The charts that I have show a 5/8" meter rated for 20 gpm and a 3/4" meter
rated for 30 gpm.  These charts are for NEPTUNE water meters which our local
purveyor uses.  This being the case, two RES sprinklers will create more
flow than the 5/8" meter is rated for, and in most cases two sprinklers will
max out the rated flow on the 3/4", but they would be under the rating by
about 4 gpm.  Roof pitches over 4/12 and sprinklers over 155 F will also
produce flows beyond the 30 gpm.  The two sprinklers in most situations will
be limited to 16 x 16 or less.  So, it seems that the 5/8" meter is not an
option, and that the 3/4" meter is pushing the edge.

Bob Knight

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of art
Sent: Friday, March 09, 2007 8:29 AM
To: [email protected]
Subject: RE: Pandora's Box

A 3/4" water supply will probably not be capable of supplying two
sprinklers. You need to have a friction loss graph for the meter. Do the
hydraulic calcs to show what it will provide then show the required pipe
size to allow the system to work. 
Art - ATCO Fire Protection Design


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Chris Brown
Sent: Friday, March 09, 2007 10:19 AM
To: [email protected]
Subject: Pandora's Box

Question to the forum:
What effect does a 5/8 inch or 3/4 inch water meter have on fire sprinkler
system installed in an NFPA 13D or NFPA 13R system. The issue is one of the
maximum continuous flow thru the meter and its effect on the ability of the
fire sprinkler system to operate as intended. I respectfully request, Please
research and answer after you have visited with the water meter
manufacturer's and or water departments as I have already done. Keep in mind
that a single residential sprinkler has a minimum of some where between 19
and 25 gpm requirements and that most dwellings have two sprinklers flowing
in the hydraulically remote area.
 
This will be fun for a Friday:)

Thank you,

Chris Brown
Fire Protection Designer
Please note our new company name, e-mail address and web site.

 

innovative leader    ▲     trusted partner

19910 West 161st Street 
Olathe, KS  66062 
Office:  913.829.8650

Direct:
Cell: 
Fax:

913.747.2056
913.208.3600
913.829.8690

www.poolefire.com <http://www.poolefire.com/> 
Office Map
<http://www.mapquest.com/maps/map.adp?address=19910%20W%20161st%20St&city=Ol
athe&state=KS&zipcode=66062-2700&country=US&title=%3cb%3e19910%20W%20161st%2
0St%3c/b%3e%3cbr%20/%3e%20Olathe,%20KS%2066062-2700,%20%20US&cid=lfmaplink2&
name=> 

This e-mail, and any files transmitted with it, are confidential and
intended solely for the use of the individual or entity to which they are
addressed.  If you have received this e-mail in error, please notify
[EMAIL PROTECTED]

 


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

-- 
No virus found in this incoming message.
Checked by AVG Free Edition.
Version: 7.5.446 / Virus Database: 268.18.7/713 - Release Date: 3/7/2007
9:24 AM
 

-- 
No virus found in this outgoing message.
Checked by AVG Free Edition.
Version: 7.5.446 / Virus Database: 268.18.7/713 - Release Date: 3/7/2007
9:24 AM
 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to