Brian, What is the adopted building code in this jurisdiction ? That's the starting point.
John Drucker -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Brian Harris Sent: Thursday, August 02, 2007 8:06 AM To: [email protected] Subject: Telecom & Data Rooms I'm being told by an Architect we are doing a school with that I need to remove any heads from the Telecom & Data rooms and that I'm not allowed to run any pipe above those ceilings either. He is basing it on the provisions for eliminating heads in and Electrical room with a 2 hour fire wall, am I missing something? I am not aware of Telecom & Data rooms falling into the same category as an Electrical room. I have approved plans from the AHJ with the heads shown in those rooms and omitted from the Electrical rooms. Any thoughts? _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)
