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] En nombre de dradha Enviado el: Lunes, 09 de Abril de 2012 09:40 a.m. Para: sprinklerforum@firesprinkler.org Asunto: Re: k -- WHAT? Hello Vince the K value for 2.5inch hose valve is 25 for a flow

RE: k -- WHAT?

2012-04-09 Thread Steve Leyton
-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ed Vining Sent: Monday, April 09, 2012 11:23 AM To: sprinklerforum@firesprinkler.org Subject: Re: k -- WHAT? My beat up old 14th Edition of the Fire Protection Handbook shows a Figure 11.6J (Taken from Chemical Engi

Re: k -- WHAT?

2012-04-09 Thread Ed Vining
My beat up old 14th Edition of the Fire Protection Handbook shows a Figure 11.6J (Taken from Chemical Engineers' Handbook). The curve goes off the chart with 1400 gpm at about 63 psi from a 2 1/2" hydrant butt. Table 11-6B shows a theoretical discharge of 1490 gpm (interpolated) at 63 psi, and188

Re: k -- WHAT?

2012-04-09 Thread dradha
Hello Vince the K value for 2.5inch hose valve is 25 for a flow(as per NFPA) of 250gpm at 100psi. Regards DR On Thu, Apr 5, 2012 at 9:14 PM, Vince Sabolik wrote: > Good morning -- > > Anyone have an approximate K value for a 2½" hose valve? > > > > > Vince Sabolik, West Tech Fire Protection, I

RE: k -- WHAT?

2012-04-05 Thread Vince Sabolik
At 12:22 PM 4/5/2012, you wrote: If you are doing a forward flow test of a backflow, why not hook the outlet up to a Hose Monster? Am I missing something? Yup, PERMANACE. The thing has to be installed permanently so it has to be designed. -- next part -- An HTML atta

RE: k -- WHAT?

2012-04-05 Thread Johnson, Duane (NIH/OD/ORS) [C]
- One Sprinkler at a Time" -Original Message- From: Johnson, Duane (NIH/OD/ORS) [C] Sent: Thursday, April 05, 2012 12:51 PM To: sprinklerforum@firesprinkler.org Subject: RE: k -- WHAT? NFPA 14 Table 8.3.1.3 indicates a 2½" angle valve to be 31 equiv ft of pipe. You can use H

RE: k -- WHAT?

2012-04-05 Thread Steve Leyton
boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Thompson, Pat Sent: Thursday, April 05, 2012 9:47 AM To: sprinklerforum@firesprinkler.org Subject: RE: k -- WHAT? K factor as applied in our industry is a coefficient for a smooth bore orifice. I am not a

RE: k -- WHAT?

2012-04-05 Thread Johnson, Duane (NIH/OD/ORS) [C]
-0487 "Protecting Science - One Sprinkler at a Time" -Original Message- From: Vince Sabolik [mailto:vi...@wtfp.net] Sent: Thursday, April 05, 2012 12:02 PM To: sprinklerforum@firesprinkler.org Subject: RE: k -- WHAT? Forward flow testing for a BFP So I guess what I'm looking

RE: k -- WHAT?

2012-04-05 Thread Thompson, Pat
K factor as applied in our industry is a coefficient for a smooth bore orifice. I am not aware of how this could be applied to a hose valve since it is not a smooth bore orifice, but I can offer some input from fire department hydraulics: GPM (Q) = (29.7*diameter squared)*square root of pressur

RE: k -- WHAT?

2012-04-05 Thread Todd Williams
>[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ron Greenman >>Sent: Thursday, April 05, 2012 8:49 AM >>To: sprinklerforum@firesprinkler.org >>Subject: Re: k -- WHAT? >> >>http://www.westerndynamics.com/Download/friclossfittings.pdf >> >>On Thu, Apr 5,

RE: k -- WHAT?

2012-04-05 Thread Cahill, Christopher
sprinkler.org] On Behalf Of G. Tim Stone Sent: Thursday, April 05, 2012 10:59 AM To: sprinklerforum@firesprinkler.org Subject: RE: k -- WHAT? Vince, How much water are you planning on flowing? 500 gpm flow @ 100 psi = K=50 500 gpm flow @ 65 psi = K=62 Regards, G. Tim Stone G. Tim Stone Consulti

RE: k -- WHAT?

2012-04-05 Thread Vince Sabolik
half Of Ron Greenman Sent: Thursday, April 05, 2012 8:49 AM To: sprinklerforum@firesprinkler.org Subject: Re: k -- WHAT? http://www.westerndynamics.com/Download/friclossfittings.pdf On Thu, Apr 5, 2012 at 8:46 AM, Seidl Jamie D. wrote: > Are you looking for friction loss through a valve,

RE: k -- WHAT?

2012-04-05 Thread Steve Leyton
Manufacturer's data sheets!!! Steve -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Seidl Jamie D. Sent: Thursday, April 05, 2012 9:01 AM To: sprinklerforum@firesprinkler.org Subject: RE: k -- WHA

RE: k -- WHAT?

2012-04-05 Thread Seidl Jamie D .
11:57 AM To: sprinklerforum@firesprinkler.org Subject: RE: k -- WHAT? Um, Ron? According to that chart a 2.5" angle valve will flow 9.9gpm at 100psi. I don't think that's quite in accordance with HW. If you are flowing 250 through the valve at 100psi, it has a K of 25.0, no?

RE: k -- WHAT?

2012-04-05 Thread G. Tim Stone
Vince, How much water are you planning on flowing? 500 gpm flow @ 100 psi = K=50 500 gpm flow @ 65 psi = K=62 Regards, G. Tim Stone G. Tim Stone Consulting, LLC NICET Level III Engineering Technician Fire Protection Sprinkler Design and Consulting Services 117 Old Stage Rd. - Es

RE: k -- WHAT?

2012-04-05 Thread Steve Leyton
What are you trying to do? Steve -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ron Greenman Sent: Thursday, April 05, 2012 8:49 AM To: sprinklerforum@firesprinkler.org Subject: Re: k

Re: k -- WHAT?

2012-04-05 Thread Ron Greenman
http://www.westerndynamics.com/Download/friclossfittings.pdf On Thu, Apr 5, 2012 at 8:46 AM, Seidl Jamie D. wrote: > Are you looking for friction loss through a valve, or are you looking to > flow a certain amount of water at a certain pressure? > > -Original Message- > From: sprinklerfo

RE: k -- WHAT?

2012-04-05 Thread Seidl Jamie D .
Are you looking for friction loss through a valve, or are you looking to flow a certain amount of water at a certain pressure? -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Vince Sabolik Sent: Thursday, Ap