excellent question. I put my money on Steve's answer. The NFPA committees that I am on (or familiar with) are aggressively moving away from encouraging occupants to use a hose (which correlates nicely with OSHA requirements).

Roland

On Jan 30, 2007, at 1:02 PM, Steve Leyton wrote:

I think that the sections I referenced are quite clear:

"For Class III systems installed without hose, the water supply requirements shall be as specified for Class I systems."

That would be ALL of the water supply design criteria, including both maximum and minimum pressures.

Steve Leyton
Protection Design & Consulting

The foregoing is the opinion of the writer alone, and does not necessarily represent the intent of the NFPA 14 Technical Committee, nor constitute a formal or informal interpretation of the standard.