Tony, Ron, and Todd, Thanks for the feedback. You're absolutely right - I mistyped when I wrote "armover" and meant to say "return bend". I think we have the solution now which is to use short (5" long) dry pendents sprinklers instead (also allowed on double preaction systems per 13) directly off the branchlines, which will run perpendicular to the ducts between the return grill drops. That meets the elevation requirement of being above the lowest point of the ductwork, avoids any obstruction issues, gives us a way to hang the pipe easily, and seems to offer a more simple solution. It also makes the "heat collector issue" a moot point although that was a very interesting observation.
Thank you very much for your help and enjoy the rest of your weekend, Steve -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of A.P.Silva Sent: Sunday, July 22, 2007 12:10 PM To: [email protected] Subject: RE: Armover Question I'm not sure whether I understand the question. But it appears it is asking how to have pendent heads below a duct on a double interlocked pre-action system. First, you need return bends, or dry pendents, not arm-overs. These heads are being added for obstructions. So the deflectors have to be flush or below the bottom of the duct/grille to clear the obstruction, not directly below it. I know some won't agree with me on this point, thinking the head has to be directly below the duct for heat collection. Granted that there is no such thing as a heat collector (unless it is about 15' x 15' the coverage area of a sprinkler), the head has only to clear the obstruction, not necessarily be directly below it. Of course, you need to position it to prevent cold soldering or provide a water shield. My two cents. Tony -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams - work Sent: July 22, 2007 6:37 AM To: [email protected] Subject: Re: Armover Question Steve, Check NFPA 13 section 7.3.2.4(3). The standard requires return bends, not just arm-overs. That would be pretty funky under a duct and you might not even be able to keep the pipe above the grills. Too bad section 8.7.3.1.7 (2007) doesn't apply to ducts as well as overhead doors. Todd At 07:31 AM 7/20/2007, you wrote: >I have a situation in a data center on a double preaction system where I >need to use standard pendent heads to sprinkler under some wide ductwork >with return grill drops coming off of the bottom of it every 5' along its >length. My branchlines will run parallel to the ducts and I want to come >off and put a head under the duct every 15'. I am using pendents because >the owner requires that the sprinkler piping be above the lowest point of >the HVAC system which is the bottom of these return grills, and because the >grills would create an obstruction if I put an upright up in between them. >Since it is a preaction system, 13 says I must either use dry pendents or >armovers. If I use an armover, I would have to offset horizontally in the >drop of the armover to get under the duct. Can you do that? > > > >Thank you very much, > > > >Steve Kowkabany, P.E. > >Fire Protection Engineer > >Neptune Fire Protection Engineering LLC > >216 Seagate Avenue Unit B > >Neptune Beach, FL 32266 > >904-652-4200 Phone > >904-212-0868 Fax > > > > > > > >_______________________________________________ >Sprinklerforum mailing list >[email protected] >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > >To Unsubscribe, send an email to:[EMAIL PROTECTED] >(Put the word unsubscribe in the subject field) Todd G. Williams, PE Fire Protection Design/Consulting Stonington, Connecticut 860-535-2080 www.fpdc.com _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)
