Steve,

Check NFPA 13 section 7.3.2.4(3). The standard requires return bends, not just arm-overs. That would be pretty funky under a duct and you might not even be able to keep the pipe above the grills. Too bad section 8.7.3.1.7 (2007) doesn't apply to ducts as well as overhead doors.

Todd


At 07:31 AM 7/20/2007, you wrote:
I have a situation in a data center on a double preaction system where I
need to use standard pendent heads to sprinkler under some wide ductwork
with return grill drops coming off of the bottom of it every 5' along its
length.  My branchlines will run parallel to the ducts and I want to come
off and put a head under the duct every 15'.  I am using pendents because
the owner requires that the sprinkler piping be above the lowest point of
the HVAC system which is the bottom of these return grills, and because the
grills would create an obstruction if I put an upright up in between them.
Since it is a preaction system, 13 says I must either use dry pendents or
armovers.  If I use an armover, I would have to offset horizontally in the
drop of the armover to get under the duct.  Can you do that?



Thank you very much,



Steve Kowkabany, P.E.

Fire Protection Engineer

Neptune Fire Protection Engineering LLC

216 Seagate Avenue Unit B

Neptune Beach, FL 32266

904-652-4200 Phone

904-212-0868 Fax







_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com