Brian,
First off, welcome to the club.
Secondly, does this mercantile space have a drop ceiling? If so, that
may dictate your spacing somewhat, especially if they want center of tile.
Overages can be tricky; it depends a lot on the building
configuration, location of rooms, etc. A set of plans came across my
desk yesterday with a 0.15/900 demand, which would equate to a base
of 135 gpm. The demand flow in the sprinkler system is 229 gpm,
almost a 70% overage. It was completely appropriate based on the
configuration. If I need to estimate the water demand, what I like to
do is lay out the sprinklers first, using the ceiling plan and the
NFPA standards. From there I would locate the remote area, count the
number of sprinklers in that area and multiply it by the minimum
flow. I would assign the overage from that figure; typically 10% for
grids and 25% for trees. (In the example I cited above, there were 12
sprinklers at a flow of 18 gpm per sprinkler, or a total of 216 gpm.
Therefore the actual flow of 229 gpm was only a 6% overage. My
estimate would have been 216 x 1.25 = 270 gpm.)
It's not an exact science, so accept it as that. I hope this helps.
Todd
Let me start by saying I've only been in the sprinkler world for just
over a
year so if any thing I ask is "rookie-ish" please keep that in mind. I'm
looking for ideas that some of you may use when starting a new project
when
it comes to selecting what heads (head spacing) to use. For example: I
am
starting a retail store (mercantile) that has a Static of 47 psi
Residual of
42 psi, & flow of 1090 gpm. What I do now to get me "in the ballpark" is
take the density x area of operation x 1.4 (for overage) + hose
allowance.
That gets me roughly the system gpm demand. So .20 x 1500 = 300 x 1.4 =
420
+ 250 (hose) = 670 gpm. I then plot that gpm on my water supply curve
(N1.85) to get the psi for that gpm; in this case that's around 45psi.
From
that psi I take out for the BFP, elevation, 40% (friction loss & etc)
and
whatever is left I find a head with an end head pressure that's slightly
under that and away I go.... Any thoughts? Suggestions? Better Ideas?
Regards,
Brian Harris
First Defense Fire Protection
Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum