Must meet both criteria. The 1½" hose station is available for untrained
persons thus the pressure limit.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Dave Thompson
Sent: Tuesday, January 30, 2007 12:11 PM
To: [email protected]
Subject: NFPA #14 and pressures


NFPA #14 states that when the static pressure at a hose connection exceeds
175 psi, a pressure regulating device shall be provided to limit the
pressure to 100 psi for 1 ½" hose connections and to 175 psi for all other
hose connections.

 

What if the standpipe is a Class III utilizing the fully sprinklered
building exception allowing 2 ½" hose valves with 1 ½" reducers, caps and
chains?

 

Does the pressure need to be limited to 100 psi or 175 psi?

 

 

Dave

 

 