Paul,
I was thinking that based on the test results & .2/1500 x 1.4 + 250 hose =
670 GPM (45 psi from curve). 45 psi - 5psi for BFP - 5psi fro elevation
(12') 40% (friction & etc) = 17 psi. Why wouldn't 16x16 EC heads work (13.3
end head pressure)?
Regards,
Brian Harris
First Defense Fire Protection
Design Engineer
[EMAIL PROTECTED]
704.948.3506 phone
704.948.3507 fax
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Paul Pinigis
Sent: Tuesday, March 27, 2007 9:58 AM
To: [email protected]
Subject: RE: Selecting Heads For a New System
Ok, with the pressure that you have available, you can pretty much
forget extended coverage sprinklers. The area per sprinkler that gave
you will require the minimum end-head pressure of 7 psi. If you have a
cushion, you can increase the area per sprinkler as long as you stay
under the curve.
Paul J. Pinigis, P.E.
Chief Life Safety Engineer
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian
Harris
Sent: Tuesday, March 27, 2007 9:52 AM
To: [email protected]
Subject: RE: Selecting Heads For a New System
I'm looking for a way to take the given information (static, residual,
flow)
for a given job and come up with a head spacing (standard or extended
coverage) that will work.
Regards,
Brian Harris
First Defense Fire Protection
Design Engineer
[EMAIL PROTECTED]
704.948.3506 phone
704.948.3507 fax
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Paul
Pinigis
Sent: Tuesday, March 27, 2007 9:46 AM
To: [email protected]
Subject: RE: Selecting Heads For a New System
I don't know if this is what you are looking for, but if you use a
sprinkler with a k-factor of 8.0 then the optimum area per sprinkler (to
minimize pressure demand) is 106 square feet. Maybe a 10 x 10.5 foot
spacing.
The approach that you take will differ depending upon the ALL of the
factors associated with the project. A holistic approach to each
project is needed.
Paul J. Pinigis, P.E.
Chief Life Safety Engineer
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian
Harris
Sent: Tuesday, March 27, 2007 8:35 AM
To: [email protected]
Subject: Selecting Heads For a New System
Let me start by saying I've only been in the sprinkler world for just
over a
year so if any thing I ask is "rookie-ish" please keep that in mind. I'm
looking for ideas that some of you may use when starting a new project
when
it comes to selecting what heads (head spacing) to use. For example: I
am
starting a retail store (mercantile) that has a Static of 47 psi
Residual of
42 psi, & flow of 1090 gpm. What I do now to get me "in the ballpark" is
take the density x area of operation x 1.4 (for overage) + hose
allowance.
That gets me roughly the system gpm demand. So .20 x 1500 = 300 x 1.4 =
420
+ 250 (hose) = 670 gpm. I then plot that gpm on my water supply curve
(N1.85) to get the psi for that gpm; in this case that's around 45psi.
From
that psi I take out for the BFP, elevation, 40% (friction loss & etc)
and
whatever is left I find a head with an end head pressure that's slightly
under that and away I go.... Any thoughts? Suggestions? Better Ideas?
Regards,
Brian Harris
First Defense Fire Protection
<mailto:[EMAIL PROTECTED]> [EMAIL PROTECTED]
704.948.3506 phone
704.948.3507 fax
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum