IBC 903.3.1.1 NFPA 13 Sprinkler Systems.

"Where the provisions of this code REQUIRE that a building OR PORTION
thereof shall be equipped THROUGHOUT with an automatic fire sprinkler
system, sprinklers SHALL be installed THROUGHOUT in accordance with
NFPA-13 EXCEPT as provided in Sections 903.3.1.1.1, 903.3.1.2 and
903.3.1.3"

IBC 903.3.1.1.1 Exempt Locations.

5. "In rooms or AREAS that are of non combustible construction with
wholly noncombustible contents".

Where a building code drives the sprinkler requirement, the provisions
of the building code "trump" those of the referenced standards.

John Drucker
Fire Protection Subcode Official
New Jersey





-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Thursday, February 08, 2007 11:24 AM
To: [email protected]
Subject: Re: INTUMESCENT PAINT

We need to ensure that we are view this issue with the correct lens.

Granted we don't like intumescent paint for a number of reasons AND I  
think the committee was too casual in addressing this issue BUT NFPA  
13 is the document that drives the decision NOT the building code.   
The BC requires fire retardant lumber to be the pressure treated  
type.  That applies to applications where the BC is requiring treated  
lumber.  IN this case, the BC allowed regular timber and since it  
doesn't have additional criteria about it in chap 9 on sprinkler  
systems, the BC is done.  So we go to NFPA 13 to protect the space.   
It says sprinkler protection (the preferred and best option) OR you  
can use treated lumber as per NFPA 703.  Guess what boys and girls,  
NFPA 703 addresses both pressure treated and COATED applications.  As  
such, coated fire retardant treatment can be used (as much as I hated  
typing that but read on).

Some notes to those involved with it's use.  NFPA 703 has  
restrictions on the type of coating  when used in a high humidity  
location.  IT also says it must be MAINTAINED to retain the  
effectiveness of the treatment under the service conditions (which  
would be for he life of the building).   Does anyone have any  
experience with it to 'splain what that entails???  As an AHJ, I'd  
require something in writing from the owner showing they are aware of  
this issue and stating it will be done.

Roland

On Feb 8, 2007, at 6:03 AM, Vince Sabolik wrote:

>
>> Thank you forum ...
>
> ... for the enlightenment and code references regarding use of  
> intumescent paint in
> lieu of attic sprinklers.  Somebody 'in authority' actually made  
> this decision.
>
> I wonder if it costs more for a 'faux' finish?
>
>

>                     Vince
>
>
>
>
>
> Vince Sabolik
> Christi Fire Protection, Inc.
> 11351 Pearl Road
> Strongsville, Ohio 44136
>
> T 440 572-7730  F 440 572-7719  Email:  
> <mailto:[EMAIL PROTECTED]>[EMAIL PROTECTED]
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to