Steve,
Yes you can derive the section modulus for all materials and cross
sections. There is plenty of software out there that you can use to do
this. If you are going to ascertain the modulus of strut, then I would ask
the manufacturer for all of his calculations and information for his
product. This way you can get the parameters that he is using to determine
if it conforms to NFPA 13. Angle iron, channel iron, pipe, etc is easy to
determine with information from many sources including shareware off the
Internet. The table in NFPA 13 is based on a maximum allowable bending
stress of 15 ksi and a midspan concentrated load from 15 ft (4.6 m) of
water-filled pipe, plus 250 lb (114 kg). Also remember that all components
of pipe hangers are required to be ferrous unless allowed differently by
the AHJ.
Thank You
Rahe Loftin, P.E.
Region 7 - GSA
Office - 817-978-7299
Fax - 817-978-8644
Cell - 817-371-3102
"Steve Leyton"
<[EMAIL PROTECTED] To
design.com> [email protected]
Sent by: cc
sprinklerforum-bo
[EMAIL PROTECTED] Subject
er.org RE: Section moduli of Unistrut
07/23/2007 10:24
AM
Please respond to
[EMAIL PROTECTED]
resprinkler.org
I don't know the specifics of Tol-Strut, Uni-Strut or Powerstrut load
bearing abilities in a trapeze application, but you were considering
this application in SoCal you would have to furnish a letter from the
manufacturer and possibly one from the project SE as well. I've seen
conduits trapezed on strut, but never piping.
Does anyone know if the "section modulus" is a standardized measurement
or value? If NFPA 13 publishes these values for "pre-engineered"
trapeze materials like pipe and angle iron, can I easily derive the
modulus value for other materials by applying a formula to the
material's dimensions or the manufacturer's stated load bearing
capacity?
Steve Leyton
PROTECTION DESIGN & CONSULTING
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Travis
Mack
Sent: Monday, July 23, 2007 8:17 AM
To: [email protected]
Subject: RE: Section moduli of Unistrut
As long as we go with the strut as indicated by the manufacturer's
criteria,
we should be OK?? You can't use slotted 1-5/8" strut for much of
anything
as I have seen some try to do on many different occasions.
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bill
Minkel
Sent: Monday, July 23, 2007 8:12 AM
To: [email protected]
Subject: RE: Section moduli of Unistrut
Unistrut will not work for most trapeeze, section modulus is very low.
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of G. Tim
Stone
Sent: Monday, July 23, 2007 8:59 AM
To: [email protected]
Subject: RE: Section moduli of Unistrut
Travis,
Check out the following link to Power Strut:
http://www.powerstrut.com/psjan2005/fibergl182.jpg
G. Tim Stone
NICET Level III Engineering Technician
Fire Protection Sprinkler Design
and Consulting Services
117 Old Stage Rd. - Essex Jct., VT. 05452
TEL: (802) 434-2968 Fax: (802) 434-4343
[EMAIL PROTECTED]
> -----Original Message-----
> From: [EMAIL PROTECTED] [mailto:sprinklerforum-
> [EMAIL PROTECTED] On Behalf Of Travis Mack
> Sent: Monday, July 23, 2007 8:29 AM
> To: [email protected]
> Subject: Section moduli of Unistrut
>
> Does anyone have a datasheet or link to download one for Unistrut (or
> something similar) that gives the section modulus. We need to size
> some unistrut for trapeze hangers. I remember a table in the unistrut
> catalogues from many years ago, but can't find it any more.
>
> Thanks for your help.
>
> Travis
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
__________ NOD32 2414 (20070723) Information __________
This message was checked by NOD32 antivirus system.
http://www.eset.com
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)