Greg:
I believe that that was what Tom D. was thinking of submitting for TIA.
Basically sizing the inlets based upon the output demand. (21/2" hose valve
will put out 250 Gpm then 1 - 21/2" inlet for each 250 Gpm demand or proof
that the number supplied will support the designed output.
It was several weeks ago and I don't remember the exact wording.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message -----
From: "Greg McGahan" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Wednesday, April 11, 2007 6:14 AM
Subject: RE: Manual wet standpipes
Along these same lines, why doesn't the code dictate FDC sizes based on
system demand?
For instance if there is one FDC feeding 3 standpipes I believe that 14
should require a minimum of a 3 way FDC to eliminate confusion and
argument.
Greg
Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Tom Duross
Sent: Wednesday, April 11, 2007 7:04 AM
To: [email protected]
Subject: RE: Manual wet standpipes
Aren't FDC's required to be within 150' of a hydrant? In the city?
I thought so or lanes need to be widened or an auxiliary hydrant provided
on
the building (sized for what flow?).
I know when I submit shop drawings, I have to state the distance in each
direction to hydrants on the site plan.
Maybe that's just me.
We've added a 3rd line through a lower FDV when we can't get the volume or
used a wye on the FDC.
Outside hose losses can be substantial, I gauge the suction hydrant and
the
FDC usually.
I attribute some to excess hose looped around and around.
Tom
GRS
If they pump them at all. I still run across protected properties where
the
fire department fails to stretch hoselines to, no less pump the FDC.
The goal is to supply the correct operating pressure to the nozzle. To do
that one needs to consider a number of factors; friction losses from the
Pumper outlet to the FDC, Standpipe and the Attack hoselines, Elevation
losses and the required Nozzle Pressure. Many departments use automatic
nozzles, some smooth bore, some combination breakways. The Nozzle pressure
of these appliances vary.
In the end its "failure to plan is a plan to fail". Meridian Plaza showed
us
what can and will go wrong.
Fire Departments and Fire Officials need to get out to each property and
FLOW standpipes at a minimum of the highest and or furthest outlet and
then
WRITE the information gained into their PREPLANS. Preplanning is the
solution, the building code and NFPA-14 have given us the tools.
Before we start talking about advanced hydraulics, and Rich we better
stick
with volume for now, we need to educate the fire department as to proper
standpipe operations. A single 2-1/2 hoseline to an FDC may not be enough,
the FDC has two 2-1/2 inlets for a reason. 150 psi at the pumper outlet
may
not be enough. Typical automatic and some breakaway 1-3/4 nozzles can flow
upwards of 200-250 GPM and many departments operate two handlines off a 10
foot pony gated wye arrangement so 500 GPM can be expected.
In my jurisdiction standpipe systems are flow tested at the time of final
acceptance, with and without the automatic water source and utilizing a
fire
department pumper. Lastly a building walkthru with the fire department is
essential.
And yes tankers have wheels in the east.
John Drucker
Fire Protection Subcode Official
Red Bank, NJ
I won't disagree but I did have a small caveat so as to not denigrate the
folks in 482 sq. mi. areas. "But the initial setup can take some time and
that's a function of how far you are from your neighboring FD's."
So in your case you can do 1000 gpm and I bet you can. But your set up
time
to get 5-6 tankers/tenders (assuming sustained 200 gpm a piece) is 30-60
minutes from your call for the tenders which may very well be 20 minutes
after the initial call for fire. Then again with a 4 mile round trip 200
gpm might stretch it a bit considering a 10 minute dump drive fill drive
cycle on a 2000 gpm tank. Around here my set up time is about 5-20
minutes
until I get to a sustained 1000 gpm with no more than 5 minutes from the
initial call for fire.
And for those that wonder about the tanker/tender east vs. west. In the
west tankers have wings. In many parts of the east we'd have no clue what
to call a fire fighting apparatus with wings but a UFO. Although as a FF
for the DOD at West Point Military Academy for a time we called them
Blackhawks and Huey's. And it's damn hard to get the water drop from a
west
coast tanker into the draft tank.
Chris
Chris:
Loved your dissertation up till the end, about the tanker/tender shuttle.
Our Fire District is about 482 Sq Miles, all the surrounding districts are
of similar size. We have a single 2200 Gal Tender 1984, most of the other
districts have the same. When our FDP finally arrives at a fire, sometimes
20 min. after the call, the haul distance for the tenders if often over 4
miles round trip, and that can very well be from a draft. Can't even keep
250 Gpm going until the second tender arrives (about 30 Min. later). I'd
love to see a 1000 Gpm tender operation, but it will never happen here.
On the same note we only have standpipes where there is water. Go figure?
Thom McMahon
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)