TYCO actually has a flex connector for this very purpose. Obviously not sch
40 galv. pipe. Use one of those and he'll be arguing with the MFG instead of
you if he still wants to argue.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message -----
From: "Greg McGahan" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Wednesday, July 25, 2007 11:57 AM
Subject: air compressor piping
Does anyone know of there are any obscure requirements in NFPA 13 or the
UFC
that requires the piping between the air compressor and the dry valve to
be
Galvanized steel pipe? We intend to use copper but have a govt inspector
telling us it has to be steel.
Thanks,
Greg