I dealt with this directly with NFPA a while back about the definition
of non-combustible hydraulic fluid is.  They told me that as long as the
fluid in question has a flash point, regardless of its temperature, then
it is considered combustible as it pertains to the elevator section in
NFPA 13. 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Greg
McGahan
Sent: Monday, January 08, 2007 10:21 AM
To: [email protected]
Subject: hydraulic elevators


We are receiving mixed reviews from AHJ's regarding this issue: Are
sprinklers required in the bottom of hydraulic elevator shafts?

I know what the code says but we have never been able to document that
ANY hydraulic elev fluid is non-combustible by definition. I was
informed this morning that we are the only contractor in the area
putting sprinklers in the bottom of these shafts.

Thanks,
Greg McGahan