Propane has a much longer shelf life, and most facilities do not "test run" 
their generator sets weekly (or maybe ever). Also it doesn't smoke like a 
deisel and requires less maintenance.
Mark at aero

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] Behalf Of
[EMAIL PROTECTED]
Sent: Friday, February 16, 2007 8:36 AM
To: [email protected]
Subject: RE: back-up power


Why propane versus the more common and probably cheaper diesel?
Environmental issues, i.e. exhaust? 

Is your primary power source considered non-reliable thus necessitating
a secondary backup source?  


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams - work
Sent: Friday, February 16, 2007 9:39 AM
To: [email protected]
Subject: back-up power

I am working on a project where an electric fire pump (diesel not an
option) and tank is the only source of water for the sprinkler system.
The primary supply is the public utility and the back-up is to come from
an on-site generator. The builder is proposing to use a propane-fired
generator. I looked in NFPA 20 and 110 and didn't see anything saying
this was a no-no. Is there a problem with this arrangement?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to