I tend to agree Thom. Yes the chip is fried, but so is the wiring and everything else at 300'F. The response of the sprinkler head is minimally affected in a 12 Sf room by the higher temperature listing, but it gives the IT dude a warm fussy. I saw some suggestions of installing the Equip in cabinets. While special Cabinets do exist for servers, they are very expensive, and they have problems controlling temperature in the server. The biggest killer of servers is heat. not from fire, but self generated heat they can't get rid of fast enough. IT magazine had an article on the server's at Microsoft or Intel and the way that the input and output cables arrangement could block or disrupt air flow over the server, and cause it to over heat. Spend the money on more A/C and leave the 360'F sprinkler in place.
Thom McMahon Firetech, Inc. 2560 Copper Ridge Dr Steamboat Springs, CO 80488-2136 Tel: 970-879-7952 Fax: 970-879-7926 ----- Original Message ----- From: "Garth W. Warren" <[EMAIL PROTECTED]> To: <[email protected]> Sent: Thursday, April 05, 2007 5:39 PM Subject: Re: Server Closet > Tom, I believe the temperature he is describing is of the chip not the > room. > The room can be 75F and the chip can be 300F if the fans aren't working > properly in the rack unit. He should get into one of his IT boards and > ask > his buds how many of them have had accidental discharges from the > sprinklers > in their server rooms...or ask his insurance carrrier... or the local fire > department. Any of them should be able to let him know that accidental > discharges happen in movies. He's not in movies, is he? > Are you assuming extra liability by installing a high temperature head in > a > closet ? > > Garth > > >> Tom: >> >> We had the same issue recently. We provided a 360'F head located at the > door >> access (4" off wall, with head guard) We had asked the IT guy at what >> temp >> was all his stuff fried anyway, and he said anything over 300'F and it >> all >> had to be replaced. Hence the 360'F head. Where it's located at the > doorway >> it is protected from most possible damage by the lintel over the door and >> the guard is just incidental. Any small leak or drip would drop straight >> down and not on any equipment. >> >> If your dead set against a wet head, I think there are Intergin Balls out >> there for confined spaces, like boat engine rooms ect. >> >> Thom McMahon >> >> >> >> >I was wondering if I could get recommendations of advice to give a > client. >> > Their IT guy is bugging them about a head we put in a server closet. >> > It's just a 6' w x 3' deep closet with their rack and a little ductless > ac >> > unit. >> > No raised floor, liebert or big ups equipment and certainly not sealed. >> > I offered high temp head but they're scared about water (wata). >> > Should I suggest total flooding inergen? Low temp rate of rise heat >> > detector? >> > I have to have an exhaust system installed with inergen, right? >> > I think they'd have to enclose the closet to keep in the gas. >> > >> > Thanks, >> > >> > Tom Duross >> > Go Red Sox >> > >> > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)