good eye! i happen to know it gets pretty hot in Ohio geo. even w/o a
fire. i was lucky to start there, and trained by The Greatest Sprink
Whom Ever Lived (thanks Vince). George, please google brad casterline,
i am the first two, ask me 2 B ur FB friend, please, i would gladly
accept and yo
ginal Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Vince Sabolik
Sent: Monday, April 16, 2012 2:40 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: k -- WHAT?
Forum --
This was my question, so I'd like to clarif
er/sec (32.2/9.81=3.28 ft/m).
Thanks for caring, I always appreciate the attention.
-Original Message-
From: George Church [mailto:g...@rowesprinkler.com]
Sent: Monday, April 16, 2012 12:51 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: k -- WHAT?
Wasn't it a hose valve for forw
4-330-6193
fax: 404-739-4172
- Original Message -
From: "Vince Sabolik"
To: sprinklerforum@firesprinkler.org
Sent: Monday, April 16, 2012 2:40:06 PM
Subject: RE: k -- WHAT?
Forum --
This was my question, so I'd like to clarify a little.
OK, yes this IS for
ch, Jr., CET
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE 570-837-6335 fax
g...@rowesprinkler.com
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brad Casterline
Sent: Mo
Behalf Of George Church
Sent: Monday, April 16, 2012 1:51 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: k -- WHAT?
Wasn't it a hose valve for forward flushing of the BFP that was the original
question?
And don't K factors have to be empirically derived? I once tried to
determin
11:37 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: k -- WHAT?
But since friction head with turbulent (sprinkler) flow is proportional to the
velocity squared, and the data from Ron Greenman's link says 'K Value for use
in the formula hf=k(v^2/2g)', and the velocity varies as the
and
100 PSI, but since they move away from v^2, we cannot trust them. Thanks
again Sir!
-Original Message-
From: Brad Casterline [mailto:bcasterl...@fsc-inc.com]
Sent: Monday, April 16, 2012 10:37 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: k -- WHAT?
But since friction head with
curve' we are looking for,
as opposed to an average over a range?
-Original Message-
From: Roland Huggins [mailto:rhugg...@firesprinkler.org]
Sent: Monday, April 16, 2012 10:00 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: k -- WHAT?
I started to say before getting overly prec
I started to say before getting overly precise (but that horse has
left the barn), it might be helpful to keep in mind that the K valve
on a sprinkler is NOT a constant at different flows. It is an
AVERAGED result for flows from 7 psi to 100 psi.
Roland
___
st run the numbers backwards and
come up with a K Value --what?
-Original Message-
From: Brad Casterline [mailto:bcasterl...@fsc-inc.com]
Sent: Saturday, April 14, 2012 2:36 PM
To: 'Vince Sabolik'
Cc: sprinklerforum@firesprinkler.org
Subject: RE: k -- WHAT?
Vince,
Vince,
I get K=149.
Instead of Q=K*P^2, I used Q=vA, (Q)cubic feet per second equals (v)feet per
second times (A)
square feet.
A=PI*radius^2,=PI*((2.5"/12/2)^2)=.034 ft^2. This is the "theoretical" area,
and we have to reduce
it proportional to the friction loss through the valve. For lack of a
---Original message-
From: Cesar Lira
To: sprinklerforum@firesprinkler.org
Sent: Mon, Apr 9, 2012 15:53:38 GMT+00:00
Subject: RE: k -- WHAT?
Each K value that you want to obtain only use the formula.
Q=√(P)*K
K=Q/ √(P)K=250/√(100)
For the case of 1.5 hose.
Q=√(P)*K
-
De: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] En nombre de dradha
Enviado el: Lunes, 09 de Abril de 2012 09:40 a.m.
Para: sprinklerforum@firesprinkler.org
Asunto: Re: k -- WHAT?
Hello Vince
the K value for 2.5inch hose valve is 25 for a flow
-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ed Vining
Sent: Monday, April 09, 2012 11:23 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: k -- WHAT?
My beat up old 14th Edition of the Fire Protection Handbook shows a Figure
11.6J (Taken from Chemical Engi
My beat up old 14th Edition of the Fire Protection Handbook shows a Figure
11.6J (Taken from Chemical Engineers' Handbook). The curve goes off the
chart with 1400 gpm at about 63 psi from a 2 1/2" hydrant butt. Table
11-6B shows a theoretical discharge of 1490 gpm (interpolated) at 63 psi,
and188
Hello Vince
the K value for 2.5inch hose valve is 25 for a flow(as per NFPA) of 250gpm
at 100psi.
