No there is not.  As a previous post indicated, the language of 508.3
states that fire flow shall be determined by "an approved method".  If
you go to Appendix B, Fire Flow for Buildings, you will find the
required minimum flow rates and durations, based on building type and
area (but NOT based on occupancy group) and the prescriptive allowance
for discounts taken for sprinklers.  But those are GROSS flow rates and
it is NOT required that you add a separate concurrent flow for
sprinklers.  The tables are based on the reasonable assumption that the
combined flow of hose streams and sprinklers, within the tabled
parameters, is adequate for both automatic and manual streams.

Steve Leyton
PROTECTION DESIGN & CONSULTING


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Pete
Schwab
Sent: Wednesday, July 25, 2007 6:33 AM
To: [email protected]
Subject: Fire Flow Requirements

Forum
Is there any code language or requirements that a private supply main
for a building/complex be capable of supplying the sprinkler system
demand (including hose demand) and the Hydrant Fire Flow demand
simultaneously.
Pete Schwab
Wayne Automatic Fire Sprinklers


Wayne Automatic Fire Sprinklers, Inc.
2006 Inductee into "The Players Hall of Fame"
at The Great Games of Business
Wayne Automatic Fire Sprinklers, Inc. "Best Places to Work"
Rated #1 in 2006
Large Business Category
by Orlando Business Journal
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to