I have been told that when the flow switch is too close to an alarm valve
the sudden flow can damage or tear off the vane. Just what I was told once,
notta clue if it's a valid concern 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Thursday, February 08, 2007 6:26 PM
To: [email protected]
Subject: Re: WATERFLOW SWITCHES

I suspect their use of the term LAMINAR FLOW is being applied too casually.
It actually occurs only at very low flows.  In a 1 inch pipe its maximum is
around 1 gpm.  I assume the concern was excessive turbulence (whether real
or probably just imagined since listed assemblies can be much closer).

Roland

On Feb 8, 2007, at 3:13 PM, Thom McMahon wrote:

> I believe the distance was 5 pipe dia., this came originally from 
> those pesky Mech. engineers, and was to allow the turbulence from the 
> valve to subside, into a more laminar flow, which at the time was 
> considered necessary for the operation of vane water flow switches. 
> Since we want to measure any flow (as low as .7 gpm or less for some 
> MFG.'s) Turbulent flow actually is more likely to activate the vane 
> switch than laminar flow at those low flow rates, hence the very short 
> distance from the valves to the FS in the riser assemblies, and floor 
> control assemblies.
>
> I believe I have correctly re-stated the info given to me by the 
> Potter rep. at the last convention.
>
> Thom McMahon
> Firetech, Inc.
> 2560 Copper Ridge Dr
> Steamboat Springs, CO 80488-2136
> Tel: 970-879-7952
> Fax: 970-879-7926
> ----- Original Message ----- From: "Roland Huggins"  
> <[EMAIL PROTECTED]>
> To: <[email protected]>
> Sent: Thursday, February 08, 2007 4:00 PM
> Subject: Re: WATERFLOW SWITCHES
>
>
>> once upon a midnight dreary, the listing required vane type water   
>> flow switches to be a minimum distance away from the main  
>> drain.    Although, if the same switch was part of a listed  
>> shotgun riser  assembly, it could be installed much closer to the 
>> main drain.  I  haven't  looked lately.
>>
>> Truth can be stranger than fiction.
>>
>> Roland
>>
>> On Feb 8, 2007, at 11:38 AM, <[EMAIL PROTECTED]>   
>> <[EMAIL PROTECTED]> wrote:
>>
>>> FYI The distance from a fitting or valve is only a "should" not a  
>>> shall. There are no UL or NFPA requirements regarding distance.  
>>> There are a number of riser assemblies on the market that put the  
>>> switch closer than the stated 24" from a valve or drain. If the  
>>> switch works during the test after installation it's a good  
>>> installation.
>>>
>>> Mike Cabral
>>>
>>> ---- Steve Leyton <[EMAIL PROTECTED]> wrote:
>>>> Look at the tech data sheet for the switch.  For Potter Signal   
>>>> products in the installation guidelines ...
>>>>
>>>> Steve Leyton
>>>> Protection Design & Consulting
>>>>
>>>>
>>>> -----Original Message-----
>>>> From: Loren Johnson [mailto:[EMAIL PROTECTED]
>>>> Sent: Thursday, February 08, 2007 11:06 AM
>>>> To: Sprinkler Forum
>>>> Subject: WATERFLOW SWITCHES
>>>>
>>>>
>>>> Forum:
>>>>
>>>> Can anyone direct me to where it indicates that a waterflow switch 
>>>> for a wet pipe system has to be so many inches away from the 
>>>> control valve or an elbow/tee?
>>>>
>>>> I seem to have seen this somewhere before, but now I am unable to 
>>>> locate it. I thought it was in a pre- vious edition of 13, but I'm 
>>>> not sure.
>>>>
>>>> Thank you.
>>>>
>>>>
>>>> Loren Johnson - CFPS, CET
>>>> Fire Protection System Consultant
>>>> The Hitchcock Company
>>>> Peoria, IL
>>>>
>>>>
>>>>
>>>> ___________________________________________________________________
>>>> __ _______________
>>>> Do you Yahoo!?
>>>> Everyone is raving about the all-new Yahoo! Mail beta.
>>>> http://new.mail.yahoo.com
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>>
>>>>
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to