We always open the top valve, and plug the closed bottom valve. Without a wrench this makes an accidental trip almost impossible. I've seen the advertisement in sprinkler age for the new "Metraflex" "Never Trip" drum drip replacement. Has anyone tried these yet? How's the cost compare to a drum drip?

Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message ----- From: "Greg McGahan" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Monday, May 14, 2007 7:01 AM
Subject: RE: drum drip


We always close both because with one open and active spring breakers, we
have had tripped systems.

Greg

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Gregg Key,
SET
Sent: Monday, May 14, 2007 8:21 AM
To: [email protected]
Subject: RE: drum drip

Todd, The fitter was probably telling you the truth, which is that he was
taught to close both valves. When I started in the field in the late 70's, I
was taught the same thing. This is a good reason to promote the AFSA
apprenticeship program so the fitters coming up now can be taught the
correct way to do things. And yes, according to the apprenticeship course,
the top valve is to be left open. Gregg

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams
- work
Sent: Sunday, May 13, 2007 8:15 AM
To: [email protected]
Subject: drum drip

When a drum drip is left in 'normal' position, which valves are open
and which closed? I always thought that the top valve is open and the
bottom valve shut. A fitter told me that both valves are supposed to
be shut. When I asked him where that came from, he admitted that's
what he was taught. Which is correct, if either?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to