Tom, I believe the temperature he is describing is of the chip not the room.
The room can be 75F and the chip can be 300F if the fans aren't working
properly in the rack unit.  He should get into one of his IT boards and ask
his buds how many of them have had accidental discharges from the sprinklers
in their server rooms...or ask his insurance carrrier... or the local fire
department.  Any of them should be able to let him know that accidental
discharges happen in movies.  He's not in movies, is he?
Are you assuming extra liability by installing a high temperature head in a
closet ?

Garth

----- Original Message ----- 
From: "Thom McMahon" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Thursday, April 05, 2007 2:01 PM
Subject: Re: Server Closet


> Tom:
>
> We had the same issue recently. We provided a 360'F head located at the
door
> access (4" off wall, with head guard) We had asked the IT guy at what temp
> was all his stuff fried anyway, and he said anything over 300'F and it all
> had to be replaced. Hence the 360'F head. Where it's located at the
doorway
> it is protected from most possible damage by the lintel over the door and
> the guard is just incidental. Any small leak or drip would drop straight
> down and not on any equipment.
>
> If your dead set against a wet head, I think there are Intergin Balls out
> there for confined spaces, like boat engine rooms ect.
>
> Thom McMahon
> Firetech, Inc.
> 2560 Copper Ridge Dr
> Steamboat Springs, CO 80488-2136
> Tel: 970-879-7952
> Fax: 970-879-7926
> ----- Original Message ----- 
> From: "Tom Duross" <[EMAIL PROTECTED]>
> To: "SprinklerForum" <[email protected]>
> Sent: Thursday, April 05, 2007 12:49 PM
> Subject: Server Closet
>
>
> >I was wondering if I could get recommendations of advice to give a
client.
> > Their IT guy is bugging them about a head we put in a server closet.
> > It's just a 6' w x 3' deep closet with their rack and a little ductless
ac
> > unit.
> > No raised floor, liebert or big ups equipment and certainly not sealed.
> > I offered high temp head but they're scared about water (wata).
> > Should I suggest total flooding inergen?  Low temp rate of rise heat
> > detector?
> > I have to have an exhaust system installed with inergen, right?
> > I think they'd have to enclose the closet to keep in the gas.
> >
> > Thanks,
> >
> > Tom Duross
> > Go Red Sox
> >
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > To Unsubscribe, send an email
to:[EMAIL PROTECTED]
> > (Put the word unsubscribe in the subject field)
> >
> >
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to