Hi Thom, I believe the shunt trip has to be installed at the top and the bottom if it is protected with a sprinkler.Also activation can be with a flow switch.Most of the time the heat detector activates the shunt trip.Also top and bottom should be protected with a smoke detector for elevator recall. Check ASME A17.1(2004) Section 2.27.3.2 I hope this helps. From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Thom McMahon Sent: Monday, May 14, 2007 11:32 AM To: [email protected] Subject: Re: Elevators
When protecting an elevator shaft of a (Otis Gen 2) or Kone (Eco Space) type elevator where the elevator equipment is contained in the shaft is protection at top and bottom of the shaft required if the shaft is of non-combustible construction? Would Shunt trips (Flow Switch or heat detector operated) be required for both heads (locations) , or just the top of shaft location? My initial thoughts are both top and bottom for heads, and just top of heat detector. Thom McMahon Firetech, Inc. 2560 Copper Ridge Dr Steamboat Springs, CO 80488-2136 Tel: 970-879-7952 Fax: 970-879-7926 ----- Original Message ----- _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)