John,

I don't have a problem with preventing cross-connection. What two
things bother me though is the equipment, and especially the heavy
handed, sometimes ignorance based, enforcement of both the local
purveyors and USC. Examples: 1, Until recently no devices existed
rated for fire service. 2, Until recently no consideration to flows
greater than domestic trickles. 3, The huge pressure drops. 4, A
purveyor (Seattle) that claims the devices must be installed so that
the top of the device is inline with the valves and the entire
assembly must be installed so that "top" is up because that's how
they're listed by USC. 5. That most sprinkler failures are caused by
shut valves. Adding extra valves in a system just increases the risk
of one being closed. 6. A a corollary to 5 I once asked the folks at
USC if I could take the second gate of and replace it with the same
company's PIV. Although the body, discs, screw, etc. were identical
(the only difference from the approved NRS version was the stuffing
box disk used to support the post and the square nut rather than a
hand wheel) they said no. (I believe that company has since gotten the
PIV approved by USC.) I've also found that when trying to open a
dialogue with these people about 1/2 play the my way or the highway
role, 1/2 are disinterested and the third half will understand that
both our goals are public safety and will talk, listen to reason, and
compromise if sensible and/or possible.

On 7/16/07, John Drucker <[EMAIL PROTECTED]> wrote:
David,

That would be akin to saying whats the chances of my building being
involved in a fire, do I really need sprinklers ?.

A building equipped with a standpipe would be one example, or perhaps
where a temporary water supply connection is made via the FDC or where
the fire departments SOG may include standing orders that FDC's be
connected to at all times.

Another thing that came to mind. The plumbing and mechanical sectors
install backflow prevention as a matter of course to prevent cross
contamination. Why does the fire protection sector feel the need for
cross contamination should not apply to fire protection systems ? (Aside
from citing the technology issues noted earlier)

John Drucker

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of David
Autry
Sent: Monday, July 16, 2007 9:15 AM
To: [email protected]
Subject: RE: Backflow: Sprinkler System

Just how many FDC's get used in a fire? Almost every sprinkler saves
that I read says the fire was out by the time the first responders got
there, or the fire was controlled and only had to use a couple lines to
put it out. I realize that high-rise fires on the left or right coast
would be a different story. I've always wondered if the FDC was used and
if so, why?

David Autry
Plans Examiner
Nebraska State Fire Marshal's Office
246 S. 14th Street
Lincoln, NE 68508
402-471-9659
402-471-3118 fax
www.sfm.ne.gov


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of John
Drucker
Sent: Saturday, July 14, 2007 8:26 AM
To: [email protected]
Subject: RE: Backflow: Sprinkler System

Roland,

Fire Departments do the damnest things, even so far as drafting from
storm sewers. It all comes back to the emergency nature of fires.

Once upon a time in draft I witnessed sand and seahells from a deck gun.
When the operator was alerted he responded by saying that they could fix
the pump later. He was correct.

My community resides on a tidal river. Many road lead right up to the
river.
Many sprinklered buildings with FDC's are along the river where the fire
department has direct unimpeded access to the river.

Lastly think fire departments don't go to draft, well consider that my
company did just that at a house fire last year. (Theres another member
of this list who was there). It does and will happen so long as that
heavy semirigid hose keeps getting installed on fire engines and
drafting remains in the SOGs.

John Drucker
Captain
Middletown Twp Fire Dept
Station 8

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Friday, July 13, 2007 10:04 AM
To: [email protected]
Subject: Re: Backflow: Sprinkler System

One of the aspects that drive an RPZ is when the fire dept draft from
non-potable sources (anytime).

Roland
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)



--