On Tue, 21 Nov 2000, Marshall Dudley wrote:

> russ e rosser wrote:
> 
> > If the
> > wands were in series with the short, I'm afraid *the body* might supply
> > enough resistance (up to 1 Meg ohm, initially) to delay the breaker
> > response.
> 
> 120 VAC and 1 megohm gives .12 mA.  That is not enough current to make it cut
> out, a fuse blow, or to even feel.
> 
> > The bottom line, of course, is to stop current flow >5mA
> > through the wands.
> 
> 2 mA is less than 5 mA, if that is a correct figure.
> 

If a 100 kilohm resistor is placed in series with each wand, the 
peak current would be limited to less than 2 mA from a short to
the 120 V AC power line. 

These would both be in series for the desired current from one wand
to the other. With 9V pulses, the peak current would be 45 microA
or less, but someone said only a few uA was needed. If 45 uA
is enough, resistors offer the best protection.

John


> >  Amid any uncertainty as to freak circuits that might
> > *possibly* arise, a fuse in-line with a wand would *definitely* eliminate
> > ANY conceivable shock above its rating.  Cheap, too, BTW.
> 
> I disagree.  How fast is the fuse, usually they can take seconds to melt when
> near their rating.  Also they don't even approach their rating until you are
> far above the 5 mA you indicate you want to guard against.
> 
> Marshall
> 
> see http://www.addisselectric.com/gfcipage.htm also.
> 
> 
> --
> The silver-list is a moderated forum for discussion of colloidal silver.
> 
> To join or quit silver-list or silver-digest send an e-mail message to: 
> [email protected]  -or-  [email protected]
> with the word subscribe or unsubscribe in the SUBJECT line.
> 
> To post, address your message to: [email protected]
> Silver-list archive: http://escribe.com/health/thesilverlist/index.html
> List maintainer: Mike Devour <[email protected]>
> 
>