Tony,
I assume you have a unlimited area F-2 (non-spinklered, one story with the
required public way/yard widths), that's how you're getting the 300K sq. ft.
unsprinklered bldg (507.2 in 2006 IBC)? If that's the case, where are you
getting the "where required" standpipe requirement from the building code? I
don't see it, is that a local requirement?

Richard Malek
[EMAIL PROTECTED]


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] Behalf Of A.P.Silva
Sent: Monday, April 23, 2007 3:16 PM
To: [email protected]
Subject: RE: Water supply NFPA 14 Standpipe & Hose System


A standpipe system is required due to size, for an unsprinklered building.
It is a building code requirement. I'm trying to encourage the owner to
sprinkler it to avoid a standpipe system and a larger water storage
requirement. So I need to calculate the water storage for sprinklers and
standpipe, for comparison.

The class III is also from the building code, which requires both 2 1/2"
hose connections (due to floor area) and 1 1/2" hose stations.

Tony

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Steve Leyton
Sent: April 23, 2007 12:58 PM
To: [email protected]
Subject: RE: Water supply NFPA 14 Standpipe & Hose System

Why is there a Class III standpipe required in the first place?

Steve Leyton
PROTECTION DESIGN & CONSULTING


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of A.P.Silva
Sent: Monday, April 23, 2007 11:48 AM
To: [email protected]
Subject: Water supply NFPA 14 Standpipe & Hose System

I'm designing a class 3 standpipe system for a single storey 300,000
sq.ft.
metal fabrication plant. No city water, so needs a water storage pond.

I'm trying to figure out the required storage volume. NFPA requires 500
gpm
from the most remote standpipe and 500 gpm from each additional stand
pipe
(for floor area exceeding 80,000 sq.ft.) with total not exceeding 1250
gpm,
for a duration of 30 minutes. My opinion is that NFPA 14 mostly covers
multi-storey buildings. When it's single storey, should I take each hose
connection as a standpipe and flow 250 gpm per connection, up to maximum
1250 gpm? It is probably the safest, as it would be the most
conservative.
Has anyone come across this situation?

The other question is regarding hose allowance for fire department. (The
building code water supply requirement does not apply in my area, if the
building has either a sprinkler or standpipe system.) NFPA 14 requires a
standpipe system to be designed for the system demand and fire
department
connections. It says to consult the AHJ for water supply from fire
department pumper. Would it be system demand OR demand for fire
department
pumper (the larger value and not both simultaneously)? Or should a hose
allowance be used same as for a sprinkler system? If so, for what
duration?

Another question (while I'm at it), NFPA 14 requires lateral piping to 2
1/2" hose connections to be protected if the building is not
sprinklered. Up
to now I've never seen piping in a single storey building in fire rated
enclosures. Is it required?

Tony

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to