A.8.5.5.3  Frequently, additional sprinkler equipment can be avoided by
reducing the width of decks or galleries and providing proper clearances.
Slatting of decks or walkways or the use of open grating as a substitute for
automatic sprinklers thereunder is not acceptable. 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Rod DiBona
Sent: Thursday, April 05, 2007 10:07 AM
To: [email protected]
Subject: open grate flooring

I am working on a large jail project where the architect has asked me to
provide value engineering ideas. One of the things that I am considering
bringing to his attention is the possibility of turning their upper cell
walkway into an open grate flooring of 4' or less. I was pretty sure that
this would eliminate the need for sprinklers under these walkways but I
wanted to substantiate it before I presented it. NFPA 13 02 edition
8.5.5.3.1 states " Sprinklers shall be installed under fixed obstructions
over 4ft wide such as ducts, decks, open grate flooring, cutting tables, and
overhead doors". Am I correct in assuming that if these "floors" are 4' or
less that sprinks will  not be required? I thought that I remembered that
there were other requirements such as percentage or size of openings
similiar to the meshing in nursing home curtains but I can't find it
anywhere. Any help is appreciated.
 
Thanks,
 
Rod DiBona
Rapid Fire Protection
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

--
No virus found in this incoming message.
Checked by AVG Free Edition.
Version: 7.5.446 / Virus Database: 268.18.26/746 - Release Date: 4/4/2007
1:09 PM
 

-- 
No virus found in this outgoing message.
Checked by AVG Free Edition.
Version: 7.5.446 / Virus Database: 268.18.26/746 - Release Date: 4/4/2007
1:09 PM
 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to