FYI The distance from a fitting or valve is only a "should" not a shall. There 
are no UL or NFPA requirements regarding distance. There are a number of riser 
assemblies on the market that put the switch closer than the stated 24" from a 
valve or drain. If the switch works during the test after installation it's a 
good installation.

Mike Cabral

---- Steve Leyton <[EMAIL PROTECTED]> wrote: 
> Look at the tech data sheet for the switch.  For Potter Signal products in 
> the installation guidelines ...
> 
> Steve Leyton
> Protection Design & Consulting
>  
> 
> -----Original Message-----
> From: Loren Johnson [mailto:[EMAIL PROTECTED]
> Sent: Thursday, February 08, 2007 11:06 AM
> To: Sprinkler Forum
> Subject: WATERFLOW SWITCHES
> 
> 
> Forum:
> 
> Can anyone direct me to where it indicates that a
> waterflow switch for a wet pipe system has to be so
> many inches away from the control valve or an
> elbow/tee?  
> 
> I seem to have seen this somewhere before, but now I
> am unable to locate it. I thought it was in a pre-
> vious edition of 13, but I'm not sure.
> 
> Thank you.
> 
> 
> Loren Johnson - CFPS, CET
> Fire Protection System Consultant
> The Hitchcock Company
> Peoria, IL
> 
> 
>  
> ____________________________________________________________________________________
> Do you Yahoo!?
> Everyone is raving about the all-new Yahoo! Mail beta.
> http://new.mail.yahoo.com
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to