FYI The distance from a fitting or valve is only a "should" not a shall. There are no UL or NFPA requirements regarding distance. There are a number of riser assemblies on the market that put the switch closer than the stated 24" from a valve or drain. If the switch works during the test after installation it's a good installation.
Mike Cabral ---- Steve Leyton <[EMAIL PROTECTED]> wrote: > Look at the tech data sheet for the switch. For Potter Signal products in > the installation guidelines ... > > Steve Leyton > Protection Design & Consulting > > > -----Original Message----- > From: Loren Johnson [mailto:[EMAIL PROTECTED] > Sent: Thursday, February 08, 2007 11:06 AM > To: Sprinkler Forum > Subject: WATERFLOW SWITCHES > > > Forum: > > Can anyone direct me to where it indicates that a > waterflow switch for a wet pipe system has to be so > many inches away from the control valve or an > elbow/tee? > > I seem to have seen this somewhere before, but now I > am unable to locate it. I thought it was in a pre- > vious edition of 13, but I'm not sure. > > Thank you. > > > Loren Johnson - CFPS, CET > Fire Protection System Consultant > The Hitchcock Company > Peoria, IL > > > > ____________________________________________________________________________________ > Do you Yahoo!? > Everyone is raving about the all-new Yahoo! Mail beta. > http://new.mail.yahoo.com > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum