Dave:

Treat the connections as Class I for purposes of the hydraulic design (NFPA 14, 
2007 7.3.4.1.2 for Class III systems without hose).    Paul's exactly right:  
if we're using the exception to eliminate small hose cabinets, the only source 
of equipment for mop-up streams would be the responding fire department.

Steve Leyton
Protection Design & Consulting

The foregoing is the opinion of the writer alone, and does not necessarily 
represent the intent of the NFPA 14 Technical Committee, nor constitute a 
formal or informal interpretation of the standard.



-----Original Message-----
From: Dave Thompson [mailto:[EMAIL PROTECTED] 
Sent: Tuesday, January 30, 2007 10:11 AM
To: [email protected]
Subject: NFPA #14 and pressures

NFPA #14 states that when the static pressure at a hose connection exceeds 175 
psi, a pressure regulating device shall be provided to limit the pressure to 
100 psi for 1 ½" hose connections and to 175 psi for all other hose connections.

 

What if the standpipe is a Class III utilizing the fully sprinklered building 
exception allowing 2 ½" hose valves with 1 ½" reducers, caps and chains?

 

Does the pressure need to be limited to 100 psi or 175 psi?

 

 

Dave

 

 

David K. Thompson

Vice President

Allstate Fire Sprinkler, Inc.

P.O. Box 2350

Hartford, CT  06146

Phone = 860-246-7711

Fax = 860-246-7707

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to