Regards
DR
On Thu, Apr 5, 2012 at 9:14 PM, Vince Sabolik wrote:
> Good morning --
>
> Anyone have an approximate K value for a 2½" hose valve?
>
>
>
>
> Vince Sabolik, West Tech Fire Protection, I
At 12:22 PM 4/5/2012, you wrote:
If you are doing a forward flow test of a backflow, why not hook the
outlet up to a Hose Monster? Am I missing something?
Yup, PERMANACE. The thing has to be installed permanently so it has
to be designed.
-- next part --
An HTML atta
- One Sprinkler at a Time"
-Original Message-
From: Johnson, Duane (NIH/OD/ORS) [C]
Sent: Thursday, April 05, 2012 12:51 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: k -- WHAT?
NFPA 14 Table 8.3.1.3 indicates a 2½" angle valve to be 31 equiv ft of pipe.
You can use H
boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Thompson, Pat
Sent: Thursday, April 05, 2012 9:47 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: k -- WHAT?
K factor as applied in our industry is a coefficient for a smooth bore orifice.
I am not a
-0487
"Protecting Science - One Sprinkler at a Time"
-Original Message-
From: Vince Sabolik [mailto:vi...@wtfp.net]
Sent: Thursday, April 05, 2012 12:02 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: k -- WHAT?
Forward flow testing for a BFP
So I guess what I'm looking
K factor as applied in our industry is a coefficient for a smooth bore orifice.
I am not aware of how this could be applied to a hose valve since it is not a
smooth bore orifice, but I can offer some input from fire department
hydraulics: GPM (Q) = (29.7*diameter squared)*square root of pressur
>[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ron Greenman
>>Sent: Thursday, April 05, 2012 8:49 AM
>>To: sprinklerforum@firesprinkler.org
>>Subject: Re: k -- WHAT?
>>
>>http://www.westerndynamics.com/Download/friclossfittings.pdf
>>
>>On Thu, Apr 5,
sprinkler.org] On Behalf Of G. Tim Stone
Sent: Thursday, April 05, 2012 10:59 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: k -- WHAT?
Vince,
How much water are you planning on flowing?
500 gpm flow @ 100 psi = K=50
500 gpm flow @ 65 psi = K=62
Regards,
G. Tim Stone
G. Tim Stone Consulti
half Of Ron Greenman
Sent: Thursday, April 05, 2012 8:49 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: k -- WHAT?
http://www.westerndynamics.com/Download/friclossfittings.pdf
On Thu, Apr 5, 2012 at 8:46 AM, Seidl Jamie D. wrote:
> Are you looking for friction loss through a valve,
Manufacturer's data sheets!!!
Steve
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Seidl Jamie D.
Sent: Thursday, April 05, 2012 9:01 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: k -- WHA
11:57 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: k -- WHAT?
Um, Ron? According to that chart a 2.5" angle valve will flow 9.9gpm at
100psi. I don't think that's quite in accordance with HW.
If you are flowing 250 through the valve at 100psi, it has a K of 25.0, no?
Vince,
How much water are you planning on flowing?
500 gpm flow @ 100 psi = K=50
500 gpm flow @ 65 psi = K=62
Regards,
G. Tim Stone
G. Tim Stone Consulting, LLC
NICET Level III Engineering Technician
Fire Protection Sprinkler Design
and Consulting Services
117 Old Stage Rd. - Es
What are you
trying to do?
Steve
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ron Greenman
Sent: Thursday, April 05, 2012 8:49 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: k
http://www.westerndynamics.com/Download/friclossfittings.pdf
On Thu, Apr 5, 2012 at 8:46 AM, Seidl Jamie D. wrote:
> Are you looking for friction loss through a valve, or are you looking to
> flow a certain amount of water at a certain pressure?
>
> -Original Message-
> From: sprinklerfo
Are you looking for friction loss through a valve, or are you looking to flow a
certain amount of water at a certain pressure?
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Vince Sabolik
Sent: Thursday, Ap