Yup, gotta love those K14.0's 13.3 psi @ 16'X16' for .20.... Oh how sweet it is...
Jamie Seidl Affordable Fire Protection, Inc. Project Manager P - (800) 862-7860 F - (704) 892-0157 -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Paul Pinigis Sent: Tuesday, March 27, 2007 10:31 AM To: [email protected] Subject: RE: Selecting Heads For a New System If you have an ECOH with a k-factor of 14 it could be done. I like that approach. Paul J. Pinigis, P.E. Chief Life Safety Engineer -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Brian Harris Sent: Tuesday, March 27, 2007 10:13 AM To: [email protected] Subject: RE: Selecting Heads For a New System Paul, I was thinking that based on the test results & .2/1500 x 1.4 + 250 hose = 670 GPM (45 psi from curve). 45 psi - 5psi for BFP - 5psi fro elevation (12') 40% (friction & etc) = 17 psi. Why wouldn't 16x16 EC heads work (13.3 end head pressure)? Regards, Brian Harris First Defense Fire Protection Design Engineer [EMAIL PROTECTED] 704.948.3506 phone 704.948.3507 fax -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Paul Pinigis Sent: Tuesday, March 27, 2007 9:58 AM To: [email protected] Subject: RE: Selecting Heads For a New System Ok, with the pressure that you have available, you can pretty much forget extended coverage sprinklers. The area per sprinkler that gave you will require the minimum end-head pressure of 7 psi. If you have a cushion, you can increase the area per sprinkler as long as you stay under the curve. Paul J. Pinigis, P.E. Chief Life Safety Engineer -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Brian Harris Sent: Tuesday, March 27, 2007 9:52 AM To: [email protected] Subject: RE: Selecting Heads For a New System I'm looking for a way to take the given information (static, residual, flow) for a given job and come up with a head spacing (standard or extended coverage) that will work. Regards, Brian Harris First Defense Fire Protection Design Engineer [EMAIL PROTECTED] 704.948.3506 phone 704.948.3507 fax -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Paul Pinigis Sent: Tuesday, March 27, 2007 9:46 AM To: [email protected] Subject: RE: Selecting Heads For a New System I don't know if this is what you are looking for, but if you use a sprinkler with a k-factor of 8.0 then the optimum area per sprinkler (to minimize pressure demand) is 106 square feet. Maybe a 10 x 10.5 foot spacing. The approach that you take will differ depending upon the ALL of the factors associated with the project. A holistic approach to each project is needed. Paul J. Pinigis, P.E. Chief Life Safety Engineer -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Brian Harris Sent: Tuesday, March 27, 2007 8:35 AM To: [email protected] Subject: Selecting Heads For a New System Let me start by saying I've only been in the sprinkler world for just over a year so if any thing I ask is "rookie-ish" please keep that in mind. I'm looking for ideas that some of you may use when starting a new project when it comes to selecting what heads (head spacing) to use. For example: I am starting a retail store (mercantile) that has a Static of 47 psi Residual of 42 psi, & flow of 1090 gpm. What I do now to get me "in the ballpark" is take the density x area of operation x 1.4 (for overage) + hose allowance. That gets me roughly the system gpm demand. So .20 x 1500 = 300 x 1.4 = 420 + 250 (hose) = 670 gpm. I then plot that gpm on my water supply curve (N1.85) to get the psi for that gpm; in this case that's around 45psi. From that psi I take out for the BFP, elevation, 40% (friction loss & etc) and whatever is left I find a head with an end head pressure that's slightly under that and away I go.... Any thoughts? Suggestions? Better Ideas? Regards, Brian Harris First Defense Fire Protection <mailto:[EMAIL PROTECTED]> [EMAIL PROTECTED] 704.948.3506 phone 704.948.3507 fax _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum