Tony,

This heat collection thing keeps coming up over and over and having
been beset with it for years I've been "I've been absorbed by the
body" since resistance has seemingly been futile. That said my son who
is still pretty fresh to this field keeps actually reading the books
with fresh eyes and no pre-conceptions. as such he keeps blowing my
old guy ideas out of the water. As he keeps pointing out 13 does not
address obstruction to heat collection, only discharge. Heat
collection is inherent in placement rules and obstruction rules are
essentially "exceptions" (bad word these days) to those placement
rules. That said I agree that the heads need not be placed under the
ducts themselves but merely on a plane equal to (depending on distance
from the ducts subject to obstruction to spray development rules) or
below the bottom of the ducts.

On 7/22/07, A.P.Silva <[EMAIL PROTECTED]> wrote:
I'm not sure whether I understand the question. But it appears it is asking
how to have pendent heads below a duct on a double interlocked pre-action
system. First, you need return bends, or dry pendents, not arm-overs. These
heads are being added for obstructions. So the deflectors have to be flush
or below the bottom of the duct/grille to clear the obstruction, not
directly below it. I know some won't agree with me on this point, thinking
the head has to be directly below the duct for heat collection. Granted that
there is no such thing as a heat collector (unless it is about 15' x 15' the
coverage area of a sprinkler), the head has only to clear the obstruction,
not necessarily be directly below it. Of course, you need to position it to
prevent cold soldering or provide a water shield.

My two cents.

Tony

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams
- work
Sent: July 22, 2007 6:37 AM
To: [email protected]
Subject: Re: Armover Question

Steve,

Check NFPA 13 section 7.3.2.4(3). The standard requires return bends,
not just arm-overs. That would be pretty funky under a duct and you
might not even be able to keep the pipe above the grills. Too bad
section 8.7.3.1.7 (2007) doesn't apply to ducts as well as overhead doors.

Todd


At 07:31 AM 7/20/2007, you wrote:
>I have a situation in a data center on a double preaction system where I
>need to use standard pendent heads to sprinkler under some wide ductwork
>with return grill drops coming off of the bottom of it every 5' along its
>length.  My branchlines will run parallel to the ducts and I want to come
>off and put a head under the duct every 15'.  I am using pendents because
>the owner requires that the sprinkler piping be above the lowest point of
>the HVAC system which is the bottom of these return grills, and because the
>grills would create an obstruction if I put an upright up in between them.
>Since it is a preaction system, 13 says I must either use dry pendents or
>armovers.  If I use an armover, I would have to offset horizontally in the
>drop of the armover to get under the duct.  Can you do that?
>
>
>
>Thank you very much,
>
>
>
>Steve Kowkabany, P.E.
>
>Fire Protection Engineer
>
>Neptune Fire Protection Engineering LLC
>
>216 Seagate Avenue Unit B
>
>Neptune Beach, FL 32266
>
>904-652-4200 Phone
>
>904-212-0868 Fax
>
>
>
>
>
>
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>To Unsubscribe, send an email to:[EMAIL PROTECTED]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)



--
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to