Some diffusers are labeled "side" discharge. They blow to the wall and bounce to make circulation. Some reviewers see this as a need for higher temp. Check with your duct contractor and AHJ to be sure.... R/ Matt
[EMAIL PROTECTED] wrote: Typical ceiling diffuser is blowing air downward, (actually in an umbrella type pattern, but who's to argue) A sidewall or side of duct mounted type would be considered horizontal. By the definition and the directions in the table it looks like you need to be at least 1'-0" from the edge of the diffuser so if you're 1'-1" you should be good to go with an Ordinary Temp. You're mighty close though. Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [EMAIL PROTECTED] http://www.lg.com -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED] Sent: Tuesday, May 08, 2007 2:45 PM To: [email protected] Subject: Sprinklers located next to diffusers Looking at Table 8.3.2.5a in 13-2002 there is a downward and horizontal diffuser. For the standard 2x2 diffuser in a suspended ceiling which is the correct to use. It is blowing air downward and horizontal? Can I install an ordinary temp pendant sprinkler 1'-1" away from one of these diffusers? Thanks _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) --------------------------------- Bored stiff? Loosen up... Download and play hundreds of games for free on Yahoo! Games. _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)