This what I think you are looking for from the 02 NFPA 13.

14.4.4.3.4* Where sprinklers are installed above and below a ceiling or in a
case where more
than two areas are supplied from a common set of branch lines, the branch
lines and supplies
shall be calculated to supply the largest water demand.

A.14.4.4.3.4 This subsection assumes a ceiling constructed so as to
reasonably ensure that a fire
on one side of the ceiling will operate sprinklers on one side only. Where a
ceiling is sufficiently
open, or of such construction that operation of sprinklers above and below
the ceiling can be anticipated,
the operation of such additional sprinklers should be considered in the
calculations.

Joe Burtell, SET, CFPS
Burtell Fire Protection, Inc.
[EMAIL PROTECTED]
www.burtellfire.com
 
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Greg McGahan
Sent: Thursday, November 30, 2006 7:36 AM
To: [email protected]
Subject: Overhead and Mezzanine calcs


Normally we error on the side of caution but we have a situation with calcs
that are not working with more than a 2.4% cushion so I have to ask.

Existing building with existing 3" water supply with new room and new
mezzanine. The new room is 51' by 15' with a lower mezzanine that is 36' x
15'. The remote area is specified at 3,000 sqft so there is no reductions
etc.

Question:  Do I need to calculate the entire area with the mezz.? I need
something concrete to submit if I do not have to include them.

Thanks,
Greg McGahan

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to