NFPA 101[2006]8.7.1.1: Protection from any area? having a degree of hazard 
greater? than that normal to the general occupancy of the building or 
structure? shall be provided? by one of the following means:(1) Enclosing the 
area? with a fire barrier? without windows that has? a 1 hour fire resistance? 
rating in accordance? with section 8.3. (2) protecting the area with automatic 
extinguishing systems in accordance? with section 9.7.? (3) Applying both 
8.7.1.1 (1) and 8.7.1.1(2) where the hazard is severe? or where? otherwise 
specified by chapter 12 through chapter 42.
A.8.7.1.1. Areas requiring special hazard protection include, but are not 
limited to, areas such as those used for storage? of combustibles of 
flammables, areas housing "heat-producing appliances", or areas used for 
maintenance? purposes.

The fancoil area is a return air plenum that need to comply with NFPA 90A;the 
wires , the equipment must fire rated for plenum. NFPA? 70 would require 
certain distances ,clearances for maintenace of the fan coil.?The fancoil has a 
motor, relays , transformers, capacitors, electric heater;sometimes the fan 
blades are made of plastic.Many things can go wrong.
mario berrios
[EMAIL PROTECTED]


-----Original Message-----
From: Todd Williams - work <[EMAIL PROTECTED]>
To: [email protected]
Sent: Sun, 29 Jul 2007 5:46 pm
Subject: Re: Fan Coil Enclosure in dwelling unit


OK, but is an enclosure only accessible via an access panel (I would assume 
something like 2' x 2') considered a closet? I would think that this falls 
under the definition of a concealed space rather than a closet and would need 
to be analyzed under section 8.14.1.2 (2002). The question then becomes, does 
this situation meet any of those criteria??
?
At 05:18 PM 7/29/2007, you wrote:?
?
>NFPA 101 [2006];30.3.5.4. In buildings sprinklered in accordance >with NFPA 
>13, closets less than 12 sq ft in area in individual >dwelling units shall not 
>be required? to be sprinklered .Closets >that contain equipment such as 
>washers ,dryers , furnaces, or water >heaters? shall be spriklered regardless 
>of size.?
>?
>Paragraph 30.3.5.4 exempts small closets from being sprinklered >because of 
>the limited? fuel load [ I do not agree] characteristics? >of apartment unit 
>closets.?The closets? exempted are limited? to >those within a living unit; 
>closets in common building areas? are >not exempted . Also, any closet that 
>contains HVAC equipment or >washers and dryers is not permitted? to take 
>advantage? of the >sprinkler exemption due to the inherent ignition? sources 
>and >combustible fuel load.?
>The electric heater in the fancoil? is not encased ,so the electric 
>>resistance is open to the air stream that carries dust and particles >of 
>paper and other matters?that can ignite.?
>mario berrios?
>[EMAIL PROTECTED]
>?
>dk?
>?
>?
>-----Original Message-----?
>From: A.P.Silva <[EMAIL PROTECTED]>?
>To: [EMAIL PROTECTED]
>Sent: Sun, 29 Jul 2007 4:02 pm?
>Subject: Fan Coil Enclosure in dwelling unit?
>?
>?
>?
>?
>No takers for my previous question. So re-posting it on the forum. Will?
>appreciate any reply.?
>?
>Tony?
>?
>-----Original Message-----?
>From: [EMAIL PROTECTED]
>[mailto:[EMAIL PROTECTED] On Behalf Of A.P.Silva?
>Sent: July 27, 2007 7:26 AM?
>To: [EMAIL PROTECTED]
>Subject: Fan Coil Enclosure in dwelling unit?
>?
>?
>?
>-----Original Message-----?
>From: [EMAIL PROTECTED]
>[mailto:[EMAIL PROTECTED] On Behalf Of A.P.Silva?
>Sent: July 27, 2007 12:05 AM?
>To: [EMAIL PROTECTED]
>Subject: RE: Questions to ask when selecting a contractor?
>?
>I remember this topic being discussed earlier, but I simply can't find it in?
>the archives.?
>?
>Five storey residential building (actually 4 storey + loft), designed to?
>NFPA 13 (1996), has electric fan coil units in every suite enclosed within?
>the walls. From the fan coil there will probably be grilles/diffusers, open?
>to the suites. Also there might be an access panel for maintenance. Other?
>than that the space is not accessible and the construction is?
>non-combustible.?
>?
>Question: would this space have to be sprinklered??
>?
>Commonsense says it shouldn't. We have electric fans in non-combustible?
>ceiling spaces, which are not sprinklered. Any code justification??
>?
>Tony?
>?
>?
>_______________________________________________?
>Sprinklerforum mailing list?
>[EMAIL PROTECTED]
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum?
>?
>To Unsubscribe, send an email to:[EMAIL PROTECTED]
>(Put the word unsubscribe in the subject field)?
>?
>_______________________________________________?
>Sprinklerforum mailing list?
>[EMAIL PROTECTED]
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum?
>?
>To Unsubscribe, send an email to:[EMAIL PROTECTED]
>(Put the word unsubscribe in the subject field)?
>?
>_______________________________________________?
>Sprinklerforum mailing list?
>[EMAIL PROTECTED]
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum?
>?
>To Unsubscribe, send an email to:[EMAIL PROTECTED]
>(Put the word unsubscribe in the subject field)?
>?
>?
>________________________________________________________________________?
>AOL now offers free email to everyone. Find out more about what's >free from 
>AOL at AOL.com.?
>_______________________________________________?
>Sprinklerforum mailing list?
>[EMAIL PROTECTED]
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum?
>?
>To Unsubscribe, send an email to:[EMAIL PROTECTED]
>(Put the word unsubscribe in the subject field)?
?
Todd G. Williams, PE?
Fire Protection Design/Consulting?
Stonington, Connecticut?
860-535-2080?
www.fpdc.com ?
_______________________________________________?
Sprinklerforum mailing list?
[EMAIL PROTECTED]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum?
?
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)?


________________________________________________________________________
AOL now offers free email to everyone.  Find out more about what's free from 
AOL at AOL.com.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to