If your required density is 0.20 gpm/sq. ft., a 5.6 k-factor will
require 21.55 psi minimum for 130 sq. ft.  With the flow data that you
described this may be a waste of precious pressure (say that three times
fast!).

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Tuesday, March 27, 2007 10:10 AM
To: [email protected]
Subject: RE: Selecting Heads For a New System

The smaller the K factor the lower the flow accumulation (based on equal
spacing) and orifices smaller than 1/2" are verboten for OH.

You could always develop a hydraulic pipe schedule using different EHP's
to get an idea of the impact on pipe size. You wouldn't want to burn a
lot of the available pressure on the end head and then have a 6" riser.

Ron Fletcher
Aero Automatic
Phoenix, AZ

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian
Harris
Sent: Tuesday, March 27, 2007 7:06 AM
To: [email protected]
Subject: RE: Selecting Heads For a New System

Ron,
What did you use to come up with 5.6k heads?

           Regards,
              Brian Harris
First Defense Fire Protection
        Design Engineer
   [EMAIL PROTECTED]
           704.948.3506 phone
           704.948.3507 fax

 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Tuesday, March 27, 2007 10:00 AM
To: [email protected]
Subject: RE: Selecting Heads For a New System

I think your 40% overage is way too high based on the flow test. A good
design oops, layout will limit the overage to less than 20%. Your not
going to use 20 x 20 EC's because of the flow test and the smaller the K
factor the lower the accumlation in the system so I would recommend 1/2"
5.6K heads at 130 max.

Ron Fletcher
Aero Automatic
Phoenix, AZ 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian
Harris
Sent: Tuesday, March 27, 2007 5:35 AM
To: [email protected]
Subject: Selecting Heads For a New System

Let me start by saying I've only been in the sprinkler world for just
over a year so if any thing I ask is "rookie-ish" please keep that in
mind. I'm looking for ideas that some of you may use when starting a new
project when it comes to selecting what heads (head spacing) to use. For
example: I am starting a retail store (mercantile) that has a Static of
47 psi Residual of
42 psi, & flow of 1090 gpm. What I do now to get me "in the ballpark" is
take the density x area of operation x 1.4 (for overage) + hose
allowance.
That gets me roughly the system gpm demand.  So .20 x 1500 = 300 x 1.4 =
420
+ 250 (hose) = 670 gpm.  I then plot that gpm on my water supply curve
(N1.85) to get the psi for that gpm; in this case that's around 45psi.
>From that psi I take out for the BFP, elevation, 40% (friction loss &
etc) and whatever is left I find a head with an end head pressure that's
slightly under that and away I go.... Any thoughts? Suggestions? Better
Ideas? 

 

           Regards,

              Brian Harris
First Defense Fire Protection


   <mailto:[EMAIL PROTECTED]> [EMAIL PROTECTED]
           704.948.3506 phone
           704.948.3507 fax



 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to