Below is a direct quote from NFPA 14 2007 edition.

7.10.1.1.1 For Class I and Class III systems, the minimum flow rate for the 
hydraulically most remote standpipe shall be 500gpm, and the calculation 
procedure shall be inaccordance with 7.10.1.2

7.10.1.1.3 The minimum flow rate for additional standpipes shall be 250 gpm per 
standpipe, with the total not to exceed 1250gpm or 1000 gpm for buildings 
sprinklered throughout

My question is for a sprinklered building what is the total standpipe system 
flow rate 1000gpm or 1500gpm? The "total" referred to in 7.10.1.1.3 can be 
interrupted as referring to only the additional standpipes.  So you would have 
1000gpm in additional standpipes and 500 for the most remote?

Thoughts???