I missed the initial posting but it appears that Steve wants to do a
standard (outlet rolled to the horizontal) armover>drop>pendant
arrangement on his DI preaction system. As Todd points out he needs to
use a return bend. But he seems to sees the branchline under duct
which Steve says is prohibited by the client for an unstated reason. I
don't see any reason why an upright
nozzle>nipple>ell>nipple>ell>drop>ell>armover>outlet ell>pendant
wouldn't meet code nor be too ugly. The problem is that anytime you
have a trip, wanted or not, you need to remove all the drops and drain
them. That is a good argument for the double-interlock but the
increased cost, maintenance and likelihood of failure during an actual
event (more complexity creates more opportunities for convergences of
malfunctions) argues against the system. For Steve's purposes,
assuming the owner is opposed to wet under any circumstances--we are,
after all, designing for the most reliable fire suppression system,
not the least likely to accidentally discharge, I'd opt for single
interlock with low pressure air supervision but with the dry pendants
whether SI or DI. Well, enough. It's Sunday morning and no time for a
sermon.

On 7/22/07, Todd Williams - work <[EMAIL PROTECTED]> wrote:
Steve,

Check NFPA 13 section 7.3.2.4(3). The standard requires return bends,
not just arm-overs. That would be pretty funky under a duct and you
might not even be able to keep the pipe above the grills. Too bad
section 8.7.3.1.7 (2007) doesn't apply to ducts as well as overhead doors.

Todd


At 07:31 AM 7/20/2007, you wrote:
>I have a situation in a data center on a double preaction system where I
>need to use standard pendent heads to sprinkler under some wide ductwork
>with return grill drops coming off of the bottom of it every 5' along its
>length.  My branchlines will run parallel to the ducts and I want to come
>off and put a head under the duct every 15'.  I am using pendents because
>the owner requires that the sprinkler piping be above the lowest point of
>the HVAC system which is the bottom of these return grills, and because the
>grills would create an obstruction if I put an upright up in between them.
>Since it is a preaction system, 13 says I must either use dry pendents or
>armovers.  If I use an armover, I would have to offset horizontally in the
>drop of the armover to get under the duct.  Can you do that?
>
>
>
>Thank you very much,
>
>
>
>Steve Kowkabany, P.E.
>
>Fire Protection Engineer
>
>Neptune Fire Protection Engineering LLC
>
>216 Seagate Avenue Unit B
>
>Neptune Beach, FL 32266
>
>904-652-4200 Phone
>
>904-212-0868 Fax
>
>
>
>
>
>
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>To Unsubscribe, send an email to:[EMAIL PROTECTED]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)



--
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to