I don't like the 24 hour study and then the 5 or 10 psi cushion, but
after looking at some 24 hour graphs I see they ask for it.  Over a 24
hour period the static pressure will vary 20 to 30 psi, not spikes but
waves.  "As appropriate" is relative.


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bill
Minkel
Sent: Tuesday, May 29, 2007 3:30 PM
To: [email protected]
Subject: RE: Minimum safety factor

Note the use of "as appropriate" 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bobby
McCullough
Sent: Tuesday, May 29, 2007 1:37 PM
To: [email protected]
Subject: RE: Minimum safety factor

He could be referring to:

13: 2007  23.2.1.2 The volume and pressure of a public water supply
shall be
determined from waterflow test data. An adjustment to the waterflow test
data to account for daily and seasonal fluctuations, possible
interruption
by flood or ice conditions, large simultaneous industrial use, future
demand
on the water supply system, or any other condition that could affect the
water supply shall be made as appropriate.

Note the use of "shall".

Georgia requires a 10 psi cushion and it is in the Rules and
Regulations.
Some local AHJs have changed it to 5 psi in combination with a 24 hour
static pressure study.

Bobby McCullough


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of George
Church
Sent: Tuesday, May 29, 2007 8:21 AM
To: [email protected]
Subject: RE: Minimum safety factor

Time to ask him to show it to you, you just can't seem to locate the
imaginary section he's trying to enforce.

I just love the paragraphs where cushions are mandated- like "add a 10%
buffer"- does that mean
Add 10% to the volume? 
Add 10% to the required pressure? 
10% of the demand? 
Decrease supply by 10%?
If they'd require tank gradient correction and then a REASONABLE
cushion,
tailored to the specific job's water supply, it would go a l;ong way in
making sense of "what they want" being reasonable. A 10 PSI cushion in a
cliff-like water supply isn't much, and 10 PSI on a 42 PSI residual-on a
mature, flat curve supply- could easily force a fire pump where it isn't
justified or an improvement.

glc

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams
- work
Sent: Tuesday, May 29, 2007 8:01 AM
To: [email protected]
Subject: Re: Minimum safety factor

I have never seen anything in NFPA 13 (I'll go out on a limb and say
there
isn't anything). FM uses a 10 psi cushion. Maybe that's where he came up
with the number.


At 07:21 AM 5/29/2007, you wrote:
>I have an AHJ requesting that I provide 10PSI (not 10%, I already
>checked) safety factors on my hydraulic calculations.  I asked him
where
>he came up with this number since they do not have a published fire 
>ordinance.  He referred me to the appendix in 13 but will not specify a

>specific section.  Is there any such section pertaining to a safety 
>factor requirement that I am missing?
>
>Thanks,
>Dewayne Martinez
>Design Build Fire Protection
>[EMAIL PROTECTED]
>
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>To Unsubscribe, send an email
to:[EMAIL PROTECTED]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to