Yes, I think it's intended that there be two FHV's available for testing at an 
approved location - ideally the most remote (usually top) of one or more 
standpipes.   Our practice is to furnish a two-way manifold at the top of all 
Class I standpipes, whether they are within a stair enclosure or free-standing 
on the roof.

WRT to the horizontal standpipe issue, I'm not sure and I think it's a great 
question.   On the one hand, the 1000 GPM cap on sprinklered buildings 
rightfully presumes that there will be a controlled fire scene and hose streams 
will be secondary and mop-up.   On the other hand, a horizontal standpipe is a 
completely different hydraulic model (at each floor) than if you took water 
from each of three FHV's that were independently supplied by two or three 
different risers.  

If you put a gun to my head, I'd say 1000 GPM cap on all sprinklered buildings, 
period.   Rich?

Steve Leyton
Protection Design & Consulting

The foregoing is the opinion of the writer alone, and does not necessarily 
represent the intent of the NFPA 14 Technical Committee, nor constitute a 
formal or informal interpretation of the standard.







-----Original Message-----
From: Ron Greenman [mailto:[EMAIL PROTECTED]
Sent: Wednesday, February 07, 2007 7:28 AM
To: [email protected]
Subject: Re: More NFPA 14 - 2003: Max Flow Horiz SP


Sounds like 750 to me if a single pipe and up to 1250 on any common
runs to multiple pipes. What's Leyton say?

On 2/7/07, Fletcher, Ron <[EMAIL PROTECTED]> wrote:
> In a fully sprinklered one story building what is the maximum flow for a
> single Class I horizontal standpipe system with more than three (30
> actual) connections? 750 gpm, 1000 gpm or 1250 gpm.
>
> 7.10.1.1.3 The minimum flow rate for additional standpipes shall be 946
> L/min (250 gpm) per standpipe, with the total not to exceed 4731 L/min
> (1250 gpm) or 3785 L/min (1000 gpm) for buildings sprinklered
> throughout.
>
> 7.10.1.2.2 Where a horizontal standpipe on a Class I and Class III
> system supplies three or more hose connections on any floor, hydraulic
> calculations and pipe sizes for each standpipe shall be based on
> providing 946 L/min (250 gpm) at the three hydraulically most remote
> hose connections on the standpipe and at the topmost outlet of each of
> the other standpipes at the minimum residual pressure required by
> Section 7.8
>
> 7.10.1.2.3 Common supply piping shall be calculated and sized to provide
> the required flow rate for all standpipes connected to such supply
> piping, with the total not to exceed 4731 L/min (1250 gpm).
>
> Ron Fletcher
> Aero Automatic Sprinkler
> Phoenix, AZ
>
> Aero Automatic Sprinkler
>
> PHoenix, AZ
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>


-- 
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to