Travis,
Trapeze hangers using strut type product is acceptable so long as it is
sized properly.  Power-Strut has a technical data sheet that provides the
section modulus for it's product in both sch 10 and sch 40 comparisons.  As
well, slotted strut is ok w/ P-S so long as it is the proper series, i.e.
PS-200, used in the section modulus.  I will send you what info I have.

Bob Knight

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Travis Mack
Sent: Monday, July 23, 2007 9:28 AM
To: [email protected]
Subject: RE: Section moduli of Unistrut

I see strut used as trapeze for piping all the time.  However, it is often
grossly undersized.  From what I have seen, you are required to use solid
strut, not the standard slotted strut that we see all the time. 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Steve Leyton
Sent: Monday, July 23, 2007 8:25 AM
To: [email protected]
Subject: RE: Section moduli of Unistrut

I don't know the specifics of Tol-Strut, Uni-Strut or Powerstrut load
bearing abilities in a trapeze application, but you were considering this
application in SoCal you would have to furnish a letter from the
manufacturer and possibly one from the project SE as well.  I've seen
conduits trapezed on strut, but never piping.  

Does anyone know if the "section modulus" is a standardized measurement or
value?  If NFPA 13 publishes these values for "pre-engineered"
trapeze materials like pipe and angle iron, can I easily derive the modulus
value for other materials by applying a formula to the material's dimensions
or the manufacturer's stated load bearing capacity?

Steve Leyton
PROTECTION DESIGN & CONSULTING


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Travis Mack
Sent: Monday, July 23, 2007 8:17 AM
To: [email protected]
Subject: RE: Section moduli of Unistrut

As long as we go with the strut as indicated by the manufacturer's criteria,
we should be OK??  You can't use slotted 1-5/8" strut for much of anything
as I have seen some try to do on many different occasions.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bill Minkel
Sent: Monday, July 23, 2007 8:12 AM
To: [email protected]
Subject: RE: Section moduli of Unistrut

Unistrut will not work for most trapeeze, section modulus is very low. 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of G. Tim Stone
Sent: Monday, July 23, 2007 8:59 AM
To: [email protected]
Subject: RE: Section moduli of Unistrut

Travis,

Check out the following link to Power Strut: 
  
http://www.powerstrut.com/psjan2005/fibergl182.jpg


G. Tim Stone


NICET Level III Engineering Technician
Fire Protection Sprinkler Design
and Consulting Services

117 Old Stage Rd. - Essex Jct., VT. 05452
TEL: (802) 434-2968          Fax: (802) 434-4343
                [EMAIL PROTECTED]

> -----Original Message-----
> From: [EMAIL PROTECTED] [mailto:sprinklerforum-

> [EMAIL PROTECTED] On Behalf Of Travis Mack
> Sent: Monday, July 23, 2007 8:29 AM
> To: [email protected]
> Subject: Section moduli of Unistrut
> 
> Does anyone have a datasheet or link to download one for Unistrut (or 
> something similar) that gives the section modulus.  We need to size 
> some unistrut for trapeze hangers.  I remember a table in the unistrut

> catalogues from many years ago, but can't find it any more.
> 
> Thanks for your help.
> 
> Travis
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

__________ NOD32 2414 (20070723) Information __________

This message was checked by NOD32 antivirus system.
http://www.eset.com


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

__________ NOD32 2414 (20070723) Information __________

This message was checked by NOD32 antivirus system.
http://www.eset.com


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

No virus found in this incoming message.
Checked by AVG Free Edition. 
Version: 7.5.476 / Virus Database: 269.10.12/910 - Release Date: 7/21/2007
3:52 PM
 

No virus found in this outgoing message.
Checked by AVG Free Edition. 
Version: 7.5.476 / Virus Database: 269.10.12/910 - Release Date: 7/21/2007
3:52 PM
 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to