NFPA #14 states that when the static pressure at a hose connection exceeds 175 psi, a pressure regulating device shall be provided to limit the pressure to 100 psi for 1 ½" hose connections and to 175 psi for all other hose connections.
What if the standpipe is a Class III utilizing the fully sprinklered building exception allowing 2 ½" hose valves with 1 ½" reducers, caps and chains? Does the pressure need to be limited to 100 psi or 175 psi? Dave David K. Thompson Vice President Allstate Fire Sprinkler, Inc. P.O. Box 2350 Hartford, CT 06146 Phone = 860-246-7711 Fax = 860-246-7707 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum