NFPA 101 [2006];30.3.5.4. In buildings sprinklered in accordance with NFPA 13, 
closets less than 12 sq ft in area in individual dwelling units shall not be 
required? to be sprinklered .Closets that contain equipment such as washers 
,dryers , furnaces, or water heaters? shall be spriklered regardless of size.

Paragraph 30.3.5.4 exempts small closets from being sprinklered because of the 
limited? fuel load [ I do not agree] characteristics? of apartment unit 
closets.?The closets? exempted are limited? to those within a living unit; 
closets in common building areas? are not exempted . Also, any closet that 
contains HVAC equipment or washers and dryers is not permitted? to take 
advantage? of the sprinkler exemption due to the inherent ignition? sources and 
combustible fuel load.
The electric heater in the fancoil? is not encased ,so the electric resistance 
is open to the air stream that carries dust and particles of paper and other 
matters?that can ignite.
mario berrios
[EMAIL PROTECTED]

dk


-----Original Message-----
From: A.P.Silva <[EMAIL PROTECTED]>
To: [email protected]
Sent: Sun, 29 Jul 2007 4:02 pm
Subject: Fan Coil Enclosure in dwelling unit




No takers for my previous question. So re-posting it on the forum. Will
appreciate any reply.

Tony

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of A.P.Silva
Sent: July 27, 2007 7:26 AM
To: [email protected]
Subject: Fan Coil Enclosure in dwelling unit



-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of A.P.Silva
Sent: July 27, 2007 12:05 AM
To: [email protected]
Subject: RE: Questions to ask when selecting a contractor

I remember this topic being discussed earlier, but I simply can't find it in
the archives.

Five storey residential building (actually 4 storey + loft), designed to
NFPA 13 (1996), has electric fan coil units in every suite enclosed within
the walls. From the fan coil there will probably be grilles/diffusers, open
to the suites. Also there might be an access panel for maintenance. Other
than that the space is not accessible and the construction is
non-combustible.

Question: would this space have to be sprinklered? 

Commonsense says it shouldn't. We have electric fans in non-combustible
ceiling spaces, which are not sprinklered. Any code justification?

Tony   


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


________________________________________________________________________
AOL now offers free email to everyone.  Find out more about what's free from 
AOL at AOL.com.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to