Typical ceiling diffuser is blowing air downward, (actually in an
umbrella type pattern, but who's to argue)  A sidewall or side of duct
mounted type would be considered horizontal.

By the definition and the directions in the table it looks like you need
to be at least 1'-0" from the edge of the diffuser so if you're 1'-1"
you should be good to go with an Ordinary Temp.  You're mighty close
though.


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Tuesday, May 08, 2007 2:45 PM
To: [email protected]
Subject: Sprinklers located next to diffusers

Looking at Table 8.3.2.5a in 13-2002 there is a downward and horizontal
diffuser.  For the standard 2x2 diffuser in a suspended ceiling which is
the correct to use.  It is blowing air downward and horizontal?  Can I
install an ordinary temp pendant sprinkler 1'-1" away from one of these
diffusers?  

Thanks
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to