Correct, that is a good explanation. Unistrut is not much good for 5' to 7'
spans of 3" or 4" or larger sprinkler pipe. Hence my previous assertation
that its use as a trapeze is limited. It is too often used where not
appropriate. This subject is done now, thanks.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Monday, July 23, 2007 11:47 AM
To: [email protected]
Subject: Re: Section moduli of Unistrut

Section modulus is an engineering formula which provides a property
(measurement) of a cross sectional shape and reflects both the shape and
orientation of the object.  It can be determined through the equation S =
I/c, where I = moment of inertia about an axis through the centroid, and c =
distance from the centroid to the extreme edge of the section.  
This is according to the "Manual for Steel Construction, 8th Edition" 
sitting on my bookshelf.  This volume also has page after page of various S
values for dozens of shapes in dozens of sizes, including both slotted and
non-slotted channel, S members, I, members, W, members, C-channel, etc.

And NFPA-13 ('02) would certainly allow you to use trap members other than
those shown in the standard, as long as they had the appropriate section
modulus.  Section 9.1.1.6.2 advises "Any other sizes or shapes giving equal
or greater section modulus shall be acceptable"  which seems pretty final to
me.

And I don't know about Unistrut not working for trapeze members.  Base don
the values shown as a minimum in NFPA-13, I could use a 0.202 section
modulus uni-strut to create a 3'-0" span trapeze to support 2-1/2" schedule
40. 

PARSLEY CONSULTING

Ken Wagoner, SET

760.745.6181 voice

760.745.0537 fax

[EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> e-mail

www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to