Design 101: Always remember that if the number of heads for a project
remains the same, and the number of branch lines is less the job costs less
to install.
Minimize the number of branchlines by maximizing the spacing between branch
lines, an allowing the heads on the branch lines to move closer together.
Recognize the use of your design. Retail in a mall? Lots of tenant changes,
smaller head spacing means more flexibility for the next tenant. End user
store, they'll probably be there for 20 years, maximize the coverage, you
don't need flexibility for the next tenant.
AFSA and NFSA both have designer training which is where you should really
be asking these types of questions. Every contractor has there own approach
to this depending on their preferred products, and preferred installation
methods. Get a mentor! AFSA may be able to help you locate one near you,
someone with experience that can work with you one on one. While this forum
is a wonderful resource, it can't provide the level of training your in need
of.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message -----
From: "Brian Harris" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Tuesday, March 27, 2007 7:52 AM
Subject: RE: Selecting Heads For a New System
I'm looking for a way to take the given information (static, residual,
flow)
for a given job and come up with a head spacing (standard or extended
coverage) that will work.
Regards,
Brian Harris
First Defense Fire Protection
Design Engineer
[EMAIL PROTECTED]
704.948.3506 phone
704.948.3507 fax
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Paul
Pinigis
Sent: Tuesday, March 27, 2007 9:46 AM
To: [email protected]
Subject: RE: Selecting Heads For a New System
I don't know if this is what you are looking for, but if you use a
sprinkler with a k-factor of 8.0 then the optimum area per sprinkler (to
minimize pressure demand) is 106 square feet. Maybe a 10 x 10.5 foot
spacing.
The approach that you take will differ depending upon the ALL of the
factors associated with the project. A holistic approach to each
project is needed.
Paul J. Pinigis, P.E.
Chief Life Safety Engineer
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian
Harris
Sent: Tuesday, March 27, 2007 8:35 AM
To: [email protected]
Subject: Selecting Heads For a New System
Let me start by saying I've only been in the sprinkler world for just
over a
year so if any thing I ask is "rookie-ish" please keep that in mind. I'm
looking for ideas that some of you may use when starting a new project
when
it comes to selecting what heads (head spacing) to use. For example: I
am
starting a retail store (mercantile) that has a Static of 47 psi
Residual of
42 psi, & flow of 1090 gpm. What I do now to get me "in the ballpark" is
take the density x area of operation x 1.4 (for overage) + hose
allowance.
That gets me roughly the system gpm demand. So .20 x 1500 = 300 x 1.4 =
420
+ 250 (hose) = 670 gpm. I then plot that gpm on my water supply curve
(N1.85) to get the psi for that gpm; in this case that's around 45psi.
From
that psi I take out for the BFP, elevation, 40% (friction loss & etc)
and
whatever is left I find a head with an end head pressure that's slightly
under that and away I go.... Any thoughts? Suggestions? Better Ideas?
Regards,
Brian Harris
First Defense Fire Protection
<mailto:[EMAIL PROTECTED]> [EMAIL PROTECTED]
704.948.3506 phone
704.948.3507 fax
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum