Check out NFPA 13, 2007, 21.20.19.2.1.  Based on that it sounds like you
will have to provide a sprinkler in that space. 


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of A.P.Silva
Sent: Monday, July 30, 2007 11:15 AM
To: [email protected]
Subject: RE: Fan Coil Enclosure in dwelling unit

The size of the concealed space is 4'x2'. The fan coil unit takes about
half of that space, 2'x2'. I don't have some specifics yet, but I
imagine there must be an access panel, about 30"x30", for maintenance.
So storage beside it can be ruled out.

The floor and ceiling of this space is concrete. Walls are drywall with
steel studs that go from floor to ceiling.

One fan coil per unit for the apartment type condominiums. In some
suites the diffusers are right on the walls enclosing the fan coil. In
some, there is some ducting to diffusers in adjacent rooms, but always
serving the same suite.

Tony   

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: July 30, 2007 8:41 AM
To: [email protected]
Subject: RE: Fan Coil Enclosure in dwelling unit

What is the size of the space in which the fan coil resides?   Is the
maintenance panel accessible by the tenant?  Is the space large enough
where items could be stored adjacent to or around the fan coil unit? 

Where the fan coil resides, is it open above to a common space such as
attic or interstitial space between floors?  

You state the space is non-combustible,  does ductwork pass from the
space occupied by the fan coil and into other adjacent spaces or only
serve one occupied unit?

When you say residential, do you mean like apartments with a single fan
coil unit serving that apartment only?

Just need some specifics.


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of A.P.Silva
Sent: Sunday, July 29, 2007 4:02 PM
To: [email protected]
Subject: Fan Coil Enclosure in dwelling unit

No takers for my previous question. So re-posting it on the forum. Will
appreciate any reply.

Tony

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of A.P.Silva
Sent: July 27, 2007 7:26 AM
To: [email protected]
Subject: Fan Coil Enclosure in dwelling unit



-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of A.P.Silva
Sent: July 27, 2007 12:05 AM
To: [email protected]
Subject: RE: Questions to ask when selecting a contractor

I remember this topic being discussed earlier, but I simply can't find
it in the archives.

Five storey residential building (actually 4 storey + loft), designed to
NFPA 13 (1996), has electric fan coil units in every suite enclosed
within the walls. From the fan coil there will probably be
grilles/diffusers, open to the suites. Also there might be an access
panel for maintenance. Other than that the space is not accessible and
the construction is non-combustible.

Question: would this space have to be sprinklered? 

Commonsense says it shouldn't. We have electric fans in non-combustible
ceiling spaces, which are not sprinklered. Any code justification?

Tony   


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to